Hey guys and Gals. If someone can give me some guidence, it would take a huge weight off my shoulders.
Essentially my pipes are banging in a two story condo, whenever any fixture is turned off. Found out from the previous owner. That up until 10 years ago the condo had PB pipe. When it ruptured all the pipes in the condo were changed to copper. Apparently the pipes have been banging for ten years. (yeesh) So this is where I'm at. Pipes bang at the same place when any fixture is turned off (but given it is a two story condo. I cant narrow the exact location down since its somewhere near the stairwell. So instead of tearing the walls apart, I installed an air chamber @ the hot water heater. Well, this worked for about two days and then the banging returned. (Figured it just flooded) I Checked the pressure and it is @ 60 psi. (which seems normal) If I decrease it to 40 or so psi by closing the ball valve the banging will go away. I guess my question is. Since the pressure seems normal. Is it probably just a loose/unstrapped pipe? And even if that is the case, since a simple air chamber made it go away for a couple of days. Would taking it out and replacing it with either an arrestor or expansion tank be the way to go? Any ideas would be greatly appreciated. Since, short of tearing the walls down, I really don't know which way to go. Thanks all |
| Need a home inspection in Pennsylvania? Check out InterNACHI's listing of Pennsylvania certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#3
|
||||
|
||||
|
You may have some unsecured piping, but have you considered installing hammer-arrestors? No special tools required...
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
||||
|
||||
|
There are now quick fixes for water hammer in plumbers mags.
They are designed to install under the sink to the main shut off for each fixture. If you can isolate which one by purchasing the unit and testing the lines you are good to go. You do not need a plumber to do this kind of work since it is part of a threaded flex braid steel line to the hot and cold with the water hammer chamber attached. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#5
|
|||
|
|||
|
Please Note:
Jonathon Bennett is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks for the reply Jeffrey. Yeah, actually I did. I put them upstairs at the washer. Thats another funny thing. It seemed after I installed them, the knock/banging seemed to be worse/harder. Also, to reiterate the situation, regardless of the fixture, all cold lines hammer when shut off. However, if I go out to the main ball valve and close it half way, the hammer is gone. Pressure is lowered somewhat, but still O.K. However, it's a small condo with terrible insulation. So it prolongs things like toilet fills. (Since it adds another 20-30 seconds)
|
|
#6
|
|||
|
|||
|
Please Note:
Jonathon Bennett is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#7
|
|||
|
|||
|
Please Note:
Jonathon Bennett is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Thanks a million, And I hope you follow this with the forthcoming pics |
|
#8
|
||||
|
||||
|
According to what you say. You should be able to put a pressure reducer on the main going to the Hot water tank.
10 PSI reduction may get rid of the water hammer. It takes 0.434 psi to raise water one foot. Conversely, one psi will raise water 2.31 feet. If water enters the basement at 60 psi static pressure, there will be 60 psi pressure near the basement floor. To move up through the basement, through the first floor, and to the shower on the second floor, we might have to push the water up 20 feet. This would result in a pressure loss of between 8 and 9 psi (20 X 0.434). 42 psi is what you will have left over. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Confused. | Kathleen Luuk | Canadian Inspectors | 79 | 4/19/11 9:06 AM |
| I am a little confused about footings and foundations | dpant | Structural Inspections | 22 | 1/6/11 1:04 AM |
| Confused by air intake and flue setup | belliott | Inspecting HVAC Systems | 24 | 8/10/09 8:44 PM |
| I'm confused & need your opinions | dplummer | Canadian Inspectors | 27 | 6/14/06 9:54 PM |