My god! That thing is an accident waiting to happen.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#17
|
|||
|
|||
|
Please Note:
Sabrina J. Roper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Mr. Cooke,
I was wondering just what would the City Housing Authorities do about this problem if I called them? Thank in advance, Sabrina |
|
#18
|
||||
|
||||
|
Quote:
The majority of the time I see this condition (not usually this severe) is on a unit that, for all intents and purpose, is functioning properly, and the shield is missing or improperly installed. In this particular case, however, this unit appears to be starving for oxygen, and its exhaust system is barely functional. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#19
|
|||
|
|||
|
Please Note:
mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
What is connected to the vent pipe heading downwards from the connection to the water heater?
|
|
#20
|
|||
|
|||
|
Quote:
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#21
|
|||
|
|||
|
Please Note:
sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
The pipe from the tee upward should probably be 5" type "B" and should also be type "B" below if in an unheated crawl space. Although there is no soot, the "burning of the eyes" when it comes on still concerns me. You in Corpus Christi Sabrina? |
|
#22
|
|||
|
|||
|
Please Note:
Sabrina J. Roper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Sparksnmore, Yes I am in Corpus Christi, Texas. I live in a 4 unit apartment complex and all 4 unit water heater are all connected into one exiting Flue Pipe. Here's a graphic I drew of how the flue piping is ran. Plus an extra image. ![]()
Last edited by Sabrina J. Roper; 5/27/07 at 4:11 AM.. |
|
#23
|
|||
|
|||
|
Please Note:
Sabrina J. Roper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Photo of the top of the Flue Pipe.
![]() Thanks, Sabrina |
|
#24
|
||||
|
||||
|
Quote:
Their job is to look after the public from things like this . If I can answer any questions please send me email Roycooke@hotmail.com On an inspection and need immediate help call my cell 613-827-2011 |
|
#25
|
|||
|
|||
|
Please Note:
sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Well I see it is type "B" pipe now. I still suspect the pipe is undersized but it's exact size is hard to tell in the pictures. I didn't see if you said or not but was the scorch already on the tank when they installed it? Did you licensed plumber friend hold a match or lighter up to the draft hood with the WH fired up to check the flue draft? OR, do you know how to do that test? An open flame should be drawn into the opening of the draft diverter @ the top of the tank and not blown out while it is "on" |
|
#26
|
||||
|
||||
|
There is nothing proper about that installation. Like I said, "accident waiting to happen". . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#27
|
||||
|
||||
|
Quote:
Unreal to say the least. But it looks like the wall might be helping the pipes stay together....wow.... Dale Duffy Inspect Arizona Companies, Inc. Phoenix Home Inspectors, Inc. Scottsdale Home Inspectors, Inc. Infraspection Certified Thermographer 602.402.5305 Home Hints eNews
InterNACHI 2007 U.S.A Member of the Year National Association of Commercial Building Inspectors, Inc. |
|
#28
|
|||
|
|||
|
Please Note:
Sabrina J. Roper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Yes that licensed plumber did do the test with a match. It drew the flame up towards the draft hood, also for a very brief second a few times it would not be drawn towards the hood....kinda like wiggling, but for a very brief second then back to drawing it upwards like it is suppose too. A far as that "burnt combustion door" I do not recall that being there when the wannabe plumber installed it. I say this because when be brought the thing upstairs and got it in the apartment I notice there were scratches on the side of the tank and a very small tiny dent...I also looked the thing over while he was putting it in that closet and I do not recall seeing that burnt area. That burnt area is very stand outish, seems I would have noticed that if it was already there. Heck that burnt area is like screaming out "Hello Look At Me." I asked this licensed plumber if this was illeagl to have all 4 apartment units ran together like this, he said yes and no, but the flue pipe is too small for all 4 to be running thru it. Is that correct what he said?? Here's a few more photos: ![]() ![]() BTW, I just went and bought another Carbon Monoxide Detector at WalMart for 20 bucks. This alarm is a First Alert...hope it's a good one...also has the UL rating on it. Thanks, Sabrina Last edited by Sabrina J. Roper; 5/27/07 at 5:12 AM.. |
|
#29
|
|||
|
|||
|
Please Note:
Sabrina J. Roper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I agree with you 100% that is is "an accident waiting to happen." All we want at this time and point is for this to be fixed so we can live here til we buy a house which our plan is by November 2007. I would hate to have to move now and then turn around again and move again in November. I also don't want to get crappy with the landlord either, I think if I did he wouldn't have a real plumber fix this problem and of course we would have no choice to move if it's not fixed ASAP. My landlord is concerned or seems to be at least, but we will see what happens Monday or Tuesday of this week as far as it being fix correctly. My landlord also told me that if I choose to use a different plumber then the wannabe plumber he uses we will have to pay half the plumbing bill and he would pay the other half.....crock of crap if ya ask me!! Yes, I could turn him in into the City Housing Authorities but that would get us evicted I'm sure.....but then again if this problem isn't fixed by Monday/Tuesday of this week we may have no other choice then to turn him in and move out of here! This is a seriuos matter just as you stated. Thanks, Sabrina |
|
#30
|
|||
|
|||
|
Please Note:
Sabrina J. Roper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
What do you think is causing the eyes to burn when this water heater comes on? My throat and nose burn too. The water heater is right off my kitchen in what I call a small utility room. Also after I get out of the shower, my face burns like it's been sunburned for several hours after showering.....any idea what that is caused from? Just a little info on this building, built in 1930....and it's Haunted! Thanks, Sabrina Last edited by Sabrina J. Roper; 5/27/07 at 7:57 AM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Combustion Air in Garage | hmcbride | Inspecting HVAC Systems | 9 | 8/7/07 3:31 PM |
| combustion air | jwisecup | Inspecting HVAC Systems | 1 | 2/3/07 7:10 PM |
| Another reason to recommend CO testers | rnewman1 | Interior Inspections | 2 | 10/12/06 8:47 AM |
| Combustion Air Availability? | cradan | Inspecting HVAC Systems | 4 | 2/19/06 10:16 AM |