Exclamation Alert! New rule impacting appliance connectors!

Here's something else new in the 2009 IRC.

"G2411.1.1. [and 310.1.1 in the Fuel Gas Code]: CSST. Corrugated Stainless Steel Tubing (CSST) gas piping systems shall be bonded to the electrical service grounding electrode system at the point where the gas enters the building. The bonding jumper shall not be smaller than 6 AWG copper wire or equivalent."

That's now a code requirement, not just a recommendation from a few manufacturer's of CSST involved in a past lawsuit.

Here's the impact: An appliance connector IS classified as CSST. Therefore, just one appliance connector in a system using other materials (black iron, copper, etc.) for gas distribution will require the system to be bonded from the gas meter to the GEC or Service Entrance Panel ground bus.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 9/17/10 at 12:27 AM..
Reply With Quote
Need a home inspection in Nevada? Check out InterNACHI's listing of Nevada certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/16/10, 11:27 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Alert! New rule impacting appliance connectors!

thanks for the info Joe!

Looks like it could get expensive when the gas meter and GEC are on opposite ends of the house. Even harder when its on a slab.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 9/17/10, 12:49 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Alert! New rule impacting appliance connectors!

Quote:
Originally Posted by jfunderburk View Post
Here's the impact: An appliance connector IS classified as CSST. Therefore, just one appliance connector in a system using other materials (black iron, copper, etc.) for gas distribution will require the system to be bonded from the gas meter to the GEC or Service Entrance Panel ground bus.
The system already requires bonding per the NEC. How does this change anything?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 9/17/10, 7:25 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Alert! New rule impacting appliance connectors!

I'm not sure what NEC code you're talking about. Are you're talking about bonding the system in general, disregarding CSST? If so, that requirement is excepted if there is an appliance that is grounded using the appliance electrical supply. However, the presence of just one appliance connector would require a separate system ground from the meter, like I described above.

I've never before called out the need for a separate system bond if an appliance connector is present.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 9/17/10, 10:52 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Alert! New rule impacting appliance connectors!

If the gas piping of the residence is metallic, it is required to be bonded to the GES - same as the water piping.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 9/17/10, 6:43 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Alert! New rule impacting appliance connectors!

Quote:
Originally Posted by jpope View Post
If the gas piping of the residence is metallic, it is required to be bonded to the GES - same as the water piping.
Starting from the gas meter? That what the CSST rule states.

If this CSST rule requires an additional ground, that could be a burden if its a slab home and the gas meter and EGC are on opposites sides of the home.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 9/18/10, 10:31 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Alert! New rule impacting appliance connectors!

Bonding is almost always accomplished at the meter in CA, regardless of where the electrical service is located.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 9/18/10, 10:41 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Alert! New rule impacting appliance connectors!

They were allowing the little green wire equipment ground inside the furnace cabinets to act as the entire gas pipe bond around here since the pipe is bonded to the furnace cabinet.

Then in late 2007 many areas started requiring "additional bonding" which had to be the large conductor at the main pipe bonded to the GEC or the service panel neutral/ground bus if CSST distribution piping was present. This was a new item for electricians but now its in the 2009 Fuel Gas code.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #9  
Old 9/18/10, 12:14 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: Alert! New rule impacting appliance connectors!

Quote:
G2411.1.1. [and 310.1.1 in the Fuel Gas Code]: CSST. Corrugated Stainless Steel Tubing (CSST) gas piping systems shall be bonded to the electrical service grounding electrode system at the point where the gas enters the building.
Note the bolded/underlined portion.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #10  
Old 9/18/10, 1:17 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Alert! New rule impacting appliance connectors!

If you do this in NYC or Westchester County, or Rockland County... The gas utility will shut down the service.

Consolidated Edison Companies are the gas and electric utility for many counties, and are the AHJ.

If this practice is found they will red flag the dwelling and shut both services off immediately.

They will require a licensed plumber and electrician perform whatever modifications are necessary, ad will require their presence on site prior to re-energizing the site, and prior to turning on the gas.
Reply With Quote
  #11  
Old 9/18/10, 3:00 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Alert! New rule impacting appliance connectors!

Quote:
Originally Posted by gromicko View Post
Note the bolded/underlined portion.
I guess that is the most notable difference in the requirement, although this is generally how it's done as a matter of course in CA, whether there is CSST or not.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 9/18/10, 4:24 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Alert! New rule impacting appliance connectors!

Quote:
Originally Posted by jfarsetta View Post
If you do this in NYC or Westchester County, or Rockland County... The gas utility will shut down the service.

Consolidated Edison Companies are the gas and electric utility for many counties, and are the AHJ.

If this practice is found they will red flag the dwelling and shut both services off immediately.

They will require a licensed plumber and electrician perform whatever modifications are necessary, ad will require their presence on site prior to re-energizing the site, and prior to turning on the gas.

Sounds like those areas use metallic piping from the street to the house.
They do not want any chance of voltage or any current flow on their main pipes and feeding from house to house etc. So it is basically pretty well grounded to the earth already without actually using an electrical system and adding in the chance for wiring errors or massive malfunctions.

Around here the service lines are plastic unless an older home in some areas.
They actually install a tracer wire next to the plastic so they can locate it later.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Hook 2 appliance connectors together? jfunderburk Inspecting HVAC Systems 6 9/8/07 3:24 PM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 5:22 PM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 7:47 AM


All times are GMT -4. The time now is 12:15 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts