The exhaust piping should be increased in size for every appliance attached to it. Also, the T-fittings are improper. They should be directional fittings (Y-fittings).

So regardless of the "match-test," the vent is not going to function properly, especially if all four units are firing at the same time.

If this were CA (UPC), you wouldn't be allowed to vent systems on different floors to the same exhaust vent. After seeing this set-up, I can see the logic.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #32  
Old 5/27/07, 7:28 PM
Sabrina J. Roper Sabrina J. Roper is offline
New User
 
Join Date: May 2007
Posts: 23
Please Note: Sabrina J. Roper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Burnt Combustion Hatch? Please Help!

Quote:
Originally Posted by jpope
The exhaust piping should be increased in size for every appliance attached to it. Also, the T-fittings are improper. They should be directional fittings (Y-fittings).

So regardless of the "match-test," the vent is not going to function properly, especially if all four units are firing at the same time.

If this were CA (UPC), you wouldn't be allowed to vent systems on different floors to the same exhaust vent. After seeing this set-up, I can see the logic.

Jpope,
Right at 1 1/2 years ago (September 2005) this apartment building was sold to new owners. The new owners had a Building Inspector come out to see what all was wrong with the building before they bought it.

When the Building Inspectors came to my apt., the Inspector opened that water heater closet and said "Oh No, No, No, None of This is Up to Code." and told the new owner as he stood there with the Inspector that it had to be replaced...well 1 1/2 years later as you can see this has not been done.

I was standing in my kitchen when this Inspector said this too, so yes Iheard this but wasn't real sure what he was talking about, but now I know!!

Thanks for all your replies and help...heck before this theard is over with I'll be a water heater inspector, LOL...learning so much from everyones input here.

Thanks again,
Hope you had a wonderful holiday,
Sabrina Roper
C.C. Texas
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Combustion Air in Garage hmcbride Inspecting HVAC Systems 9 8/7/07 2:31 PM
combustion air jwisecup Inspecting HVAC Systems 1 2/3/07 6:10 PM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 7:47 AM
Combustion Air Availability? cradan Inspecting HVAC Systems 4 2/19/06 9:16 AM


All times are GMT -4. The time now is 8:41 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts