InterNACHI


Go Back   InterNACHI Message Board > Specific Inspection Topics > Plumbing

Notices

Plumbing Contains discussions about plumbing.

Reply
 
LinkBack Thread Tools
  #16  
Old 5/8/09, 8:11 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,753
Default Re: Closed plumbing systems & expansion tanks

Quote:
Originally Posted by jfunderburk View Post
A builder of a new home is claiming that there is no backflow preventor present on the home and thus no expansion tank is required.

Isn't a backflow preventor integrated into this pressure reducer? Notice the one-way arrow.

Attachment 28482 Attachment 28483
The arrow indicates flow, but does not necessarily indicate ONE WAY flow.

I usually call this a regulator, but that is not important. High pressure enters the up stream side and the pressure is reduced passing thorough the device to an acceptable pressure.

Now, if for any reason the pressure is raised on the down stream side (house side) of the regulator there is no way for it to go back wards through the regulator until the pressure over comes the up stream side (Street side) pressure. And more than likely that is a LOT pressure to overcome or a regulator would not have been installed in the first place.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
Find an InterNACHI certified New Hampshire Home Inspector (and anywhere else in North America)
  #17  
Old 5/8/09, 8:39 PM
Jonathan T. Hittle's Avatar
Jonathan T. Hittle Jonathan T. Hittle is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Eaton, OH
Posts: 94
Talking Re: Closed plumbing systems & expansion tanks

THERMAL EXPANSION CONSIDERATIONS
Installing a pressure reducing valve creates a closed water system. Thermal expansion occurs
in a closed system when water is heated and pressure builds up. A thermal by-pass designed
into the reducing valve can dissipate the expanded pressure back to the service main.
When the system pressure in a closed system increases to a pressure greater than the supply
pressure by just one pound, the o-ring on the stem will flex (see Fig. A) and allow the excess
pressure to be relieved to the supply side until pressures on both the system and supply sides
are equal. When a faucet on the system side in used, thus lowering the pressure, the valve
opens as soon as the system pressure falls below the set outlet pressure, typically 50 lbs.
The valve and the system then return to normal as shown in Fig. B above. The PRVH features
a ball and seat type of check valve as a thermal by-pass but the principle is similar.


I have a State of Ohio Backflow license and I thought I would put in my two cents. Remember backflow requirements vary by municipality and state.
Reply With Quote
  #18  
Old 5/8/09, 8:53 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,224
Default Re: Closed plumbing systems & expansion tanks

When did the IRC start requiring a thermal expansion device? 2003?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #19  
Old 5/8/09, 9:48 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,831
Send a message via Yahoo to jfunderburk
Default Re: Closed plumbing systems & expansion tanks

Quote:
Originally Posted by bking View Post
When did the IRC start requiring a thermal expansion device? 2003?
It's in the '03 IRC. Here's how it's worded there (P2903.4):

"...an approved device for thermal expansion control shall be installed on any water supply system utilizing storage water heating equipment whenever the building supply pressure exceeds the pressure-reducing valve setting or when any device, such as a pressure-reducing valve, backflow preventer or check valve, is installed that prevents pressure relief through the building supply..."

That's worded differently from 06. If I had read that first, it would have answered my question. Seems plain that a pressure reducer requires a thermal expansion device.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #20  
Old 5/8/09, 9:50 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,753
Default Re: Closed plumbing systems & expansion tanks

Quote:
Originally Posted by jfunderburk View Post
It's in the '03 IRC. Here's how it's worded there (P2903.4):

"...an approved device for thermal expansion control shall be installed on any water supply system utilizing storage water heating equipment whenever the building supply pressure exceeds the pressure-reducing valve setting or when any device, such as a pressure-reducing valve, backflow preventer or check valve, is installed that prevents pressure relief through the building supply..."

That's worded differently from 06. If I had read that first, it would have answered my question. Seems plain that a pressure reducer requires a thermal expansion device.

Thanks Joe, I did not want to leave my chair.

And I read it the same as you do.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #21  
Old 5/9/09, 10:06 AM
Timothy D. Saunders Timothy D. Saunders is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Sharpsburg, Md
Posts: 13
Default Re: Closed plumbing systems & expansion tanks

Orange piping is usually reserved for fire suppression systems. If the label on the piping is NIBCO, they are a manufacture of fire sprinkler system piping
Usually the water service would be black.
Very strange
Reply With Quote
  #22  
Old 5/9/09, 10:23 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,442
Default Re: Closed plumbing systems & expansion tanks

Well the valve you had shown does not have a back flow with it
Some come with one , Some even have a pressure relief valve. I would say a thermal tank will be in order . The arrow shows the direction of flow some what like valves . Ever seen a valve put in back wards It will reduce flow a fair bit.
Reply With Quote
  #23  
Old 5/9/09, 10:31 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,831
Send a message via Yahoo to jfunderburk
Default Re: Closed plumbing systems & expansion tanks

Quote:
Originally Posted by tsaunders View Post
Orange piping is usually reserved for fire suppression systems. If the label on the piping is NIBCO, they are a manufacture of fire sprinkler system piping
Usually the water service would be black.
Very strange
It's PEX isn't it? Is there anything wrong with using it for residential potable water?



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #24  
Old 5/9/09, 10:36 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,831
Send a message via Yahoo to jfunderburk
Default Re: Closed plumbing systems & expansion tanks

Here's something you may wish to use. No charge. Modify to suit your needs.

"The water heater does not have an approved device for thermal control installed (an expansion tank or pressure relief valve). The device's purpose is to prevent spikes in water pressure due to water heating that could damage the internal components of a water heater, cause a leak at the temperature-pressure relief valve, or cause a leak at plumbing fittings elsewhere in the home. Recent changes in today's commonly accepted standards require such a device when a new water heater is installed, but there is no standard that requires an upgrade to an existing unit. Regardless, installation of a thermal expansion control device is recommended to prevent the types of damage described above. A reference document about expansion tanks is attached at the end of this report for your information."

Here's an attachment I include with my reports when I cite this: http://www.aohomeinspection.com/pdf/...on-control.pdf



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 5/9/09 at 10:42 AM..
Reply With Quote
  #25  
Old 5/9/09, 3:53 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 489
Default Re: Closed plumbing systems & expansion tanks

good call on the orange line. i believe it is fire suppression



Bruce Thompson
Professional Inspector, Lic. #9199
Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area.
www.TylerHomeInspector.com
NACHI 06081394
Reply With Quote
  #26  
Old 5/9/09, 4:06 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 489
Default Re: Closed plumbing systems & expansion tanks

Ok, now I'm not sure. I vaguely remember fire suppression piping using glued joints.

Anyone else got any ideas? Obviously a fire suppression system (if the house had one) would need to be regulated just as the potable system.



Bruce Thompson
Professional Inspector, Lic. #9199
Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area.
www.TylerHomeInspector.com
NACHI 06081394
Reply With Quote
  #27  
Old 5/9/09, 5:20 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,224
Default Re: Closed plumbing systems & expansion tanks

Thats Red Nibco Durapex, lots of used in homes around here, actually the best PEX on the market IMO.

http://www.nibco.com/assets/PEX%20Spools%20NPI.pdf

Look at all of Joe's picture, you can see how it looks redder in some areas, it is kinda orange but the flash on most cameras really makes it look bright orange.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #28  
Old 5/9/09, 7:27 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,753
Default Re: Closed plumbing systems & expansion tanks

Quote:
Originally Posted by tsaunders View Post
Orange piping is usually reserved for fire suppression systems. If the label on the piping is NIBCO, they are a manufacture of fire sprinkler system piping
Usually the water service would be black.
Very strange

NIBCO makes everything.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues 293 2/10/08 2:20 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 6:58 PM
Emergency Lighting (commercial) mcyr Electrical 24 6/10/06 11:06 AM


All times are GMT -4. The time now is 10:49 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts