  #1  
Old 3/24/07, 11:23 PM
Larry E. Freeze Larry E. Freeze is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Leander, TX
Posts: 27
Default Backflow prevention for dishwashers

I imagine, optimally, an air-admittance valve would be in order.
But what about dishwashers w/o AAV's?

Is an upward slope from the dishwasher and then a slope downward
toward the garbage disposal (or waste drain) acceptable?

I have seen some that have virtually completely level d/w drain slope,
and previous owners have complained about dirty water being left in the bottom of the dishwasher after a cycle.
I certainly write those up.

But back to ?: Is upward slope from d/w and then downward slope toward waste drain good enough for anti-backflow?
Reply With Quote
  #2  
Old 3/24/07, 11:25 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Backflow prevention for dishwashers

Typically, yes. It's called a high loop.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 3/24/07, 11:28 PM
Larry E. Freeze Larry E. Freeze is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Leander, TX
Posts: 27
Default Re: Backflow prevention for dishwashers

Thanks!
That's what I figured.
Now I know what it's called !
Thanks again,
Larry
Reply With Quote
  #4  
Old 3/24/07, 11:54 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Backflow prevention for dishwashers

Quote:
Originally Posted by lfreeze
I imagine, optimally, an air-admittance valve would be in order.
But what about dishwashers w/o AAV's?
I assume you're actually referring to an air-gap rather than an AAV.

AAV's are a vent system which has nothing to do with back-flow prevention. An air-gap device is used in dishwasher drain lines to prevent back-flow.

High-loops are allowed by many model codes, but not here in CA.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 3/25/07, 1:10 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Backflow prevention for dishwashers

Quote:
Originally Posted by jpope
High-loops are allowed by many model codes, but not here in CA.
As with everything, though, final say-so is up to the local AHJ. I have a gazillion bazillion brand new multi-million dollar homes in brand new subdivisions with dishwashers on kitchen islands where the local AHJ here allows high loops.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #6  
Old 3/25/07, 12:39 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Backflow prevention for dishwashers

I see these often too. But the code is very clear about this, and it should be mentioned in your report.

Here's how I state it. . .

The dishwasher is functional but discharges without an air-gap fitting, which is mandated by California Building Standards. The absence of the air-gap fitting may also create a drainage problem and a health hazard.

and here's the code. . .

CPC 807.4 No domestic dishwashing machine shall be directly connected to a drainage system or food waste disposer without the use of an approved dishwasher airgap fitting on the discharge side of the dishwashing machine.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 3/25/07, 1:00 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Backflow prevention for dishwashers

Quote:
Originally Posted by jpope
I see these often too. But the code is very clear about this, and it should be mentioned in your report.
I mention it, but I don't use code references or "mandates" like you do.

And it's still up to the local AHJ to interpret:

Quote:
Originally Posted by jpope
CPC 807.4 No domestic dishwashing machine shall be directly connected to a drainage system or food waste disposer without the use of an approved dishwasher airgap fitting on the discharge side of the dishwashing machine.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #8  
Old 3/25/07, 2:19 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Backflow prevention for dishwashers

Quote:
Originally Posted by rray
And it's still up to the local AHJ to interpret:
Not much left to the imagination here, it's pretty cut and dry.

Quote:
No dishwashing machine shall be connected to a drainage system without an airgap fitting.
Now, obviously, a variance can be obtained to circumvent almost any code requirement, but I am certainly not going to just "assume" this has been done. The homeowner can do the work to verify this.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 3/25/07, 2:25 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Backflow prevention for dishwashers

Quote:
Originally Posted by jpope
Not much left to the imagination here, it's pretty cut and dry.
Sometimes the AHJ does probably use his imagination for purposes of interpretation.

Quote:
Originally Posted by jpope
Now, obviously, a variance can be obtained to circumvent almost any code requirement, but I am certainly not going to just "assume" this has been done. The homeowner can do the work to verify this.
Or they can hire me as a consultant to verify it at $100 per hour, which several have done. Now that I know what subdivisions are involved, I can simply put the information in my report, and if they still want me to verify current interpretations, I do that.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #10  
Old 3/25/07, 9:07 PM
Clifford P. Judkins Clifford P. Judkins is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Wasilla, AK
Posts: 1
Default Re: Backflow prevention for dishwashers

If it does not have an AAV , The discharge hose must be atleast 32 inches long and extend above the level of the dishwasher per the IRC
Quote:
Originally Posted by lfreeze
I imagine, optimally, an air-admittance valve would be in order.
But what about dishwashers w/o AAV's?

Is an upward slope from the dishwasher and then a slope downward
toward the garbage disposal (or waste drain) acceptable?

I have seen some that have virtually completely level d/w drain slope,
and previous owners have complained about dirty water being left in the bottom of the dishwasher after a cycle.
I certainly write those up.

But back to ?: Is upward slope from d/w and then downward slope toward waste drain good enough for anti-backflow?
Reply With Quote
  #11  
Old 3/25/07, 10:22 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Backflow prevention for dishwashers

Quote:
Originally Posted by cjudkins
If it does not have an AAV , The discharge hose must be atleast 32 inches long and extend above the level of the dishwasher per the IRC
An AAV is a vent system. An AAV is not the same as an air-gap or high-loop, and it performs a completely different function.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
asking help regarding backflow preventer afrost Plumbing Inspections 7 5/2/07 9:08 PM
Backflow Preventor AND Pressure Reducing Valve??? tlorenz Inspecting HVAC Systems 1 9/26/06 9:08 AM
Backflow inspection dbucknavich General Inspection Discussion 6 8/10/06 2:46 PM
An Ounce of Prevention, How Not to get Sued by Mark Cohen gromicko Miscellaneous Discussion for Inspectors 0 2/6/06 3:10 AM


All times are GMT -4. The time now is 9:24 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts