Default Can you use copper Flex

Can you use copper flex pipping for the TPRV drain line. It extends down for about a foot connects to regular copper pipping and then out to the exterior.
First time I have seen this.
Reply With Quote
  #2  
Old 5/20/08, 11:49 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Can you use copper Flex

I personaly would not have a problem.
Reply With Quote
  #3  
Old 5/20/08, 12:01 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Can you use copper Flex

Quote:
Originally Posted by sjohns
Can you use copper flex pipping for the TPRV drain line. It extends down for about a foot connects to regular copper pipping and then out to the exterior.
First time I have seen this.
If it's 3/4" and not kinked I would have no problem with it.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #4  
Old 5/20/08, 4:08 PM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: Can you use copper Flex

See the TPR mini course.
http://www.nachi.org/waterheaterdisc...leased2007.htm



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #5  
Old 5/20/08, 5:26 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Can you use copper Flex

Technically, the answer is No, you should not use the common flexible water supply connector such as a BrassCraft BD00 but you do see it quite often. As an example, a typical Cash Acme T&P valve will discharge at a pressure of 175 psi and/or a temperature of 210°F. The BrassCraft flexible copper connector is rated at 125 psi at 180°. So, you can easily see where the water being discharged could exceed the operating characteristics of the flex connector. The argument, although weak, is that the temperature and/or pressure would only be present for a short period of time. Well, that's the rub isn't it? How long is too long? 1 second, 10 seconds, a minute? I admit that it does make for a nice looking installation but I'm of the opinion that it is not proper.

Here's a snippet from the BrassCraft catalog re: copper flex connectors:
can-you-use-copper-flex-capture.jpg
Reply With Quote
  #6  
Old 5/20/08, 5:49 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Can you use copper Flex

The pressure you speak of does not account for the fact there is flow.
If it was flex on its own I would be more concerned with movement of the pipe.
175 is the pressure if capped
Reply With Quote
  #7  
Old 5/20/08, 8:44 PM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: Can you use copper Flex

Describe exactly what you mean by flex. Are you talking soft copper or other and how is it connected to the hard copper?



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #8  
Old 5/21/08, 12:22 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Can you use copper Flex

In my neck of the woods, the answer is no. I had it confirmed a few weeks ago by a local AHJ and two plumbers.



NACHI 2005 U.S. Member of the Year

Last edited by rray; 5/21/08 at 1:42 PM..
Reply With Quote
  #9  
Old 5/21/08, 11:41 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Can you use copper Flex

Quote:
Originally Posted by rray
In my neck of the woods, the answer is now. I had it confirmed a few weeks ago by a local AHJ and two plumbers.
Not allowed by the CPC (UPC). Not now, not ever



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 5/21/08, 11:44 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Can you use copper Flex

Quote:
Originally Posted by jpope
Not allowed by the CPC (UPC). Not now, not ever
Jeff, do mean soft copper or corrugated flex?

Can you post the relevant portion of the CPC(UPC)



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #11  
Old 5/21/08, 11:46 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Can you use copper Flex

I'll take marketing for $500 Russel...

Quote:
Originally Posted by rray
the answer is now.
Buzz, Buzz..

RR, "Yes, Rick"

What is, When do you you want your phone to ring?

Reply With Quote
  #12  
Old 5/21/08, 1:44 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Can you use copper Flex

Quote:
Originally Posted by jpope
Not allowed by the CPC (UPC). Not now, not ever
ROTFLMAO. My VRS made one of its few errors, inserting "know" for "no." I manually went and corrected it by deleting that stupid K. I didn't realize that W's could be so problematic.

Corrected my previous post. Thanks, Jeff.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #13  
Old 5/21/08, 1:45 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Can you use copper Flex

Quote:
Originally Posted by rmaday
I'll take marketing for $500 Russel...



Buzz, Buzz..

RR, "Yes, Rick"

What is, When do you you want your phone to ring?

I just got in from a rough 7:00 a.m. inspection, so I needed this humor!



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #14  
Old 5/21/08, 4:30 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Can you use copper Flex

Quote:
Originally Posted by mlarson
Jeff, do mean soft copper or corrugated flex?

Can you post the relevant portion of the CPC(UPC)

608.5 Relief valves located inside a building shall be provided with a drain, not smaller than the relief valve outlet, of galvanized steel, hard drawn copper piping and fittings, CPVC, or listed relief valve drain tube with fittings which will not reduce the internal bore of the pipe or tubing (straight lengths as opposed to coils) and shall extend from the valve to the outside of the building with the end of the pipe not more than two (2) feet (610 mm) nor less than six (6) inches (152 mm) above the ground or the flood level of the area receiving the discharge and pointing downward. Such drains may terminate at other approved locations. No part of such drain pipe shall be trapped or subject to freezing. The terminal end of the drain pipe shall not be threaded.




IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
flex copper and LPG kgerhauser Plumbing Inspections 6 4/19/08 9:40 PM
Tinned copper & Copper mnahrgang Electrical Inspections 2 3/13/08 6:21 PM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 8:10 AM
Bathroom Shut-off Valves - Mineral deposits - Do you note them as leaking in reports? jwatts1 Plumbing Inspections 8 7/29/06 11:50 AM
Looking for comment by Caoimhín P. Connell phinsperger Ancillary Inspection Services & Additional Topics 2 2/18/06 11:22 AM