sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default anything wrong with this TPRV

Do you see anything wrong here?

Thanks,
Attached Thumbnails
anything-wrong-temperature-pressure-relief-valve-img_3873.jpg   anything-wrong-temperature-pressure-relief-valve-img_3875.jpg   anything-wrong-temperature-pressure-relief-valve-img_3876.jpg  



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #2  
Old 7/20/08, 4:24 PM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,707
Default Re: anything wrong with this TPRV

No air gap device, and where does it end up?
Reply With Quote
  #3  
Old 7/20/08, 8:01 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,048
Default Re: anything wrong with this TPRV

PVC is not allowed for use as relief piping, nor is it allowed for distribution within the building.

Also, the termination should be visible, unless this is a mobile/manufactured home.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 7/20/08, 8:12 PM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: anything wrong with this TPRV

What is that fitting going in to the TPRV? To many elbows (specially for plastic). Unless that is CPVC (I can't tell Jeff), it is installed with the wrong material. Home owner can't see when the valve is blowing off. There are no shut offs at all, should at least isolate heater on the cold side.
Just an aside, wiring needs an electrician (it looks like it is taped into the wall).
Just put down that "Water Heater needs professional assistance".



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #5  
Old 7/20/08, 8:31 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: anything wrong with this TPRV

Quote:
Originally Posted by jpope
PVC is not allowed for use as relief piping, nor is it allowed for distribution within the building.

Also, the termination should be visible, unless this is a mobile/manufactured home.
Hi Jeff,

Are you assuming it is PVC due to the purple primer used or color of the pipe? If it were CPVC would they have used a different primer? I have some purple primer in my garage and it is acceptable for CPVC use and doesn't say anything about not for potable water?

I think this may be a good catch Jeff as the rest of the plumbing is CPVC and doesn't have the purple primer. I may have to revisit before I issue the report.

Yes, this is manufactured housing.

Further input is appreciated.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #6  
Old 7/20/08, 8:49 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,048
Default Re: anything wrong with this TPRV

The pipe color looks too white for CPVC, which usually has a yellowish tint to it.

The markings are visible, but I didn't zoom in to identify it.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 7/20/08, 9:20 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: anything wrong with this TPRV

I was wondering about your thoughts on the color, as soon as I read your post and looked at the colors I thought the same thing.

I have tried to zoom in and read, but am unable to, the lettering is too blurry.

I guess I will be going back tomorrow. Better that then finding out the hardway down the road.

Thanks,



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #8  
Old 7/20/08, 10:50 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: anything wrong with this TPRV

Besides the PVC question, and the lack of a water shut-off, you could suggest a drain pan. That way, the discharge pipe could go straight down into the pan, only one elbow.
The electrical supply ought to be protected with flex conduit, although it looks like the tank is usually covered by a wood panel.
Earthquake straps are probably redundant, but we watch for them out here.
Reply With Quote
  #9  
Old 7/20/08, 10:59 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,608
Default Re: anything wrong with this TPRV

Quote:
Originally Posted by sfalvey
I was wondering about your thoughts on the color, as soon as I read your post and looked at the colors I thought the same thing.

I have tried to zoom in and read, but am unable to, the lettering is too blurry.

I guess I will be going back tomorrow. Better that then finding out the hardway down the road.

Thanks,
I think you have enough other defects to call out to save you a trip back.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #10  
Old 7/21/08, 5:36 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: anything wrong with this TPRV

I'm not sure I'd make the return trip either.

Fittings attached to copper flex have orange CPVC glue none of the others do and I've not seen CPVC unions where orange glue was not visible, unless compression unions were used.

I'd also question compatability of piping and glues used, I don't recall where you can join CPVC and PVC together properly without a compression fitting, no glue involved. Not that this set up would be approved.

Enough items have been identified by others that this requires repairs by an electrician and plumber...if they don't want to do their jobs properly, oh well

jmo



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #11  
Old 7/21/08, 6:07 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: anything wrong with this TPRV

This may help.

http://www.nibco.com/assets/cpvc_manual.pdf Page 6

Marcel
Reply With Quote
  #12  
Old 7/21/08, 8:05 AM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is online now
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: anything wrong with this TPRV

I noticed it was a Manufactured home right away, and in all honesty, almost all the low to mid end homes in my area are installed this way. I saw one installed 2 years ago, using the same TPRV setup. Usually they drill a hole in the floor and drain it into the crawl space. Not espicially desiarable, but considering the chipboard flooring they use, a small drip becomes a structural issue.

This is all too common in a MFG home.
Reply With Quote
  #13  
Old 7/21/08, 6:35 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: anything wrong with this TPRV

Thanks for all the input.

I felt obligated to report things as they are so I made the trip back out, fortunately I got a call this morning for a Draw inspection that was only 10 minutes away.

The plastic lines are CVPC, I think the flash on the camera whitened the plastic for the photo. CMA, I feel better now and can be confident about my report.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #14  
Old 7/21/08, 6:51 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: anything wrong with this TPRV

Quote:
Originally Posted by sfalvey
Do you see anything wrong here?

Thanks,
Does the piping run to the exterior? Or does it terminate under the trailer?
Reply With Quote
  #15  
Old 7/21/08, 9:21 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: anything wrong with this TPRV

It does terminate under the trailer.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Free Books And Articles For Electrical jtedesco1 Electrical Inspections 14 1/6/08 6:45 PM
TPRV questions Rick Maday Plumbing Inspections 1 8/23/07 12:51 AM
TPRV line and condensate line marriage ccarrington Plumbing Inspections 3 4/29/06 7:59 AM


All times are GMT -4. The time now is 10:25 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts