  #16  
Old 1/30/10, 12:01 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Appliance connector thru the floor

Quote:
Originally Posted by rarmacost View Post
Another question is were the line passes through the wall, should it be sleeved or insulated
It SHOULDN'T pass through a wall or floor.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Need a home inspection in Connecticut? Check out InterNACHI's listing of Connecticut certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 1/30/10, 1:40 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Appliance connectors

No one mentioned lack of a drip leg in the first one.
No shutoff either.
Reply With Quote
  #18  
Old 1/30/10, 1:43 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Appliance connectors

Why is the flex coming off a regulator in the second one?
Reply With Quote
  #19  
Old 1/30/10, 1:43 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Appliance connectors

Quote:
Originally Posted by belliott View Post
No one mentioned lack of a drip leg in the first one.
No shutoff either.
Bob, I mentioned somewhere that the shutoff was beneath the fireplace, in the family room, where it ought to be.

Regarding drip legs, the gas companies around here do not require it on residential.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #20  
Old 1/30/10, 1:52 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Appliance connectors

Quote:
Originally Posted by jfunderburk View Post
Bob, I mentioned somewhere that the shutoff was beneath the fireplace, in the family room, where it ought to be.

Regarding drip legs, the gas companies around here do not require it on residential.
Yeah saw the shutoff comment after ,but is there a individual shutoff for that branch before the flex?

I think that is required .

That is not csst and the flex may need to be changed.
Reply With Quote
  #21  
Old 1/30/10, 10:21 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Appliance connectors

Manufacturers instructions should always supercede local codes.

IRC - G2422.1.2 (411.1.2) Appliance fuel connectors......shall not be concealed within, or extended through, walls, floors, partitions, ceilings or household appliances........
Exception: fireplace inserts factory equipped with grommets, sleeves or other means of protection in accordance with the listing of the appliance.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #22  
Old 1/30/10, 10:59 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Appliance connectors

Quote:
Originally Posted by belliott View Post
Yeah saw the shutoff comment after ,but is there a individual shutoff for that branch before the flex?

I think that is required .

That is not csst and the flex may need to be changed.
CSST would be the proper fix IMO. There was no shutoff prior to the connector and I'm not aware of the need for one. The code that sticks in my mind requires a shut-off in the same room and within 6 feet of the appliance.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #23  
Old 1/30/10, 7:10 PM
Robert W. Jude's Avatar
Robert W. Jude Robert W. Jude is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: Lafayette, IN
Posts: 2,084
Default Re: Appliance connectors

so a black iron pipe through the floor, and then a gas connector would make it ok? sounds like your statement doesnt allow any connections...
Reply With Quote
  #24  
Old 1/30/10, 8:26 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Appliance connectors

Quote:
Originally Posted by rjude View Post
so a black iron pipe through the floor, and then a gas connector would make it ok? sounds like your statement doesnt allow any connections...
The usual method is copper tubing or CSST run through the floor.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #25  
Old 1/30/10, 10:41 PM
Robert W. Jude's Avatar
Robert W. Jude Robert W. Jude is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: Lafayette, IN
Posts: 2,084
Default Re: Appliance connectors

(a) All pipe used for the installation, extension,
alteration, and/or repair of any gas piping shall be
standard weight wrought iron or steel, yellow brass
(containing not more than 75% copper), or internally
tinned or equivalently treated copper of iron pipe size.

from the uniform plumbing code... not sure if copper tubing is sufficient material
Reply With Quote
  #26  
Old 1/30/10, 10:50 PM
Robert W. Jude's Avatar
Robert W. Jude Robert W. Jude is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: Lafayette, IN
Posts: 2,084
Default Re: Appliance connectors

Copper pipe, or tubing is NEVER ALLOWED BY CODE IN THE US FOR NATURAL GAS DISTRIBUTION! There are various reasons for this which I'm not going to even bother getting into because they are irrelevant. Bottom line is copper is NEVER ALLOWED BY CODE IN THE US FOR NATURAL GAS DISTRIBUTION!
It is very common to see copper tubing used in rural areas for propane gas distribution. This is allowed. Propane and natural gas are two different gasses.

from finishing.com
Reply With Quote
  #27  
Old 1/30/10, 11:14 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Appliance connectors

Quote:
Originally Posted by rjude View Post
Copper pipe, or tubing is NEVER ALLOWED BY CODE IN THE US FOR NATURAL GAS DISTRIBUTION! There are various reasons for this which I'm not going to even bother getting into because they are irrelevant. Bottom line is copper is NEVER ALLOWED BY CODE IN THE US FOR NATURAL GAS DISTRIBUTION!
It is very common to see copper tubing used in rural areas for propane gas distribution. This is allowed. Propane and natural gas are two different gasses.

from finishing.com
Actually the chemical additive that corrodes copper is not used anymore.(been debated here many times).
Reply With Quote
  #28  
Old 1/31/10, 7:43 AM
Robert W. Jude's Avatar
Robert W. Jude Robert W. Jude is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: Lafayette, IN
Posts: 2,084
Default Re: Appliance connectors

thanks Bob
Reply With Quote
Need a home inspection in Connecticut? Check out InterNACHI's listing of Connecticut certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #29  
Old 1/31/10, 9:38 AM
Robert W. Jude's Avatar
Robert W. Jude Robert W. Jude is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: Lafayette, IN
Posts: 2,084
Default Re: Appliance connectors

what exactly do you define as a "connector" any flex hose?
Attached Thumbnails
appliance-connectors-copper-tube-heat-exchanger-online-training-ben-gromicko-2.jpg  
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Max load allowed on 2x2 ledger bking Structural Inspections 4 12/23/07 2:05 PM
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM
Moisture control for slab on grade in protecting floor finishes mcyr General Inspection Discussion 2 8/13/07 7:53 PM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 7:47 AM


All times are GMT -4. The time now is 12:18 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts