I have an air admittance value in the crawl space with the top of the value 2" from the bottom of the floor insulation. Does anyone see an issue with that?

Thanks,
Russell Truluck
Reply With Quote
  #2  
Old 6/4/08, 6:45 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Air admittance values

No. AAV's are OK in a crawlspace or even inside a sink cabinet.

If I see more than one AAV in a home, then there are issues.
Reply With Quote
  #3  
Old 6/4/08, 7:46 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Air admittance values

Quote:
Originally Posted by dvalley
No. AAV's are OK in a crawlspace or even inside a sink cabinet.

If I see more than one AAV in a home, then there are issues.
Agreed.
Reply With Quote
  #4  
Old 6/4/08, 8:13 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Air admittance values

I've never heard of AAV's being allowed in a crawl space. Admittedly, I don't see many AAV's in CA (because they're not allowed by State Standards) but from what I know they're required to be near or above the flood level of the fixture(s) they serve.

It seems to me that an AAV in a crawl space is just asking for trouble. . .

David - why would multiple AAV's be a problem?
Attached Files
File Type: pdf AAV.pdf (96.1 KB, 168 views)



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 6/4/08 at 8:48 PM..
Reply With Quote
  #5  
Old 6/5/08, 1:40 AM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: Air admittance values

If you had an AAV below the level of the trap, what would be the point. Gases are supposed to rise through the system.



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #6  
Old 6/5/08, 2:50 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Air admittance values

Quote:
Originally Posted by jpope
Admittedly, I don't see many AAV's in CA (because they're not allowed by State Standards) but from what I know they're required to be near or above the flood level of the fixture(s) they serve.
Once again we apparently do things differently down here in San Diego. I have whole subdivisions of expensive homes with multiple AAV's in the houses: Rancho Bernardo, Scripps Ranch, 4S Ranch, Del Mar Highlands, Del Mar Heights, Rancho Penasquitos, and probably a few others. The first time I ran into them back in 2001, I called my plumber and he didn't have a problem with them. Then I called two other plumbers and they didn't have a problem with them either. That gave me the concensus that I was looking for.

When I find one under the kitchen sink, I know they will be in the bathrooms and the laundry, and, indeed, they area.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #7  
Old 6/5/08, 8:52 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Air admittance values

Quote:
Originally Posted by jpope
David - why would multiple AAV's be a problem?
They make sewer stacks for that reason.
Reply With Quote
  #8  
Old 6/5/08, 10:53 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Air admittance values

But why would multiple AAV's be a problem?



NACHI 2005 U.S. Member of the Year

Last edited by rray; 6/6/08 at 6:14 AM..
Reply With Quote
  #9  
Old 6/5/08, 11:15 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Air admittance values

Quote:
Originally Posted by rray
Bu why would multiple AAV's be a problem?
Probably not a problem unless there is no main vent stack for the stucture.
They are not a perfect devices or without problems in the long term.

Your AHJ and codes would determine what is allowed in your area.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #10  
Old 6/5/08, 11:21 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Air admittance values

Quote:
Originally Posted by mlarson
Probably not a problem unless there is no main vent stack for the stucture.
Exactly.

Quote:
Originally Posted by mlarson
They are not a perfect devices or without problems in the long term.
As with anything, though, right?

Quote:
Originally Posted by mlarson
Your AHJ and codes would determine what is allowed in your area.
As the AHJ's have already done here.

I find multiple AAV's in the rich areas with McMansions. The reason is because all those ugly vents sticking up through the roof make the roof ugly. So when one has 19 bathrooms and 37 sinks, one really doesn't want 37 doohickeys sticking up through the roof making the roof uglier than it already is.

Fewer doohickeys sticking up through the roof also make it easier for our South-of-the-Border roofing labor to install the roof. That flashing around 37 doohickeys can be soooooooo troublesome.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #11  
Old 6/5/08, 3:00 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Air admittance values

The CPC does not recognize AAV's. As always, local jurisdictions vary. I've seen them in subdivisions as well as in manufactured homes - it usually depends on whether the area is incorporated within the county, having their own building standards. Unincorporated areas will usually be following State Codes.

In most homes (where I've seen AAV's), they've been installed in the attic. Manufactured homes will generally have them at each fixture (that's why I asked), but I can't recall ever seeing one in a crawlspace. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 6/6/08, 5:44 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Air admittance values

Quote:
Originally Posted by rray
Bu why would multiple AAV's be a problem?
I never stated that they are a problem. I stated that there will be issues with multiple AAV's.

If construction is well planned ahead of time, and sewer stacks are considered into the plan, AAV's are not needed because multiple fixtures can be added into a single sewer stack.

Normally I see a single AAV's in manufactured homes (at the kitchen sink) due to the distance from the bathroom to the kitchen. I hardly ever see AAV's in SF homes.
Reply With Quote
  #13  
Old 6/6/08, 6:15 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Air admittance values

Quote:
Originally Posted by dvalley
I stated that there will be issues with multiple AAV's.
So I'll repeat the question, which you quoted:

Quote:
Originally Posted by rray
But why would multiple AAV's be a problem?
Or, in other words, what "issues" would there be with multiple AAV's.

I'm trying to learn something here. Thanks.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #14  
Old 6/6/08, 6:19 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Air admittance values

Quote:
Originally Posted by rray
So I'll repeat the question, which you quoted:


Or, in other words, what "issues" would there be with multiple AAV's.

I'm trying to learn something here. Thanks.
Russel,

Use your head for something other than a hat rack....
Reply With Quote
  #15  
Old 6/6/08, 7:00 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Air admittance values

Quote:
Originally Posted by dvalley
Russel,

Use your head for something other than a hat rack....
That's what I thought. You can't come up with any "issues." That's okay. I did learn something.



NACHI 2005 U.S. Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Emissivity Values from Fluke mkyriacou Thermal Imaging, Infrared Cameras & Energy Audits 5 5/10/08 8:50 PM
Air admittance valves rtruluck Plumbing Inspections 2 12/29/07 4:24 PM
Homeowners are going underwater as loans pass home values jburkeson1 Miscellaneous Discussion for Inspectors 3 11/11/06 8:19 PM
Proper use of an air admittance valve? cceccarelli Plumbing Inspections 5 5/12/06 6:16 PM