  #16  
Old 5/26/07, 2:40 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Burnt Combustion Hatch? Please Help!

My god! That thing is an accident waiting to happen.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #17  
Old 5/26/07, 8:15 AM
Sabrina J. Roper Sabrina J. Roper is offline
New User
 
Join Date: May 2007
Posts: 23
Please Note: Sabrina J. Roper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Burnt Combustion Hatch? Please Help!

Mr. Cooke,
I was wondering just what would the City Housing Authorities do about this problem if I called them?

Thank in advance,
Sabrina
Reply With Quote
  #18  
Old 5/26/07, 12:24 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Burnt Combustion Hatch? Please Help!

Quote:
Originally Posted by lkage
Jeff, I very rarely have the flame roll out of the cabinet, with the heat shield open and firing the burner, when inspecting the water heater burners...maybe I've been lucky?
Even without the actual "flame" rolling out, the heat will cause discoloration that will worsen over time.

The majority of the time I see this condition (not usually this severe) is on a unit that, for all intents and purpose, is functioning properly, and the shield is missing or improperly installed.

In this particular case, however, this unit appears to be starving for oxygen, and its exhaust system is barely functional.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #19  
Old 5/26/07, 1:00 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Burnt Combustion Hatch? Please Help!

What is connected to the vent pipe heading downwards from the connection to the water heater?
Reply With Quote
  #20  
Old 5/26/07, 4:23 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Burnt Combustion Hatch? Please Help!

Quote:
Originally Posted by jpope
Even without the actual "flame" rolling out, the heat will cause discoloration that will worsen over time.

The majority of the time I see this condition (not usually this severe) is on a unit that, for all intents and purpose, is functioning properly, and the shield is missing or improperly installed.

In this particular case, however, this unit appears to be starving for oxygen, and its exhaust system is barely functional.
10/4



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #21  
Old 5/26/07, 5:28 PM
sparksnmore sparksnmore is offline
Active Poster
 
Join Date: Oct 2006
Location: midwest
Posts: 177
Please Note: sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Burnt Combustion Hatch? Please Help!

Quote:
Originally Posted by mthomas2
What is connected to the vent pipe heading downwards from the connection to the water heater?
Just guessing from the picture but it looks to me like the 4" flue which I believe would normally be 3" off the WH is teed into a 4" single wall coming from a furnace below.
The pipe from the tee upward should probably be 5" type "B" and should also be type "B" below if in an unheated crawl space.

Although there is no soot, the "burning of the eyes" when it comes on still concerns me.


You in Corpus Christi Sabrina?
Reply With Quote
  #22  
Old 5/26/07, 8:42 PM
Sabrina J. Roper Sabrina J. Roper is offline
New User
 
Join Date: May 2007
Posts: 23
Please Note: Sabrina J. Roper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Burnt Combustion Hatch? Please Help!

Quote:
Originally Posted by sparksnmore
Just guessing from the picture but it looks to me like the 4" flue which I believe would normally be 3" off the WH is teed into a 4" single wall coming from a furnace below.
The pipe from the tee upward should probably be 5" type "B" and should also be type "B" below if in an unheated crawl space.

Although there is no soot, the "burning of the eyes" when it comes on still concerns me.


You in Corpus Christi Sabrina?

Sparksnmore,
Yes I am in Corpus Christi, Texas.
I live in a 4 unit apartment complex and all 4 unit water heater are all connected into one exiting Flue Pipe.

Here's a graphic I drew of how the flue piping is ran.
Plus an extra image.







Last edited by Sabrina J. Roper; 5/27/07 at 4:11 AM..
Reply With Quote
  #23  
Old 5/26/07, 10:07 PM
Sabrina J. Roper Sabrina J. Roper is offline
New User
 
Join Date: May 2007
Posts: 23
Please Note: Sabrina J. Roper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Burnt Combustion Hatch? Please Help!

Photo of the top of the Flue Pipe.



Thanks,
Sabrina
Reply With Quote
  #24  
Old 5/26/07, 10:10 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,949
Default Re: Burnt Combustion Hatch? Please Help!

Quote:
Originally Posted by Sabrina J. Roper
Mr. Cooke,
I was wondering just what would the City Housing Authorities do about this problem if I called them?

Thank in advance,
Sabrina
Here in Canada they would act on it I am sure as having it reported and not following up and they had asome one hurt or died would give them a lot of grief and more then likely cost them their job.
Their job is to look after the public from things like this .



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #25  
Old 5/27/07, 1:46 AM
sparksnmore sparksnmore is offline
Active Poster
 
Join Date: Oct 2006
Location: midwest
Posts: 177
Please Note: sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Burnt Combustion Hatch? Please Help!

Quote:
Originally Posted by Sabrina J. Roper
Sparksnmore,
Yes I am in Corpus Christi, Texas.
I live in a 4 unit apartment complex and all 4 unit water heater are all connected into one exiting Flue Pipe.

Here's a graphic I drew of how the flue piping is ran.
Plus an extra image.
Nice drawing, that helps a lot !

Well I see it is type "B" pipe now.
I still suspect the pipe is undersized but it's exact size is hard to tell in the pictures.

I didn't see if you said or not but was the scorch already on the tank when they installed it?

Did you licensed plumber friend hold a match or lighter up to the draft hood with the WH fired up to check the flue draft?
OR,
do you know how to do that test?

An open flame should be drawn into the opening of the draft diverter @ the top of the tank and not blown out while it is "on"
Reply With Quote
  #26  
Old 5/27/07, 1:50 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Burnt Combustion Hatch? Please Help!

There is nothing proper about that installation. Like I said, "accident waiting to happen". . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #27  
Old 5/27/07, 2:12 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,068
Default Re: Burnt Combustion Hatch? Please Help!

Quote:
Originally Posted by jpope
There is nothing proper about that installation. Like I said, "accident waiting to happen". . .
Nothing proper is right.

Unreal to say the least.

But it looks like the wall might be helping the pipes stay together....wow....
Reply With Quote
  #28  
Old 5/27/07, 4:52 AM
Sabrina J. Roper Sabrina J. Roper is offline
New User
 
Join Date: May 2007
Posts: 23
Please Note: Sabrina J. Roper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Burnt Combustion Hatch? Please Help!

Quote:
Originally Posted by sparksnmore
Nice drawing, that helps a lot !

Well I see it is type "B" pipe now.
I still suspect the pipe is undersized but it's exact size is hard to tell in the pictures.

I didn't see if you said or not but was the scorch already on the tank when they installed it?

Did you licensed plumber friend hold a match or lighter up to the draft hood with the WH fired up to check the flue draft?
OR,
do you know how to do that test?

An open flame should be drawn into the opening of the draft diverter @ the top of the tank and not blownile it is "on"
Sparksnmore,
Yes that licensed plumber did do the test with a match. It drew the flame up towards the draft hood, also for a very brief second a few times it would not be drawn towards the hood....kinda like wiggling, but for a very brief second then back to drawing it upwards like it is suppose too.

A far as that "burnt combustion door" I do not recall that being there when the wannabe plumber installed it. I say this because when be brought the thing upstairs and got it in the apartment I notice there were scratches on the side of the tank and a very small tiny dent...I also looked the thing over while he was putting it in that closet and I do not recall seeing that burnt area. That burnt area is very stand outish, seems I would have noticed that if it was already there. Heck that burnt area is like screaming out "Hello Look At Me."

I asked this licensed plumber if this was illeagl to have all 4 apartment units ran together like this, he said yes and no, but the flue pipe is too small for all 4 to be running thru it. Is that correct what he said??

Here's a few more photos:




BTW, I just went and bought another Carbon Monoxide Detector at WalMart for 20 bucks. This alarm is a First Alert...hope it's a good one...also has the UL rating on it.


Thanks,
Sabrina

Last edited by Sabrina J. Roper; 5/27/07 at 5:12 AM..
Reply With Quote
  #29  
Old 5/27/07, 5:07 AM
Sabrina J. Roper Sabrina J. Roper is offline
New User
 
Join Date: May 2007
Posts: 23
Please Note: Sabrina J. Roper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Burnt Combustion Hatch? Please Help!

Quote:
Originally Posted by jpope
There is nothing proper about that installation. Like I said, "accident waiting to happen". . .
Jpope,
I agree with you 100% that is is "an accident waiting to happen."

All we want at this time and point is for this to be fixed so we can live here til we buy a house which our plan is by November 2007. I would hate to have to move now and then turn around again and move again in November.

I also don't want to get crappy with the landlord either, I think if I did he wouldn't have a real plumber fix this problem and of course we would have no choice to move if it's not fixed ASAP.

My landlord is concerned or seems to be at least, but we will see what happens Monday or Tuesday of this week as far as it being fix correctly.

My landlord also told me that if I choose to use a different plumber then the wannabe plumber he uses we will have to pay half the plumbing bill and he would pay the other half.....crock of crap if ya ask me!!

Yes, I could turn him in into the City Housing Authorities but that would get us evicted I'm sure.....but then again if this problem isn't fixed by Monday/Tuesday of this week we may have no other choice then to turn him in and move out of here!

This is a seriuos matter just as you stated.

Thanks,
Sabrina
Reply With Quote
  #30  
Old 5/27/07, 7:54 AM
Sabrina J. Roper Sabrina J. Roper is offline
New User
 
Join Date: May 2007
Posts: 23
Please Note: Sabrina J. Roper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Burnt Combustion Hatch? Please Help!

Quote:
Originally Posted by sparksnmore

Although there is no soot, the "burning of the eyes" when it comes on still concerns me.


You in Corpus Christi Sabrina?
Sparknmore,
What do you think is causing the eyes to burn when this water heater comes on? My throat and nose burn too. The water heater is right off my kitchen in what I call a small utility room.

Also after I get out of the shower, my face burns like it's been sunburned for several hours after showering.....any idea what that is caused from?

Just a little info on this building, built in 1930....and it's Haunted!

Thanks,
Sabrina

Last edited by Sabrina J. Roper; 5/27/07 at 7:57 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Combustion Air in Garage hmcbride Inspecting HVAC Systems 9 8/7/07 3:31 PM
combustion air jwisecup Inspecting HVAC Systems 1 2/3/07 7:10 PM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 8:47 AM