Default Can anyone tell me what the tank is in this attic picture? 100 year old house.

Can anyone tell me what the tank is in this attic picture?
The house is a 1900 house.
It appears the tank is attached to a wet drain in the attic.

Thanks,

Craig Barger
Attached Thumbnails
can-anyone-tell-me-tank-attic-picture-100-year-old-house-100_0494.jpg  
Reply With Quote
  #2  
Old 7/24/08, 8:02 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Can anyone tell me what the tank is in this attic picture? 100 year old house.

LINK

Old Heating Boilers (steam or hot water) may have No Relief Valve at All - Check the Attic



Some very old heating boilers may not have a relief valve installed.
These systems used a pressure relieving overflow tank located high in the building, above any upper floor radiators or baseboards, often in the building attic.
The attic pressure tank was open to the atmosphere and often itself included an overflow pipe which would permit any excess water (or pressure) to flow out of the tank and out of the building, perhaps through a building wall to the outdoors.
While these attic systems for boiler pressure relief safety worked well for decades, placing a temperature relief valve right on or very close to the heating boiler is a safer installation.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]

Last edited by mlarson; 7/24/08 at 8:07 PM..
Reply With Quote
  #3  
Old 7/24/08, 8:05 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Can anyone tell me what the tank is in this attic picture? 100 year old house.

Quote:
Originally Posted by cbarger
Can anyone tell me what the tank is in this attic picture?
The house is a 1900 house.
It appears the tank is attached to a wet drain in the attic.

Thanks,

Craig Barger
Looks like an old boiler expansion tank.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 7/24/08, 8:05 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Can anyone tell me what the tank is in this attic picture? 100 year old house.

And this

Q: What does an expansion tank look like?
A: A typical one looked like this. LINK

Q: Where did the expansion tank go?
A: Typically, at the high point of the system. You'll usually find them in the attic. The tank gives the expanding and contracting water a place to rise and fall.
Q: Suppose I put too much water into the system when I first fill it up. What will happen?
A: It will overflow from the tank through its vent and wind up on the roof.
Q: Can this do any harm?
A: Not to the system. It might leave some rust stains on the roof if the system is old, but that's about it.
Q: How much water should I put into the tank when I'm first filling the system?
A: Normally, you should maintain the tank at one-third full when the water is cold (there's often a gauge glass on the side of the tank so you can see what you're doing). As the water heats and expands, it will rise into the upper two-thirds of the tank and stop before spilling over onto the roof.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #5  
Old 7/24/08, 8:26 PM
cbarger cbarger is offline
InterNACHI Member
 
Join Date: May 2008
Location: Pueblo West, Co
Posts: 6
Default Re: Can anyone tell me what the tank is in this attic picture? 100 year old house.

Nice. Thanks guys.
Appreciate it.

Craig
Reply With Quote
  #6  
Old 7/24/08, 9:39 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Can anyone tell me what the tank is in this attic picture? 100 year old house.

Quote:
Originally Posted by mlarson
And this

Q: What does an expansion tank look like?
A: A typical one looked like this. LINK




Q: Where did the expansion tank go?
A: Typically, at the high point of the system. You'll usually find them in the attic. The tank gives the expanding and contracting water a place to rise and fall.
Q: Suppose I put too much water into the system when I first fill it up. What will happen?
A: It will overflow from the tank through its vent and wind up on the roof.
Q: Can this do any harm?
A: Not to the system. It might leave some rust stains on the roof if the system is old, but that's about it.
Q: How much water should I put into the tank when I'm first filling the system?
A: Normally, you should maintain the tank at one-third full when the water is cold (there's often a gauge glass on the side of the tank so you can see what you're doing). As the water heats and expands, it will rise into the upper two-thirds of the tank and stop before spilling over onto the roof.
These were called "open systems" up here. Have only seen 2 in my 26 years of inspecting. Last one, the tank was mounted over the bath vanity with the drain going up into the attic and out to the eaves. The original cast iron boiler was still operating but with an efficiency of only 62-63% (I test furnace/boiler efficiency as part of my inspections).
Reply With Quote
  #7  
Old 7/24/08, 10:43 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Can anyone tell me what the tank is in this attic picture? 100 year old house.

Steam Boiler head pressure tank.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #8  
Old 7/24/08, 11:57 PM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: Can anyone tell me what the tank is in this attic picture? 100 year old house.

Nice call Mike. Took a few of them out back when I first started working. The great thing I remember is how wonderfully light and easy to get down the stairs they were.



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #9  
Old 7/25/08, 1:57 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Can anyone tell me what the tank is in this attic picture? 100 year old house.

Quote:
Originally Posted by Brian A. MacNeish
These were called "open systems" up here. Have only seen 2 in my 26 years of inspecting. Last one, the tank was mounted over the bath vanity with the drain going up into the attic and out to the eaves. The original cast iron boiler was still operating but with an efficiency of only 62-63% (I test furnace/boiler efficiency as part of my inspections).
Agreed, they are an expansion tank, but not a pressure tank, "open system" is what I would call it.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #10  
Old 7/25/08, 10:05 AM
dhelm's Avatar
dhelm dhelm is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Bellingham, Wa
Posts: 704
Default Re: Can anyone tell me what the tank is in this attic picture? 100 year old house.

Aw come on. You guys never seen a bootleggers attic? Obviously the original owner was makin' shine!



Helm Home Inspection
David Helm, Owner/Inspector
http//www.helmhomeinspections.com
Reply With Quote
  #11  
Old 7/26/08, 5:48 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Can anyone tell me what the tank is in this attic picture? 100 year old house.

Such an arrangement worked well because the operating pressure of those old boilers was very low (could not be greater that the weight of the water in the system up to the discharge). If you were operating a 'boiler' at such a pressure today that would still be a very effective 'overpressure' arrangement.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Stupid ASHI legislatin in Washington DEAD. gromicko Legislation, Licensing & Legal Issues for Inspectors 20 1/29/08 9:05 AM
House with Septic Tank.... gbrasseur Plumbing Inspections 4 11/5/06 8:09 AM
Family's house is infested with mold rspriggs Ancillary Inspection Services & Additional Topics 6 1/28/06 2:05 AM


All times are GMT -4. The time now is 8:41 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts