Default Code Ref for TPR valve piping?

Hi again.

Does anyone have a UPC code reference for approved piping material for TPR valve piping? It is my understanding that PVC does not meet the minimum temperature requirements and that CPVC does. Quick glance netted nothing in the IRC.

Thanks
Attached Thumbnails
code-ref-tpr-valve-piping-kowalczyk-inspection-042-small-.jpg.jpg
Views:	151
Size:	31.2 KB
ID:	5647  

Last edited by hspinnler; 9/20/06 at 12:04 AM.. Reason: Pic added
Reply With Quote
  #2  
Old 9/20/06, 12:46 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: Code Ref for TPR valve piping?

UPC 608.5 Relief valves located inside a building shall be provided with a drain, not smaller than the relief valve outlet, of galvanized steel, hard drawn copper piping and fittings, CPVC, or listed relief valve drain tube with fittings which will not reduce the internal bore of the pipe or tubing (straight lengths as opposed to coils) and shall extend from the valve to the outside of the building with the end of the pipe not more than two (2) feet (610 mm) nor less than six (6) inches (152 mm) above the ground or the flood level of the area receiving the discharge and pointing downward. Such drains may terminate at other approved locations. No part of such drain pipe shall be trapped or subject to freezing. The terminal end of the drain pipe shall not be threaded.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 9/20/06, 12:47 AM
David E. Helm's Avatar
David E. Helm David E. Helm is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Bellingham, Wa
Posts: 689
Default Re: Code Ref for TPR valve piping?

Don't know the code but that line looks like it goes uphill. Would certainly call that out.



Helm Home Inspection
David Helm, Owner/Inspector
http//www.helmhomeinspections.com
Reply With Quote
  #4  
Old 9/20/06, 12:51 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: Code Ref for TPR valve piping?


IRC P2803.6.2 Relief valve drains. Relief valve drains shall comply with Section P2904.5 or ASME A112.4.1.


IRC P2904.5 Water-distribution pipe. Water-distribution piping within dwelling units shall conform to NSF 61 and shall conform to one of the standards listed in Table P2904.5. All hot-water-distribution pipe and tubing shall have a minimum pressure rating of 100 psi at 180°F (689 kPa at 82°C).




IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 9/20/06, 1:14 AM
hspinnler's Avatar
hspinnler hspinnler is offline
Active Poster
 
Join Date: Apr 2005
Location: Hoschton, GA
Posts: 146
Please Note: hspinnler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Ref for TPR valve piping?

Thanks David & Jeff. Those quick code reference listings are helpful Jeff. I do have the book open and read those passages.

Something else I want to bring up. As IRC states in 2803.6.1 Relief valve drains. The discharge pipe shall be installed so as to drain by gravity flow and shall terminate atmospherically not more than 6" above the floor.

I often see installations where piping from TPR valve(usually 3/4" copper) has one or more 90 degree turns before heading upward towards the main floor (when in basement) A certain percentage of time there is no cleanout or "bleeder" valve and I call that out.

Now, if the code refs. state slope to drain and you're in a location like a basement where this is not possible, this is where a Watts 210 valve must be used? I'm asking because the valve in the photo is a Watts 100XL. http://www.watts.com/pdf/ES-10L-100XL.pdf
Reply With Quote
  #6  
Old 9/20/06, 1:14 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: Code Ref for TPR valve piping?

Here is the reference table. . .
Attached Files
File Type: pdf 2003 IRC.pdf (30.2 KB, 164 views)



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #7  
Old 9/20/06, 12:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: Code Ref for TPR valve piping?

Quote:
Originally Posted by hspinnler
Now, if the code refs. state slope to drain and you're in a location like a basement where this is not possible, this is where a Watts 210 valve must be used?
The Watts valve in your photo is a standard "temperature and pressure relief" valve. When the temp or pressure becomes excessive, the valve will relieve that pressure, as often as is necessary.

The Watts 210 is a gas shutoff valve and relies only on temperature, and must be manually reset once it has operated. A pressure relief valve is required to be used in combination with the Watts 210.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 9/20/06 at 12:08 PM..
Reply With Quote
  #8  
Old 9/20/06, 10:31 PM
whandley's Avatar
whandley whandley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,104
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Code Ref for TPR valve piping?

Hey Jeff,

Most of the building departments I deal with want a TPR valve drain line to terminate no more than 6" above grade and or the waste receptor. They do allow condensation drain lines to terminate from 6" to 24" above grade.


504.6 Requirements for discharge piping.
The discharge
piping serving a pressure relief valve, temperature relief valve
or combination thereof shall:
1. Not be directly connected to the drainage system.
2. Discharge through an air gap located in the same room
as the water heater.
3. Not be smaller than the diameter of the outlet of the
valve served and shall discharge full size to the air gap.
4. Serve a single relief device and shall not connect to piping
serving any other relief device or equipment.
5. Discharge to the floor, to an indirect waste receptor or
to the outdoors. Where discharging to the outdoors in
areas subject to freezing, discharge piping shall be first
piped to an indirect waste receptor through an air gap
located in a conditioned area.
6. Discharge in a manner that does not cause personal
injury or structural damage.
7. Discharge to a termination point that is readily observable
by the building occupants.
8. Not be trapped.
9. Be installed so as to flow by gravity.
10. Not terminate more than 6 inches (152 mm) above the
floor or waste receptor.
11. Not have a threaded connection at the end of such piping.


