Reply
 
LinkBack Thread Tools
  #1  
Old 7/12/08, 7:21 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default And the TPR drain ends...

WH on 2nd floor.
TRP drain terminates above floor drain in pic 2.
In storage room in 1/2 bath downstairs.
Attached Thumbnails
and-tpr-drain-ends-tpr1-400.jpg   and-tpr-drain-ends-100_1571-400.jpg  
Reply With Quote
  #2  
Old 7/12/08, 9:48 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,564
Default Re: And the TPR drain ends...

hhhhhmmmmmmmmmmmmmmmmm



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #3  
Old 7/12/08, 10:23 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: And the TPR drain ends...

Quote:
Originally Posted by jmckee
hhhhhmmmmmmmmmmmmmmmmm
What?...you don't know the words???
Reply With Quote
  #4  
Old 7/12/08, 10:29 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,564
Default Re: And the TPR drain ends...

Quote:
Originally Posted by jwilliams4
What?...you don't know the words???
speechless i guess Jae....what do You think about that picture....????



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #5  
Old 7/12/08, 10:32 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: And the TPR drain ends...

Quote:
Originally Posted by rmaday
WH on 2nd floor.
TRP drain terminates above floor drain in pic 2.
In storage room in 1/2 bath downstairs.
Looks good too me Rick--------
Reply With Quote
  #6  
Old 7/12/08, 10:59 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: And the TPR drain ends...

Quote:
Originally Posted by dduffy
Looks good too me Rick--------
Curious as to why they would run it all the way through the walls and down another floor when there is a floor drain in the room with the WH?
Reply With Quote
  #7  
Old 7/13/08, 1:09 AM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: And the TPR drain ends...

Because with the pressure from a TPR opening up and a grate on the Flr Drn, well Water Water everywhere.
Looks okay to me too.



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #8  
Old 7/13/08, 1:30 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: And the TPR drain ends...

Quote:
Originally Posted by jgilleland
Because with the pressure from a TPR opening up and a grate on the Flr Drn, well Water Water everywhere.
Looks okay to me too.
Thanks for the responses.

I guess my biggest concern is that they wouldn't know (couldn't see) if it was discharging.

Also, don't know if it makes a difference but there was no grate on the upstaird Flr Drain.
Reply With Quote
  #9  
Old 7/13/08, 2:06 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: And the TPR drain ends...

Bold is what concerns me

Quote:
Originally Posted by TPR mini-course
The following recommendations regarding TPR discharge pipes are based largely on the 2006 International Residential Code P2803.61 as well as other building and plumbing codes.
The discharge piping serving a TPR valve should:
  1. Be constructed of an approved material such as CPVC, copper, polyethylene, galvanized steel, polybutylene, polypropylene, or stainless steel.
  2. Not be smaller than the diameter of the outlet of the valve it serves (usually no smaller than 3/4").
  3. Shall not reduce in size from the valve to the air gap (point of discharge).
  4. Be as short and as straight as possible so as to avoid undue stress on the valve.
  5. Be installed so as to drain by flow of gravity.
  6. Not be trapped since standing water may become contaminated and backflow into the potable water.
  7. Discharge to the floor, to an indirect waste receptor, or to the outdoors.
  8. Not be directly connected to the drainage system to prevent backflow of potentially contaminating the potable water.
  9. Discharge through a visible air gap (atmosphere) in the same room as the water heater.
  10. Be first piped to an indirect waste receptor through an air gap located in a heated area when discharging to the outdoors in areas subject to freezing, since freezing water could block the pipe.
  11. Not terminate more than 6 inches (152 mm) above the floor or waste receptor.
  12. Discharge in a manner that could not cause scalding.
  13. Discharge in a manner that could not cause structural or property damage.
  14. Discharge to a termination point that is readily observable by occupants because discharge indicates that something is wrong.
  15. Be piped independent of other equipment drains, water heater pans, or relief valve discharge piping to the point of discharge.
  16. Not have valves anywhere.
  17. Not have tee fittings.
  18. Not have a threaded connection at the end of the pipe so as to avoid capping.
Reply With Quote
  #10  
Old 7/13/08, 6:33 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: And the TPR drain ends...

I see these type of PTR valve installations in Condos.

I simply explain to my clients, why I like to see the PTR termination and note that the PTR valve can not be monitored.

Definitely make a note about the elbows in the PTR extension pipes.
Reply With Quote
  #11  
Old 7/13/08, 2:33 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: And the TPR drain ends...

Rick yours is not as cute as mine this one terminated within the shower stall just in case one needed an extra boost of good hot water Multiple problems with this one installed by the local Drunk. Installed within an open area of the bathroom PVC on the relief valve into the shower stall, copper whip to the control valve no manual shut off at the appliance and single wall flue vent into the attic with no clearance to combustibles</IMG></IMG></IMG>
Attached Thumbnails
and-tpr-drain-ends-111-s.-elm-newkirk-7-10-08-francis-roady-040.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 7/13/08, 9:10 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: And the TPR drain ends...

Quote:
Originally Posted by rmaday
Bold is what concerns me
4. Be as short and as straight as possible so as to avoid undue stress on the valve.
9. Discharge through a visible air gap (atmosphere) in the same room as the water heater.
14. Discharge to a termination point that is readily observable by occupants because discharge indicates that something is wrong.

I would love it if that were the case here, but most, if not all, manufacturers approve of 4-6 90° angles. I guess that's "as straight as possible."
Rarely in new construction do I see the pipe terminating in the same room as the water heater. They now route them outside, which I don't like because of #14. Nonetheless, every AHJ in every city here approves of them being terminated outside.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #13  
Old 7/13/08, 9:59 PM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: And the TPR drain ends...

Typical condo weirdness...
At one of my recent condo inspections in a well known large chicago building ( that looks like a setr of corn cobbs), I found the small tank water heaters TPR discharge was a copper flex ( kinked too) that was routed up to disharge into the small ss kitchen sink through what looked like the soap dispenser spigot. Of course i called it out as extremely dangerous and amateurish installation. It appears that every unit in this massive building that was converted was done this way.

I alerted the city plumbing inspectors office. They were pretty shocked and glad i called.




Joseph Tribuzio 708 453 8447
Tribuzio Home Inspection Services

CHICAGOLAND, ILLINOIS
www.thishomeinspector.com

ID# NACHI07062507

IL Lic#450.003128

Radon lic# RNIT2008216
Home Inspector Pro Software

HIP Web Hosting


Reply With Quote
  #14  
Old 7/13/08, 10:45 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,608
Default Re: And the TPR drain ends...

Quote:
Originally Posted by jtribuzio
Typical condo weirdness...
At one of my recent condo inspections in a well known large chicago building ( that looks like a setr of corn cobbs), I found the small tank water heaters TPR discharge was a copper flex ( kinked too) that was routed up to disharge into the small ss kitchen sink through what looked like the soap dispenser spigot. Of course i called it out as extremely dangerous and amateurish installation. It appears that every unit in this massive building that was converted was done this way.

I alerted the city plumbing inspectors office. They were pretty shocked and glad i called.
I thought the plumbers union were the big boys up there.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #15  
Old 7/13/08, 10:57 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: And the TPR drain ends...

Quote:
Originally Posted by jtribuzio
It appears that every unit in this massive building that was converted was done this way.
Send each and every one of them an INVOICE

Payable to:
ADAIR INSPECTION
1733 GOLIAD DRIVE
GARLAND, TX 75042-4238




ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 10:24 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts