Default Black iron & water heater

Can black iron be used at the hot & cold water at the top of the tank?

If no why so?
Attached Thumbnails
black-iron-and-water-heater-105107-022-small-.jpg.jpg
Views:	81
Size:	39.3 KB
ID:	14502  
Reply With Quote
  #2  
Old 9/14/07, 2:38 PM
lfoster's Avatar
lfoster lfoster is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 489
Please Note: lfoster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Black iron & water heater

I found thin --- Uniform Plumbing Code 2003

604.1 Water distribution pipe, building supply water pipe, and fittings shall be of brass, copper, case iron, CPVC, galvanized malleable iron, galvanized wrought iron, galvanized steel, PEX or other approved materials.
Reply With Quote
  #3  
Old 9/14/07, 2:40 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Black iron & water heater

Yes. It most certainly can. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 9/14/07, 2:43 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,555
Default Re: Black iron & water heater

Thanks

I have never seen black iron at the top of the tank. Just wanted to make sure.
Reply With Quote
  #5  
Old 9/14/07, 2:45 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Black iron & water heater

It's very common to see black iron pipe used for fire sprinkler piping in commercial applications.
It was once common for residential water piping but lost favor due the potential of rusting out.
Reply With Quote
  #6  
Old 9/14/07, 6:07 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Black iron & water heater

You will get spanked here for using black iron on water not allowed.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 9/14/07, 6:12 PM
Henry Valenzano, CMI's Avatar
Henry Valenzano, CMI Henry Valenzano, CMI is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Colorado Springs, CO
Posts: 1,555
Send a message via MSN to hvalenzano
Default Re: Black iron & water heater

Quote:
Originally Posted by dmacy
Can black iron be used at the hot & cold water at the top of the tank?

If no why so?
It can be used but it is not recommended because the rust partials break off and spread to the rest of the system. It will also destroy the glass liner of the water heater. i always recommend that it be replaced.

The use of black iron on sprinkler sys and boilers is ok because that water is not oxygenated



Henry Valenzano CMI (Hank)
Double Check Home Inspection LLC.
www.DCHI.com Hank@DCHI.com 719-635-6425
Colorado Arms Repair : Gunsmith
www.ArmsRepair.com Henry@ArmsRepair.com
Reply With Quote
  #8  
Old 9/14/07, 10:22 PM
lfoster's Avatar
lfoster lfoster is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 489
Please Note: lfoster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Black iron & water heater

Does it give the water a bad smell / taste?
If not, what does?
Reply With Quote
  #9  
Old 9/15/07, 4:36 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Black iron & water heater

Quote:
Originally Posted by hvalenzano
The use of black iron on sprinkler sys and boilers is ok because that water is not oxygenated
I'm not sure I'm following you there, Henry.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #10  
Old 9/15/07, 4:38 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Black iron & water heater

Quote:
Originally Posted by lfoster
Does it give the water a bad smell / taste?
If not, what does?
Various chemicals in the water.

My brother's house in eastern Slidell, Louisiana, has water that smells like rotten eggs all the time. And the ice cubes are always yellow. Hmmmmmm. The whole neighborhood has rotten egg-smelling water. They were hoping that when Katrina washed away all the houses it would have washed away the bad water, too, but no such luck. New house, old smell.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #11  
Old 9/15/07, 10:38 AM
Henry Valenzano, CMI's Avatar
Henry Valenzano, CMI Henry Valenzano, CMI is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Colorado Springs, CO
Posts: 1,555
Send a message via MSN to hvalenzano
Default Re: Black iron & water heater

Quote:
Originally Posted by rray
I'm not sure I'm following you there, Henry.
Sprinklers and boilers are closed systems as long as you do not add more fresh water the oxygen in the water separates. When the oxygen is gone there is no more rusting. on a domestic system you are always running water so you are putting fresh oxygenated water back in the system.



Henry Valenzano CMI (Hank)
Double Check Home Inspection LLC.
www.DCHI.com Hank@DCHI.com 719-635-6425
Colorado Arms Repair : Gunsmith
www.ArmsRepair.com Henry@ArmsRepair.com
Reply With Quote
  #12  
Old 9/15/07, 12:13 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Black iron & water heater

Quote:
Originally Posted by hvalenzano
Sprinklers and boilers are closed systems as long as you do not add more fresh water the oxygen in the water separates. When the oxygen is gone there is no more rusting. on a domestic system you are always running water so you are putting fresh oxygenated water back in the system.
Those two systems are only "closed systems" for a period of time. As soon as they are used, which you acknowledged when you said "as long as you do not add more" water, then it is an open system for that period of time. No system outside of the laboratory can be completely closed, only closure to varying degrees.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #13  
Old 9/15/07, 3:59 PM
Henry Valenzano, CMI's Avatar
Henry Valenzano, CMI Henry Valenzano, CMI is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Colorado Springs, CO
Posts: 1,555
Send a message via MSN to hvalenzano
Default Re: Black iron & water heater

Quote:
Originally Posted by rray
Those two systems are only "closed systems" for a period of time. As soon as they are used, which you acknowledged when you said "as long as you do not add more" water, then it is an open system for that period of time. No system outside of the laboratory can be completely closed, only closure to varying degrees.
True but when water is not moving it gets stagnant and the air separates. so the air is not in contact with the pipe like it is in a domestic system. Its just like the difference in a dead lake and a stream. a dead lake has no movement so it gets stagnant it looses its oxygen and a running stream is always moving so it gets aireiated.



Henry Valenzano CMI (Hank)
Double Check Home Inspection LLC.
www.DCHI.com Hank@DCHI.com 719-635-6425
Colorado Arms Repair : Gunsmith
www.ArmsRepair.com Henry@ArmsRepair.com
Reply With Quote
  #14  
Old 9/15/07, 5:40 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Black iron & water heater

Quote:
Originally Posted by hvalenzano
True but when water is not moving it gets stagnant and the air separates. so the air is not in contact with the pipe like it is in a domestic system. Its just like the difference in a dead lake and a stream. a dead lake has no movement so it gets stagnant it looses its oxygen and a running stream is always moving so it gets aireiated.
If it's a closed system, and "the air separates," where does the air go?



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #15  
Old 9/15/07, 5:43 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Black iron & water heater

Quote:
Originally Posted by rray
If it's a closed system, and "the air separates," where does the air go?
An (automatic) air bleed valve removes the air from the system.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water Heater Dip Tube Failure jacaron Plumbing Inspections 2 2/25/07 12:28 AM
Venting an oil-fired water heater mh718 Inspecting HVAC Systems 3 11/16/06 10:36 AM
TPR & Combusiton Air thejnicki Plumbing Inspections 16 9/18/06 9:55 PM