Reply With Quote
  #9  
Old 9/20/06, 11:21 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: Code Ref for TPR valve piping?

Quote:
Originally Posted by whandley
Most of the building departments I deal with want a TPR valve drain line to terminate no more than 6" above grade and or the waste receptor. They do allow condensation drain lines to terminate from 6" to 24" above grade.
In the state of CA, unincorporated cities/townships fall under the authority/jurisdiction of the Building Standards Commission and the Division of the State Architect. In such cases, CPC 608.5 defines the requirements for the termination of the discharge piping - not more than two (2) feet (610 mm) nor less than six (6) inches (152 mm) above the ground.

Most areas I know of in CA, follow this code as part of the 2001 California Code of Regulations, Title 24.

Your reference is from the International Plumbing Code (IPC) which is part of the International Residential Code (IRC). I don't know of any jurisdictions in CA that follow the "I" codes.

Is the OC following the I codes?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 9/20/06 at 11:24 PM..
Reply With Quote
  #10  
Old 2/16/07, 4:04 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 1,216
Default Re: Code Ref for TPR valve piping?

What do you say about an extension pipe coming off a tp valve on a hot water tank that you can not identify. I saw one today. PVC, but the labeling was scratched out or worn out. What is the actual language that you would use in your report?
In my report, I caused an uproar, because I recommended that since I could not determine that it was safe that the extension pipe on the tp valve be replaced.
Reply With Quote
  #11  
Old 2/16/07, 10:39 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Code Ref for TPR valve piping?

Quote:
Originally Posted by bgromicko
What do you say about an extension pipe coming off a tp valve on a hot water tank that you can not identify. I saw one today. PVC, but the labeling was scratched out or worn out. What is the actual language that you would use in your report?
In my report, I caused an uproar, because I recommended that since I could not determine that it was safe that the extension pipe on the tp valve be replaced.
I'm not sure I understand. You say you couldn't identify it. Then you said it was PVC.

What labeling?

How was it unsafe?

P.S. Are you related to Nick?
Reply With Quote
  #12  
Old 5/30/07, 9:13 PM
Justin Watts Justin Watts is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Rancho Santa Margarita, CA
Posts: 762
Default Re: Code Ref for TPR valve piping?

Hey Guys,
Here is an issue... I have been wrestling with. How about T and P discharge pipes that discharge "lateral" across with little or (no) slope then discharge downward... You will see these at the top of water heaters.

I think it is a major safety issue that a lot of licensed plumbers even overlook when installing water heaters and TP valves. Slope is required for the discharge pipe and quite often its not there!

Do you guys often encounter this???
Curious...
Justin
www.americandreamhomeinspection.net
Reply With Quote
  #13  
Old 5/31/07, 12:42 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,753
Default Re: Code Ref for TPR valve piping?

As long as it is not plumbed up hill it is ok.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #14  
Old 5/31/07, 1:01 AM
William R. DeVries, CMHI's Avatar
William R. DeVries, CMHI William R. DeVries, CMHI is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Kingston
Posts: 852
Default Re: Code Ref for TPR valve piping?

TPPRV Drain Piping Max of 4 90deg elbows & max 30ft
When the water heater is in a basement or below grade, it may not be possible to arrange for a gravity drain of the TPRV. A Watts 210 valve can be installed. The temperture-sensing bulb of the valve goes in the upper portion of the tank, and the gas piping runs through the valve. The Watts 210 shuts off the gas it the temperture is in excessive. In addition a seperate water pressure relif valve must be installed in the piping and must drain as shown

Not sure if this answers your question but I thought I'd give it a whirl as i get so many answers from here
Billy
Attached Thumbnails
code-ref-tpr-valve-piping-scan0001.jpg  



Certified Level I Thermography (ITC)
Certified Mold Inspector (Pro-Lab)
Certified Mold Inspector IAC2
Certified Home Inspector INACHI 07040201
Commercial Property Inspection
2008 InterNACHI member of the year



Magnum Property Inspection
Inspect it before you buy it
647 217 8473

We use and recommend
Home Inspector Pro Software
HomeGauge Software

Last edited by wdevries; 5/31/07 at 1:06 AM..
Reply With Quote
  #15  
Old 5/31/07, 3:16 AM
Justin Watts Justin Watts is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Rancho Santa Margarita, CA
Posts: 762
Default Re: Code Ref for TPR valve piping?

Yes, I have seen that Code Check diagram.... they are great references for code.

As for the "lateral" line... I think it could still pose a "possible" safety hazard especially if corrosion or mineral encrustation clogs the lateral line after extended time maybe years of dripping... the water could lead back to the valve and cause failure. I am not sure how much testing has been done. But liability could be an issue here....

Especially since the code states the T and P discharge line is "required" to have slope...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
No "H" clips? jbreazeale Structural 7 5/17/07 3:28 PM
Newbie here with a slab "standards" question Robert Young, #3 Structural 17 4/10/07 11:48 AM


All times are GMT -4. The time now is 2:02 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts