Default B-Vent Clearance

First time I have seen this.
Attached Thumbnails
b-vent-clearance-7129-ellis-dr-8-3-09-018.jpg  
Reply With Quote
Find an InterNACHI certified Kansas Home Inspector (and anywhere else in North America)
  #2  
Old 8/4/09, 2:06 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: B-Vent Clearance

Quote:
Originally Posted by bkelly2 View Post
First time I have seen this.
It looks like B-vent which needs 1" minimum clearance to combustibles.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 8/4/09, 7:13 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: B-Vent Clearance

http://apps.risd.edu/envirohealth_ms...ntcompound.txt

From the above link:

UNITED STATES GYPSUM -- SHEETROCK TOPPING JOINT COMPOUND - CEMENT WALLBOARD JOINT
MATERIAL SAFETY DATA SHEET


Fire and Explosion Hazard Data

Flash Point: NONE
Extinguishing Media: NOT COMBUSTIBLE. MEDIA SUITABLE FOR SURROUNDING FIRE
(FP N).



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #4  
Old 8/4/09, 7:18 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: B-Vent Clearance

Are you sure it is cement wallboard ?
Reply With Quote
  #5  
Old 8/4/09, 7:35 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: B-Vent Clearance

In the National Fire Protection Association's NFPA 101 Code for Safety to Life from Fire in Buildings and Structures, a noncombustible material is defined as a material that, "in the form in which it is used and under the conditions anticipated, will not aid combustion or add appreciable heat to an ambient fire. "Materials are tested for noncombustibility in ASTM E 136 Standard Test Method for Behavior of Materials in a Vertical Tube Furnace at 750 degrees C. The test exposes small samples of the material to a stream of air heated to 750 degrees C, (1382 degrees F).

The material is deemed noncombustible if:

1) Sample temperatures at no time exceed 780 degrees C, (1436 degrees F).

2) There is no flaming after 30 seconds. 3) Once the sample loses 50% of its weight, there is no flaming and sample temperatures never exceed 750 degrees C, (1382 degrees F). ASTM E 136 is an extremely strict test and under its criterion, few building materials qualify as noncombustible. Two USG Interiors products which do are CERAMIC HERITAGE and most THERMAFIBER insulation products.

In regard to gypsum wallboard, the product's paper facing prevents it from passing ASTM E 136. However, because it does have a demonstrated ability to perform in fire rated assemblies, the NFPA has placed it in a special classification called limited-combustible. This category distinguishes gypsum wallboard from other, more highly combustible products. To qualify as limited-combustible, a material must have a noncombustible structural base or core, a surface less than 1/8 in. (0.3 cm) thickness and a flame-spread rating of 50 or less.


This last requirement can be confusing because the three national model building codes, (ICBO's Uniform Building Code, SBCCI's Standard Building Code and BOCA's National Building Code), all allow composite materials that meet the NFPA's definition of limited-combustible, to be classified as noncombustible.




InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #6  
Old 8/4/09, 7:40 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: B-Vent Clearance

And...

http://www.rumford.com/drywall.html


Is Drywall Combustible?

An interesting question. Can you attach drywall directly in contact with a masonry chimney?




Two Views




Drywall in not Combustible
According to USG in an article pointed out by Jeff Lockhart
Date: Wed, 23 Oct 2002
From: Jeff Lockhart
Subject: Fire code & sheetrock
To: Jim Buckley
Jim,
I just came across something which I've never seen mentioned in any article dealing with fireplace & chimney clearances. I've wanted to wrap my (interior) chimney & the sides of the firebox in sheetrock, as I've seen in many pictures, but both the old & new codes wouldn't permit it. But this data sheet from USG lists sheetrock as a limited-combustible, and states that it would be allowed. Here's the article:
Regards,
Jeff
USG Data Sheet
Case Studies
In the National Fire Protection Association�NFPA 101 Code for Safety to Life from Fire in Buildings and Structures, a noncombustible material is defined as a material that, "in the form in which it is used and under the conditions anticipated, will not aid combustion or add appreciable heat to an ambient fire." Materials are tested for noncombustibility in ASTM E 136 Standard Test Method for Behavior of Materials in a Vertical Tube Furnace at 750? C. The test exposes small samples of the material to a stream of air heated to 750? C, (1382? F). The material is deemed noncombustible if:
1) Sample temperatures at no time exceed 780? C, (1436? F).
2) There is no flaming after 30 seconds. 3) Once the sample loses 50% of its weight, there is no flaming and sample temperatures never exceed 750? C, (1382? F). ASTM E 136 is an extremely strict test and under its criterion, few building materials qualify as noncombustible. Two USG Interiors products which do are CERAMIC HERITAGE and most THERMAFIBER insulation products.
In regard to gypsum wallboard, the product's paper facing prevents it from passing ASTM E 136. However, because it does have a demonstrated ability to perform in fire rated assemblies, the NFPA has placed it in a special classification called limited-combustible This category distinguishes gypsum wallboard from other, more highly combustible products. To qualify as limited-combustible, a material must have a noncombustible structural base or core, a surface less than 1/8 in. (0.3 cm) thickness and a flame-spread rating of 50 or less.
This last requirement can be confusing because the three national model building codes, (ICBO's Uniform Building Code, SBCCI's Standard Building Code and BOCA's National Building Code), all allow composite materials that meet the NFPA�definition of limited-combustible, to be classified as noncombustible.



Drywall is Combustible
According to the State of New Jersey as pointed out by Michael Thomas 2/26/07
Jim,
Thought you might find this Bulletin (below) of interest:
Michael Thomas
Paragon Home Inspection, LLC
mdt@paragoninspects.com
PO Box 1455 Evanston,IL 60204-1455
847.721.0776
BULLETIN NO. 90-3
State of New Jersey
Department of Community Affairs
Division of Codes and Standards
PO Box 802
Trenton, New Jersey 08625-0802
Richard J. Codey
Acting Governor
Charles A. Richman
Acting Commissioner
Date: December 1990
Revised: December 2005 Subject: Gypsum Wallboard Classification
Reference: N.J.A.C. 5:23-3.14, Building Subcode, Section 703.4.2
N.J.A.C. 5:23-3.20, Mechanical Subcode, Chapter 2
Page 1 of 1
It has recently come to the attention of the Department of Community Affairs that gypsum wallboard is something being mistakenly considered a noncombustible material when applying the clearance-to-combustibles requirements of the Mechanical Subcode.
The definition of ?noncombustible? in the Mechanical Subcode differs from the definition in the Building Subcode. The Building Subcode?s Section 703.4.2, Composite Materials, states that a material having a structural base of noncombustible material (meeting ASTM E136), with a combustible surface not more than 0.125- inch thick, and having a flame-spread rating not greater than 50 (when tested in accordance with ASTM E84) is acceptable as a noncombustible material. Because the Building Subcode allows such ?composite? materials, gypsum wallboard can be considered noncombustible as defined by the Building Subcode.
The Mechanical Subcode does not contain such a provision for composite materials. Noncombustible materials in the context of the Mechanical Subcode are those materials which pass ASTM E136. Gypsum board, because of its combustible facing, will not pass ASTM E136. (The only exception to this applies to Type I commercial kitchen hoods at Section 507.9 of the Mechanical Subcode.)
The difference in standards is due to the different purposes of the two subcodes. The Building Subcode is concerned with the performance of a material under the conditions during a fire, while the Mechanical Subcode is concerned with performance during exposure to a constant high-heat source. Therefore remember, under the Mechanical Subcode, gypsum wallboard is classified as a combustible material.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #7  
Old 8/4/09, 10:41 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,608
Default Re: B-Vent Clearance

Quote:
Originally Posted by lkage View Post
The material is deemed noncombustible if:


In regard to gypsum wallboard, the product's paper facing prevents it from passing ASTM E 136. However, because it does have a demonstrated ability to perform in fire rated assemblies, the NFPA has placed it in a special classification called limited-combustible. This category distinguishes gypsum wallboard from other, more highly combustible products. To qualify as limited-combustible, a material must have a noncombustible structural base or core, a surface less than 1/8 in. (0.3 cm) thickness and a flame-spread rating of 50 or less.


This last requirement can be confusing because the three national model building codes, (ICBO's Uniform Building Code, SBCCI's Standard Building Code and BOCA's National Building Code), all allow composite materials that meet the NFPA's definition of limited-combustible, to be classified as noncombustible.
Would the painted surface affect the limits of the wallboard being combustible?
Paint on drywall and the vent.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #8  
Old 8/5/09, 5:50 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: B-Vent Clearance

Quote:
Can I install drywall or wall board right up against the gas vent?
No. Drywall and wallboard are considered combustible materials and should not be installed against the vent including the use of this material to close off the hole around the vent. Type B Gas Vent requires a minimum of one-inch clearance to combustibles. This one-inch is a typical clearance for all brands of Type B Vent, but each section of vent pipe is marked with the clearance required by Underwriter Laboratories, so it should be checked.
Does Type B Gas Vent have a fire rating?
But then I already knew that. http://www.americanmetalproducts.com...vent/faq.htm#6

B Vent as per manufactures listed guidelines is not supposed to touch drywall.
Reply With Quote
  #9  
Old 8/5/09, 10:09 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: B-Vent Clearance

Isn't drywall used as a fire barrier?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 8/5/09, 11:32 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: B-Vent Clearance

Quote:
Originally Posted by jfunderburk View Post
Isn't drywall used as a fire barrier?
Ah, that is where you are not asking the correct question Joe. The question is about B-Vent not dry wall. B-Vent, as listed (UL I believe) needs clearance. Check the manufacturer's installation instructions.
Reply With Quote
  #11  
Old 8/5/09, 11:38 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: B-Vent Clearance

Quote:
Originally Posted by bkelly2 View Post
Ah, that is where you are not asking the correct question Joe. The question is about B-Vent not dry wall. B-Vent, as listed (UL I believe) needs clearance. Check the manufacturer's installation instructions.
Is there any clearance required other than clearance to combustible materials.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 8/5/09, 11:56 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: B-Vent Clearance

http://www.northlineexpress.com/imag...structions.pdf
Reply With Quote
  #13  
Old 8/6/09, 12:10 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: B-Vent Clearance

I word searched the document for "clearance" and in every instance it refers to clearance from combustible materials. It can obviously be in contact with collars, straps, flashings, and other materials. Why not non-combustible sheetrock?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Find an InterNACHI certified Kansas Home Inspector (and anywhere else in North America)
  #14  
Old 8/6/09, 12:43 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: B-Vent Clearance

Quote:
Originally Posted by jfunderburk View Post
I word searched the document for "clearance" and in every instance it refers to clearance from combustible materials. It can obviously be in contact with collars, straps, flashings, and other materials. Why not non-combustible sheetrock?
Ok I'll play, why not?? I just follow what the Manufacturer says for their product Joe. If I spent much time asking why every time I wondered about something I would never finish an inspection.
Reply With Quote
  #15  
Old 8/6/09, 9:16 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: B-Vent Clearance

Quote:
Originally Posted by bkelly2 View Post
Ok I'll play, why not?? I just follow what the Manufacturer says for their product Joe. If I spent much time asking why every time I wondered about something I would never finish an inspection.
And in this case, what do the manufacturers recommend that you think has been violated?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pellet stove help chellickson General Inspection Discussion 23 8/19/10 1:23 AM
Fireplace Vent and Patio Cover Framing Clearance? rwashington Exterior Inspections 6 6/10/08 9:54 PM
Microwave range vent clearance mbarnett Inspecting HVAC Systems 3 5/15/08 5:21 AM
Required Clearance For Thru-Wall Fireplace Vent & Windows kmccullough Inspecting HVAC Systems 2 3/2/08 12:08 PM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 5:22 PM


All times are GMT -4. The time now is 10:26 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts