Exclamation Can a TPR valve discharge to a water heater pan???

2009 IRC change highlighted below:

"P2803.6.1 Requirements for discharge pipe. The discharge
piping serving a pressure-relief valve, temperature relief
valve or combination valve shall:

1. Not be directly connected to the drainage system.
2. Discharge through an air gap located in the same
room as the water heater.
3. Not be smaller than the diameter of the outlet of the
valve served and shall discharge full size to the air
gap.
4. Serve a single relief device and shall not connect to
piping serving any other relief device or equipment.

5. Discharge to the floor, to the pan serving the
water heater
or storage tank, to a waste receptor
or to the outdoors.


6. Discharge in a manner that does not cause personal
injury or structural damage.
7. Discharge to a termination point that is readily
observable by the building occupants.
8. Not be trapped.
9. Be installed to flow by gravity.
10. Not terminate more than 6 inches (152 mm) above
the floor or waste receptor.
11. Not have a threaded connection at the end of the piping.
12. Not have valves or tee fittings.
13. Be constructed of those materials listed in Section
P2904.5 or materials tested, rated and approved for
such use in accordance with ASME A112.4.1. 438"



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/16/10, 8:49 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Can a TPR valve discharge to a water heater pan???

Didn't you answer your own question???
Reply With Quote
  #3  
Old 9/16/10, 8:57 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Can a TPR valve discharge to a water heater pan???

Quote:
Originally Posted by jjonas View Post
Didn't you answer your own question???
I think that was the point of the thread... It's been discussed here several times, and the conclusion was that it couldn't. Apparently now there is a change that allows it.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #4  
Old 9/16/10, 9:04 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Can a TPR valve discharge to a water heater pan???

Quote:
Originally Posted by mnahrgang View Post
I think that was the point of the thread... It's been discussed here several times, and the conclusion was that it couldn't. Apparently now there is a change that allows it.
Okay, thought it was a strange question for Joe to be asking, but sometimes one never knows.
Reply With Quote
  #5  
Old 9/16/10, 10:35 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Can a TPR valve discharge to a water heater pan???

Prohibited in CA.

2010 CPC 508.5 Relief Valve Discharge. Discharge from a relief valve into a water heater pan shall be prohibited.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 9/16/10, 2:40 PM
Jim Kolke's Avatar
Jim Kolke Jim Kolke is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Wilmette, Illinois
Posts: 58
Default Re: Can a TPR valve discharge to a water heater pan???

Dont really understand why they wouldnt allow the drain to dump into a pan. Its still going to a drain.
Reply With Quote
  #7  
Old 9/16/10, 3:07 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Can a TPR valve discharge to a water heater pan???

Quote:
Originally Posted by jkolke1 View Post
Dont really understand why they wouldnt allow the drain to dump into a pan. Its still going to a drain.
I think it's a question of volume. If a TPR discharges it's going to be under pressure. While the drain in the pan is likely the same size as the TPR discharge, it is only gravity fed. Therefore the pan will fill up and overflow.

In my opinion it really isn't going to matter much one way or the other. If the TPR is dripping, the pan will be sufficient. If it's discharging, it's going to be splashing all over everything anyway, so the pan is going to likely be redundant.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #8  
Old 9/16/10, 4:13 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Can a TPR valve discharge to a water heater pan???

Quote:
Originally Posted by jjonas View Post
Didn't you answer your own question???
Yes. I knew the answer. (Did you?) I was trying to be helpful.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 9/16/10, 4:16 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Can a TPR valve discharge to a water heater pan???

Quote:
Originally Posted by mnahrgang View Post
I think that was the point of the thread... It's been discussed here several times, and the conclusion was that it couldn't. Apparently now there is a change that allows it.
Exactly.

Ben Gromicko even has a training package somewhere that say's it's prohibited because the pan doesn't meet the definition of a waste receptor because the size of the drain pipe wouldn't be able to accommodate a full discharge from the water heater. At least, that was the logic. I suppose the plumber and home builder's lobby got it changed.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 9/16/10, 6:51 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Can a TPR valve discharge to a water heater pan???

Here is an advanced question involving #4 of the 2009 code posted above....

4. Serve a single relief device and shall not connect to
piping serving any other relief device or equipment.



What if you see that the TPR is dumping into a larger pipe that also has the washer safety pan feeding into it at some other point?

The question is not about "will it handle the flow" but simply "does it meet the intent of the code".



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #11  
Old 9/16/10, 10:27 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Can a TPR valve discharge to a water heater pan???

The plumber would not waste their time or money running it to the exterior if it could just be dumped in the overflow pan.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sulphur smell bsmith Plumbing Inspections 2 6/6/08 8:32 PM
Water Heater Pressure Valve wrosario Plumbing Inspections 3 7/7/06 7:27 PM
small valve on cold water supply ahead of water heater? Walt Hoffman Plumbing Inspections 6 1/23/06 7:44 AM


All times are GMT -4. The time now is 2:13 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts