Default Appliance connectors

Photo taken from crawl space. Anyone see anything wrong? Piping is feeding the gas logs.

appliance-connectors-012910-083.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 1/29/10 at 11:41 PM..
Reply With Quote
Need a home inspection in Florida? Check out InterNACHI's listing of Florida certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/29/10, 10:53 PM
James A. Levy's Avatar
James A. Levy James A. Levy is online now
InterNACHI Member
 
Join Date: Dec 2008
Location: Medford,NJ
Posts: 2,772
Default Re: Appliance connector thru the floor

Quote:
Originally Posted by jfunderburk View Post
Photo taken from crawl space. Anyone see anything wrong? Piping is feeding the gas logs.

Attachment 34602
Other than flex lines are not to pass through floor levels, no its cool.
Reply With Quote
  #3  
Old 1/29/10, 10:55 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Appliance connector thru the floor

Is the gas line laying across the cooper pipe?



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #4  
Old 1/29/10, 10:57 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Appliance connector thru the floor

Flex connectors for gas fireplaces are usually allowed to pass through floors or walls. I had a similar situation last year and found the code for it somewhere, but can't find it now. I'll look again in the morning.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #5  
Old 1/29/10, 11:11 PM
James A. Levy's Avatar
James A. Levy James A. Levy is online now
InterNACHI Member
 
Join Date: Dec 2008
Location: Medford,NJ
Posts: 2,772
Default Re: Appliance connector thru the floor

Quote:
Originally Posted by bsmith View Post
Flex connectors for gas fireplaces are usually allowed to pass through floors or walls. I had a similar situation last year and found the code for it somewhere, but can't find it now. I'll look again in the morning.
I have never heard of that. Walls yes floors no. I would be interested in knowing.
Reply With Quote
  #6  
Old 1/29/10, 11:13 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Appliance connector thru the floor

This is from instructions for the common Dormont piping:

4. DO NOT install the gas connector so that it is concealed within or runs through any wall,floor or other partition. The gas outlet must be in the same room as the appliance. This is so it is visible for periodic inspection.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #7  
Old 1/29/10, 11:15 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Appliance connector thru the floor

How long is the connector? Where is the shut off?



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #8  
Old 1/29/10, 11:19 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Appliance connector thru the floor

It was probably 6 feet long. The shutoff was beneath the firebox of the manufactured fireplace.

Here's what I said:

"A gas appliance connector passes through a floor; a practice which the manufacturer prohibits. The manufacturers of these devices state: "Do not conceal connector or run connector through enclosed outdoor BBQ pits, walls, partitions, floors or appliance panels." Service by a licensed plumbing or HVAC contractor is recommended."

That quote came from a connector I picked up at Lowes a long time ago and documented the warning.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 1/29/10, 11:23 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Appliance connector thru the floor

Anyone think this is OK?

appliance-connectors-011410-124.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 1/29/10, 11:34 PM
rarmacost rarmacost is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Conroe, TX
Posts: 53
Default Re: Appliance connector thru the floor

M2202.3 of the IRC 2006 allows it when rigid connections are impractical and to reduce jarring and vibration. labeled in accordance with UL 539.
From the picture I don't see anything impractical as to why a rigid line coudn't be installed the only other thing not seen is the absence of a dripleg.
Another question is were the line passes through the wall, should it be sleeved or insulated



Robert Armacost
TREC # 10230
Armacost Home Inspections
Reply With Quote
  #11  
Old 1/29/10, 11:39 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Appliance connector thru the floor

Quote:
Originally Posted by rarmacost View Post
M2202.3 of the IRC 2006 allows it when rigid connections are impractical and to reduce jarring and vibration. labeled in accordance with UL 539.
From the picture I don't see anything impractical as to why a rigid line coudn't be installed the only other thing not seen is the absence of a dripleg.
Another question is were the line passes through the wall, should it be sleeved or insulated
Nothing in the standard you mention allows an appliance connector to ever penetrate an HVAC cabinet, floor, wall, etc. because the manufacturers specifically prohibit that practice.

"M2202.3 Flexible connectors. Flexible metal hose used
where rigid connections are impractical or to reduce the effect
of jarring and vibration shall be listed and labeled in accordance
with UL 536 and shall be installed in compliance with its
label and the manufacturer’s installation instructions. Connectors
made from combustible materials shall not be used inside
of buildings or above ground outside of buildings."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 1/29/10 at 11:59 PM..
Reply With Quote
  #12  
Old 1/29/10, 11:42 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Appliance connector thru the floor

Quote:
Originally Posted by bhartley View Post
Is the gas line laying across the cooper pipe?
Looks like it. I didn't catch that. Aren't those connectors stainless? Would that present a corrosion problem???



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 1/29/10, 11:57 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Appliance connectors

Technically it would but the amount depends on the environment. You already said it was an improper installation so it is a moot point as far as the report goes.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Need a home inspection in Florida? Check out InterNACHI's listing of Florida certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/29/10, 11:57 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Appliance connector thru the floor

Quote:
Originally Posted by bsmith View Post
Flex connectors for gas fireplaces are usually allowed to pass through floors or walls. I had a similar situation last year and found the code for it somewhere, but can't find it now. I'll look again in the morning.
I'll be shocked if you find a code that says it's OK to violate the manufacturers' installation instructions, which prohibit that practice.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #15  
Old 1/29/10, 11:59 PM
rarmacost rarmacost is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Conroe, TX
Posts: 53
Default Re: Appliance connectors

I wasn't refurring to the hvac cabinet, by the time I got my first post off you asked another question. I need to type faster



Robert Armacost
TREC # 10230
Armacost Home Inspections
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Max load allowed on 2x2 ledger bking Structural Inspections 4 12/23/07 2:05 PM
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM
Moisture control for slab on grade in protecting floor finishes mcyr General Inspection Discussion 2 8/13/07 7:53 PM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 7:47 AM


All times are GMT -4. The time now is 12:18 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts