Quote:
Originally Posted by jtedesco1
No it is a requirement:


See 250.104(B) Other Metal Piping
No, it is not a requirement, Joe. Not nationwide.l Why did you say it was?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #17  
Old 10/13/06, 6:16 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding both hot and hold supply pipes

Quote:
Originally Posted by kshepard
No, it is not a requirement, Joe. Not nationwide.l Why did you say it was?
See the NEC Manual of Style for use of terms that are used when identifying various Articles and Sections in the NEC.

When adopted by any Jurisdiction the NEC includes instructions on enforcement procedures in 90.4 (often not clearly understood by some) and see Section 90.5 where "SHALL" is used in any rules in the NEC it is a requirement and is a mandatory term, and unless the local or State modified the NEC it is the law.

If you need further clarification on the question of adoption or interpretation of the rule in question question call the NFPA or IAEI directly and ask for an Official Interpretation.


• 250.104(D): Relocated requirements for bonding water piping and structural metal to separately derived systems from 250.104(A)(4) of 2002 Code.

250.104 Bonding of Piping Systems and Exposed Structural Steel

(B) Other Metal Piping Where installed in or attached to a building or structure, metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.

FPN: Bonding all piping and metal air ducts within the premises will provide additional safety."

NECH COMMENTARY:

"Unlike the metal piping systems covered in 250.104(A), this requirement applies only to metal piping systems that are likely to become energized. What this means is that where metal piping systems and electrical circuits interface through mechanical and electrical connections within equipment, a failure of electrical insulation can result in the connected piping system(s) becoming energized. Gas appliances are a common example of metal gas piping and electrical circuits being connected to a common piece of equipment, and in this case the 250.104(B) requirements apply. The required bonding of these other piping systems can occur at the same locations specified in 250.104(A), or an additional provision within this paragraph permits the equipment grounding conductor of the circuit that is likely to energize the piping as the means for bonding the piping. Typically, the use of an additional bonding jumper is not necessary to comply with this requirement because the equipment grounding connection to the non–current-carrying metal parts of the appliance also provides a bonding connection to the metal piping attached to the appliance. This is a bonding requirement, and the other piping is not being used as an electrode. Therefore, this requirement does not conflict with 250.52(B)(1), which prohibits the use of metal underground gas piping as a grounding electrode for electrical services or other sources of supply."

www.nfpa.org

I stand by my comments!
__________________
Reply With Quote
  #18  
Old 10/13/06, 11:26 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Bonding both hot and hold supply pipes

Quote:
Originally Posted by kshepard
No, it is not a requirement, Joe. Not nationwide.l Why did you say it was?
Kenton,

Check your local code as it is written. I think you will find that bonding of the metallic water piping is required, even in your area. Whether or not this requirement is enforced, is an entirely separate issue.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #19  
Old 5/3/08, 2:32 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Bonding both hot and hold supply pipes

This is not a defect, but it should be called out, correct? What type of wording should be used?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #20  
Old 5/3/08, 2:51 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Bonding both hot and hold supply pipes

Quote:
Originally Posted by jtedesco1
No it is a requirement:

See 250.104(B) Other Metal Piping

Any piping that can likely become energized is already 'bonded/grounded" by the circuit that can energize it. Example, 30a circuit to the water heater bonds it also. 120v cicuit to gas stove, has a ground too.



PS I have pipe clamps and 4awg for dedicated bonds in my house. hot 2 cold 2 gas 2 etc
Reply With Quote
  #21  
Old 5/3/08, 11:13 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Bonding both hot and hold supply pipes

Quote:
Originally Posted by nbhi
This is not a defect, but it should be called out, correct? What type of wording should be used?
The hot and cold water pipes should be bonded.

“Bonding”is connecting any metallic pipe that may become energized and must be bonded (to ground). Bonding is generally done by connecting a “jumper” wire across the water pipes. Often water heaters are installed with di-electric unions which breaks any grounding path through the heater. Bonding all piping and metal air ducts within the premises will provide additional safety. Any metallic gas lines should also be bonded for safety.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #22  
Old 5/4/08, 1:31 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Bonding both hot and hold supply pipes

http://www.iaei.org/subscriber/magaz...f/johnston.htm



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #23  
Old 5/4/08, 8:00 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Bonding both hot and hold supply pipes

Thanks Jae, thats what I am looking for.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 2:13 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts