Are AAV's allowed with S traps. In this installation the AAV does not have the minimum 4" clearance above the crown of the trap but I was just wondering if they are allowed on S traps in most areas.
Attached Thumbnails
air-admittance-valve-s-trap-p2030139.jpg  
Reply With Quote
Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/5/11, 11:13 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AAV on "S" Trap

Quote:
Originally Posted by kblair1 View Post
Are AAV's allowed with S traps. In this installation the AAV does not have the minimum 4" clearance above the crown of the trap but I was just wondering if they are allowed on S traps in most areas.
Not allowed in Canada unless by some local inspectors.
Reply With Quote
  #3  
Old 2/6/11, 12:48 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: AAV on "S" Trap

The question should be - "are AAV's allowed" - period. The S-trap is wrong, regardless of the vent system used.

Many jurisdictions do not allow AAV's, so you'll have to check with your AHJ. If so, then it should be at a higher elevation under the sink.

That whole drain line configuration is a mess, I'd defer the entire thing for correction.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 2/6/11, 1:08 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: AAV on "S" Trap

Would have been cheaper and easier to do it the right way to begin with!
Reply With Quote
  #5  
Old 2/6/11, 7:17 PM
agallatin agallatin is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Trail BC
Posts: 194
Default Re: AAV on "S" Trap

AAVs are allowed here but only in applications where stacks aren't possible . Such as a sink in a kitchen island , that would be the most likely . Yes the job in the pics is a mess .



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
  #6  
Old 2/6/11, 8:25 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: AAV on "S" Trap

Jeff is right, the s-trap is illegal and the studor vent is only allowed in certain areas. Here in Maine this whole abortion is illegal.
Reply With Quote
  #7  
Old 2/6/11, 10:44 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AAV on "S" Trap

Quote:
Originally Posted by agallatin View Post
AAVs are allowed here but only in applications where stacks aren't possible . Such as a sink in a kitchen island , that would be the most likely . Yes the job in the pics is a mess .
No need to use AAV in an island sink.

http://www.familyhandyman.com/DIY-Pr...an-island-sink
Reply With Quote
  #8  
Old 2/7/11, 5:28 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: AAV on "S" Trap

Brian, help in lieu of suspense to help the guy.

air-admittance-valve-s-trap-island-venting.jpg

Reply With Quote
  #9  
Old 2/7/11, 10:11 PM
James R. Szczesny's Avatar
James R. Szczesny James R. Szczesny is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Seattle,Wa
Posts: 332
Default Re: AAV on "S" Trap

Nice pic Marcel,



J.Szczesny
4 Seasons Home Inspections
Washington State Inspector # 711
800 5th Ave #101-385
Seattle, Wa 98104
(206)391-0285

online @ www.4seasonsinspects.com
email @ info@4seasonsinspects.com
toll free cal @ 866-512-9972

"For the best protection,
get the right inspection"


Reply With Quote
  #10  
Old 2/7/11, 10:47 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AAV on "S" Trap

Quote:
Originally Posted by mcyr View Post
Brian, help in lieu of suspense to help the guy.

Attachment 41916

Didn't the picture from the article come through on your system? If it did then I don't understand your comment.

When you get into the article the picture actually blows up very well!
Reply With Quote
  #11  
Old 2/21/11, 8:42 AM
Gary Mohel Gary Mohel is offline
InterNACHI Member
 
Join Date: Feb 2011
Posts: 2
Default Re: AAV on "S" Trap

Can an AAV be used in a crawl space on a pier and beam house?
Reply With Quote
  #12  
Old 3/6/11, 2:18 AM
Dustin Racine Dustin Racine is offline
New User
 
Join Date: Mar 2011
Posts: 4
Please Note: Dustin Racine is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: AAV on "S" Trap

here (alberta) u can only use aav's or "cheater vents" 1)on a island, 2)where theres a serious chance of freeze up on a vent terminating to open air or 3) where installing a true vent is not practible (assuming if u had to start opening walls to tie vent in above "flood level rim" of fixture on above floor). Not word for word out of the code, but thats my interpretation.Also, cheater vents should be piped as high as possible under cabinets for best results, "T" fittings are not allowed in drainage applications, and as u said there's also a "s-trap" That drain should be ripped out and redone.
Reply With Quote
  #13  
Old 3/9/11, 6:37 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: AAV on "S" Trap

Quote:
Originally Posted by Brian A. MacNeish View Post
Not allowed in Canada unless by some local inspectors.

Brian
What province are you in. It's my understanding that they are allowed in Ontario...saw our friend Mike Holmes install one on one of his shows.
Reply With Quote
Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 3/9/11, 6:43 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: AAV on "S" Trap

Occupation: Plumber
Years Experience: since '89 as a journeyman
Location: Rankin Inlet, Nunavut, Canada
Join Date: Sep 2008
Posts: 1,468
Nominated 21 Times in 11 Posts
Thread of the Week Award(s): 3
i can't speak for the ontario code but while it hasn't been approved for use in canada, stores are allowed to sell them.

as long as it is installed as close as possible to the trap, accessible, and as high as possible for the fixture it serves (ie; under the counter), you shouldn't have any problems.

if it's installed properly, when the water is discharged or drained from the fixture you should be able to hear it sucking in air.

Another post says;


They are legal in Canada, but with restrictions. The main one being the vent must be of the "approved type" ie. Studor AAV, Oatey SureVent, etc.


Section 2.5.9 of the National Plumbing Code of Canada covers this.

Here's the entry from the code book (I love my scanner!)



2.5.9. Air Admittance Valves
(See A-2.2.10.16.(1) in Appendix A.)

2.5.9.1. Air Admittance Valve as a Vent Terminal

1)
Individual vents
may terminate with a connection to an air admittance valve as provided in Articles 2.5.9.2. and 2.5.9.3. (See also Sentence 2.2.10.16.(1).)

2.5.9.2. Air Admittance Valves


1)
Air admittance valves
shall only be used to vent
a)fixtures located in island counters,
b)fixtures that may be affected by frost closure of the vent due to local climatic conditions,
c)fixtures in one- and two-family dwellings undergoing renovation, or
d)installations where connection to a vent may not be practical.

2)
Air admittance valves shall be located
a)not less than 100 mm above the horizontal branch drain or fixture drain being vented,
b)within the maximum developed length permitted for the vent, and
c)not less than 150 mm above insulation materials.

2.5.9.3. Installation Conditions


1)
Air admittance valves
shall not be installed in supply or return air plenums, or in locations where they may be exposed to freezing temperatures.

2)
Air admittance valves shall be installed in accordance with the manufacturer`s installation instructions.

3)
Air admittance valves shall be rated for the size of vent pipe to which they are connected.

4) Installed
air admittance valves shall be
a)accessible, and
b)located in a space that allows air to enter the valve.

5) Every drainage system shall have one vent that terminates to the outdoors in conformance with Sentence 2.5.6.2.(1).
Reply With Quote
  #15  
Old 3/9/11, 7:03 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: AAV on "S" Trap

Looks like they have to be installed in the horizontal part of the drain also, pretty much eliminating them from use on an S-trap.

7.5.9.2. Air Admittance Valves


(1)
Air admittance valves shall only be used to vent,
(a)

fixtures in buildings undergoing renovation, and
(b) installations where connection to a

vent may not be practical.
(2)


The air admittance valves shall be located,
(a) above the

flood level rim of the fixture it serves,
(b) within the maximum

developed length permitted for the vent,
(c) not less than 150 mm above insulation materials, and
(d) installed in a location not subject to back pressure.
(3)


Air admittance valves shall,
(a) only vent

fixtures located on the same storey, and
(b) be connected to the horizontal

fixture drain.


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Condensation Drain line question acassady Inspecting HVAC Systems 25 2/26/12 11:40 AM
Trap weird and crown weir dpant Plumbing Inspections 22 1/24/11 11:41 PM
Trap Primer Question jallingham Plumbing Inspections 5 2/15/08 7:36 PM
Negative angle trap arm issue rlind Plumbing Inspections 4 4/14/06 11:00 PM
Grease Trap / Drum Trap David White Plumbing Inspections 1 2/7/06 5:41 PM


All times are GMT -4. The time now is 12:15 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts