Brand new construction. This is the cold water supply valve for the H2O Heater. When the heater heats up, condensation comes out of the plastic tube. What should I call it and why is it there? Thank you in advance for all your help!
Attached Thumbnails
a-p8150120-2-.jpg.JPG
Views:	131
Size:	40.9 KB
ID:	13964   a-p8150121-2-.jpg.JPG
Views:	108
Size:	40.7 KB
ID:	13965  



Tom Yeager
Owner/Certified Inspector
Inspect-It 1st
303-464-9090
www.tyeagerinspects.com
NEHA Radon Certification # 104169 RT
NACHI Certified Home Inspector
Reply With Quote
  #2  
Old 8/15/07, 10:54 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this?

it is an expansion valve and takes the place of an expansion tank-----they waste at little water to relief the pressure----hence the little drain tube attached
Reply With Quote
  #3  
Old 8/15/07, 11:32 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this?

Quote:
Originally Posted by cbuell
it is an expansion valve and takes the place of an expansion tank-----they waste at little water to relief the pressure----hence the little drain tube attached
I have never seen an expansion tank on a hot water tank so why an expansion valve. They are required on heating boilers due to the check valves in the water replacement/supply line. Is there a check valve somewhere in the supply line? Does it also have the regular TPR valve?
Reply With Quote
  #4  
Old 8/15/07, 11:46 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this?

When water is heated it expands. If the inlet is not blocked by a check valve, pressure reducing valve, or other device, the increase in volume simply travels back into the source. If the inlet is blocked, this increase in volume will cause an increase in pressure, sometimes to dangerous levels and the Temp/Press valve may open.

A thermal expansion tank can be installed in the line that will absorb the increase in volume, preventing the relief valve from discharging unnecessarily.


Reply With Quote
  #5  
Old 8/16/07, 12:07 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this?

Quote:
Originally Posted by rwand1

A thermal expansion tank can be installed in the line that will absorb the increase in volume, preventing the relief valve from discharging unnecessarily.
Know the theory, Raymond, but do you see many or have seen any expansion tanks on hot water tanks unless they were being used for space heating purposes?
Reply With Quote
  #6  
Old 8/16/07, 12:47 AM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this?

Brian A. MacNeish asked:

Quote:
"Know the theory, Raymond, but do you see many or have seen any expansion tanks on hot water tanks unless they were being used for space heating purposes?"
Space heating has nothing to do with when expansion tanks or expansion valves are required or should be installed on water heaters.

Plumbing Codes such as the IRC require an expansion tank or similar device on any tanked water heater where there is present a backflow perventer, a pressure-reducing valve, or other flow restricter on the cold-water supply.

Charles Buell has this one correct.
Reply With Quote
  #7  
Old 8/16/07, 12:50 AM
sparksnmore sparksnmore is offline
Active Poster
 
Join Date: Oct 2006
Location: midwest
Posts: 177
Please Note: sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this?

We're starting to see and install more and more of them every day now around here.
I believe because the water company started putting in check valves to keep hot water from backing through their meters.
Reply With Quote
  #8  
Old 8/16/07, 1:51 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 6,931
Default Re: What is this?

Quote:
Originally Posted by tyeager
Brand new construction. This is the cold water supply valve for the H2O Heater. When the heater heats up, condensation comes out of the plastic tube. What should I call it and why is it there? Thank you in advance for all your help!
That's what I found on this one last week, with gas compression fittings and no TPR valve. I couldn't get a pic from the other side. This was a '93 W.H.



Christopher Currins
Certified, Licensed

Proudly serving the Illinois Metro-East

Illinois Home Inspector

Top 5 Tasks for January

Last edited by ccurrins; 4/20/09 at 1:47 AM..
Reply With Quote
  #9  
Old 8/16/07, 7:55 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this?

Quote:
Originally Posted by homebild

Space heating has nothing to do with when expansion tanks or expansion valves are required or should be installed on water heaters.

Plumbing Codes such as the IRC require an expansion tank or similar device on any tanked water heater where there is present a backflow perventer, a pressure-reducing valve, or other flow restricter on the cold-water supply.

Charles Buell has this one correct.
We very rarely have any of the highlighted items installed on cold supply lines here. I've been inspecting for 23 years and have only seen a few pressure reducing valves installed. I know why an expansion tank should be installed but is not required practice here yet, maybe due to so little need and no failures yet.
Reply With Quote
  #10  
Old 8/16/07, 9:20 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this?

Brian

You need to get out of your corner of the world.
Reply With Quote
  #11  
Old 8/16/07, 3:41 PM
Tom Yeager Tom Yeager is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Broomfield, CO
Posts: 40
Default Re: What is this?

Thanks for all your input! The point is, it is an expansion valve. Why it is there, we're not sure (Yes, the heater has the appropriate TPR valve.) Maybe it's some local code thing (Lakewood CO) But it seems to be functioning as intended. At least now I know what to call them if/when I see it again! Thanks!



Tom Yeager
Owner/Certified Inspector
Inspect-It 1st
303-464-9090
www.tyeagerinspects.com
NEHA Radon Certification # 104169 RT
NACHI Certified Home Inspector
Reply With Quote
  #12  
Old 8/16/07, 10:10 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this?

Quote:
Originally Posted by rwand1
Brian

You need to get out of your corner of the world.
It's more relaxing down here. Some of the housing is the oldest in Canada which makes for interesting inspections. The first house I owned and renovated is over 200 years old now, had some re-cycled ( doing this around 1800???) roof boards in it and is still being lived in by the family I bought it from (who bought it back from me).

A lobster fisherman lives 600 feet down the road from me. Beautiful scenery around St. Margaret's Bay. My kids (when small) and I had 6 different swimming holes/white sand beaches within 10 km. Cirque de Soliel is in town now (40 km away). Halifax is more like a big town than an impersonal city. My son's girlfriend (from London, ON) couldn't believe the friendliness ("I was just standing in line and someone started up a conversation!!"). No alarm system on the house.

No! I think I'm going to stay here!!! The quality of life is so cheap!!
Reply With Quote
  #13  
Old 8/16/07, 10:24 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this?

Brian where do u reside, your profile is void of facts?

I have been to PEI and really like the innocence. Something you don't see to much off. Everyone genuinely friendly.

My company logo is of a Mill circa 1849 which I onced owned. I wouldn't move back to the big smoke for all the tea in China.
Reply With Quote
  #14  
Old 8/16/07, 11:01 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this?

Quote:
Originally Posted by rwand1
Brian where do u reside, See above- St. Margaret's Bay....40 km from Halifax

your profile is void of facts?
Something I must have learned from those CAHPI types......just to p_$$ you and Roy!!!

I have been to PEI and really like the innocence. Something you don't see to much off. Everyone genuinely friendly.
We have a chapter meeting there every year in the summer. The golfing is a big draw there now. Vijay Singh and Mike Weir played there a couple of weeks ago.

My company logo is of a Mill circa 1849 which I onced owned. I wouldn't move back to the big smoke for all the tea in China.
I always said if I was going to live in or near a city, it would be San Francisco or Halifax.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 1:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts