Default Attic Plumbing

I have never seen water supply lines routed through an attic. Looking for opinions from any inspector who has encountered attic plumbing. Keep in mind the cold environment for the Maryland area where this home is located. Yes, there is a heating element for the cold water side and as you can see foam insulation. Of course, the heating element could fail.



attic-plumbing-barclay-098-medium-.jpg.jpg
Views:	207
Size:	46.9 KB
ID:	26115

attic-plumbing-barclay-096-medium-.jpg.jpg
Views:	229
Size:	84.4 KB
ID:	26116

attic-plumbing-barclay-105-medium-.jpg.jpg
Views:	192
Size:	83.2 KB
ID:	26117




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #2  
Old 1/10/09, 1:36 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Attic Plumbing

Attic-routed plumbing is very common. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 1/10/09, 1:44 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: Attic Plumbing

Even in cold weather climates?




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #4  
Old 1/10/09, 2:00 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Attic Plumbing

Quote:
Originally Posted by jevans View Post
Even in cold weather climates?
No, that Pope fella forgets he lives in California.

That metal braided heat cable has me wondering if that is a legitimate install for that product.

Any tags indicating who the manufacture is?



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #5  
Old 1/10/09, 2:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Attic Plumbing

Quote:
Originally Posted by mlarson View Post
No, that Pope fella forgets he lives in California.
True dat.

How do you repipe in colder climates (assuming no basement and no crawl space)?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 1/10/09, 2:05 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: Attic Plumbing

Michael,
Did not notice a tag, the thermostat is Honeywell. I think the plumbing may have been re-routed from the original slab location. You can see the slab with abandoned copper & poly lines in the photos posted in the Structural Section yesterday. It all seems to be tied together.




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #7  
Old 1/10/09, 2:06 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Attic Plumbing

Quote:
Originally Posted by jpope View Post
True dat.

How do you repipe in colder climates (assuming no basement and no crwal space)?
In the attic but below the layer of insulation and no pipe insulation.
The insulation traps the heat from below and warms the pipe.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #8  
Old 1/10/09, 2:08 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: Attic Plumbing

Why no pipe insulation?




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #9  
Old 1/10/09, 2:13 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Attic Plumbing

Quote:
Originally Posted by jevans View Post
Why no pipe insulation?
It is not needed and you want the pipe exposed to the warmest temp just above the interior ceiling materials.

Even if you have to run the pipe perpendicular to the joists or truss bottom chord, all you have to do is have the insulation go up and over the pipe with no insulation below it.

Of course this is problematic with any blown in insulation systems and would require a open sided half box above the pipe. You need to trap the warm from below for it to work.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #10  
Old 1/10/09, 2:18 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: Attic Plumbing

Thanks for the information. I spoke with a local retired inspector who was in the business for 21 years, and he does not recall ever seeing water supplies in an attic. But, there may have been occasions when the plumbing was concealed below the insulation as you suggested.




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #11  
Old 1/10/09, 3:21 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Attic Plumbing

A prudent man might point out that there is no freeze alarm or any other warning device that would warn of heat tape failure. Heat tapes do have a lifespan, but it's unclear to me what that might be. I replace them from time to time, typically under mobile homes, but normally only following a pipe failure. There are commercially available freeze alarms with a probe you stick under the Armaflex. An extended power failure would also put the pipework at risk for freezing if the home was not equipped with a generator or provisions to connect a portable generator. This might be something worthwhile to point out.
Reply With Quote
  #12  
Old 1/12/09, 1:16 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: Attic Plumbing

Update. According to the local plumbing inspector, this installation is not allowed. As mentioned in this thread, the county may possibly allow attic plumbing if placed above the ceiling and covered with adequate insulation.




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #13  
Old 1/12/09, 1:39 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Attic Plumbing

Pretty common to have water heaters in attics here. This is what I say, depending on whether or not insulation is provided.

"The visible portions of the water pipes in the attic are insulated and are in acceptable condition, but should be monitored because of their location. Leaks from pipes that pass through an attic can be soaked up by insulation, and are difficult to detect until significant damage is evident elsewhere."

"Water pipes in the attic are un-insulated and insulation is recommended to prevent freezing. The pipes should be monitored because of their location. Leaks from pipes that pass through an attic can be soaked up by insulation, and are difficult to detect until significant damage is evident elsewhere. Note: combustible insulation should not be closer than 1" to a water heater flue."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #14  
Old 1/12/09, 3:58 PM
sfigert sfigert is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Cecil, Oh
Posts: 162
Default Re: Attic Plumbing

Did you note that where the pipes are fastened to the rafter legs that the insulation has been cut and removed? This may allow the cold climate to transfer to the pipes, and also may make the heat tape work more. The insulation should have been left on in these areas and large straps around insulation & pipes. I generally use conduit clamps sized to fit the O.D. if the insulation myself. Also the I.D. of the insulation should be sized to fit the pipe plus the heat tape. It looks as if some of the insulation seams were slightly open. They need to be closed tight.
Looks like Frost-Tek type heat tape. This is about the best I have found to use.



Scott A. Figert
www.sfigert.com
www.nachi.org NACHI #06042595
Figert Building Inspection, Ltd.
(419) 399-4472 Office & Home Sweet Home
Reply With Quote
  #15  
Old 1/12/09, 4:53 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: Attic Plumbing

There are open insulation joints from apparent shrinkage or movement. The joints were taped together at one time, the tape residue is visible.
Mounting the copper so high above the ceiling does not appear to be correct, and is not according to our local county inspector.


attic-plumbing-barclay-099.jpg




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
No "H" clips? jbreazeale Structural Inspections 7 5/17/07 2:28 PM
Spray Foam to the Rescue ? mcyr Structural Inspections 3 3/27/07 7:29 PM
A few useful posts - I forget from whom jmichalski Plumbing Inspections 12 3/30/06 9:06 PM


All times are GMT -4. The time now is 12:19 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts