Old 8/9/09, 10:24 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 794
Default Corrugated Drain

Is this type of corrugated drain acceptable?
Attached Thumbnails
corrugated-drain-p8090100.jpg  



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
Find an InterNACHI certified Georgia Home Inspector (and anywhere else in North America)
  #2  
Old 8/9/09, 10:59 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Corrugated Drain

Absolutely not. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 8/9/09, 11:19 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 794
Default Re: Corrugated Drain

Thanks for confirming, Jeff.



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #4  
Old 8/9/09, 11:54 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Corrugated Drain

Besides the fact that these "flex pipes" are not approved for drain lines, the one in your picture is actually intended to be a tail piece (vertical), not a trap arm (horizontal).

Improper use of an improper pipe



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 8/10/09, 12:02 AM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 794
Default Re: Corrugated Drain

Jeff, it begs the question-If they are not approved for drain lines, then why do they even make them? Why make something that can mess up a system? I agree with you, I didn't like it when I saw it.



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #6  
Old 8/10/09, 12:05 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Corrugated Drain

Quote:
Originally Posted by jpope View Post
Besides the fact that these "flex pipes" are not approved for drain lines, the one in your picture is actually intended to be a tail piece (vertical), not a trap arm (horizontal).

Improper use of an improper pipe
Jeff, where is it stated that it's "not approved"? Maybe I need to strengthen my report comment.

All I've ever said about them (if installed as a tailpiece) is this: "The *LOCATION* sink employs an unconventional, flexible, corrugated drainpipe that could contribute to blockages and we do not endorse it."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 8/10/09, 6:47 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Corrugated Drain

Quote:
Originally Posted by mmerino View Post
Jeff, it begs the question-If they are not approved for drain lines, then why do they even make them? Why make something that can mess up a system? I agree with you, I didn't like it when I saw it.
Manufacturers make these as universal drain lines. Homeowners purchase these POS because they refuse to spend their hard earned money on a professional installation by a licensed Plumber.

Homeowners all have one thought in mind.....Why waste my money on a Plumber or even measure, cut and glue a smooth walled PVC waste line when I can purchase a flexible waste line that will easily install in minutes and only set me back a few dollars. Leak fixed.
Reply With Quote
  #8  
Old 8/10/09, 10:37 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Corrugated Drain

Quote:
Originally Posted by jfunderburk View Post
Jeff, where is it stated that it's "not approved"? Maybe I need to strengthen my report comment.
Drain/waste lines are not allowed to be corrugated. They must have smooth wall interior, which is why I said "not approved." I'm headed out this morning, so I don't have time to look up the exact code-language.

Here is how I write it;

Quote:
The *LOCATION* sink employs an unapproved, flexible, corrugated drainpipe that will contribute to blockages and it should be replaced by a qualified plumber.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 8/10/09 at 2:04 PM..
Reply With Quote
  #9  
Old 8/10/09, 11:44 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Corrugated Drain

From the California Plumbing Code and UPC;

PART I – DRAINAGE SYSTEMS

701.0 Materials


701.1
Drainage piping shall be cast iron, galvanized steel, galvanized wrought iron, lead, copper, brass, Schedule 40 ABS DWV, Schedule 40 PVC DWV, extra strength vitrified clay pipe, or other approved materials having a smooth and uniform bore (continued)



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 8/10/09, 12:23 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Corrugated Drain

Not allowed in Illinois plumbing code.

There are plenty of materials that are sold which are not allowed.

Romex is sold in the Chicago area when it is not approved.
PVC TPR piping.
Flex drain pipes.
Mini-Breakers (takes up one panel slot, but has two breakers) not allowed in Chicago, but sold.
Exposed bulb light fixtures.
Foil or vinyl clothes dryer vent tubes. In fact, the two largest appliance retailers, around here, always install the dryers with these vent tubes).

Never underestimate the stupidity of the uninformed public, nor the greed of home improvment store owners.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!

Last edited by wdecker; 8/10/09 at 8:50 PM.. Reason: Spelling. Go figure.
Reply With Quote
  #11  
Old 8/10/09, 12:52 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Corrugated Drain

Thanks guys for the code quote.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 8/10/09, 1:26 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 794
Default Re: Corrugated Drain

Will, what took you so long to post?



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #13  
Old 8/10/09, 8:49 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Corrugated Drain

Quote:
Originally Posted by mmerino View Post
Will, what took you so long to post?
I have been busy doing inspections, writing reports, preparing CE classes and dealing with my youngest, who started drivers ed.

Be afraid! Be VERY afraid!



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
Find an InterNACHI certified Georgia Home Inspector (and anywhere else in North America)
  #14  
Old 8/11/09, 12:09 AM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 794
Default Re: Corrugated Drain

Quote:
Originally Posted by wdecker View Post
I have been busy doing inspections, writing reports, preparing CE classes and dealing with my youngest, who started drivers ed.

Be afraid! Be VERY afraid!
I am staying off the road!!



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
No secondary (pan) drain in Attic Okay per builder mgault Inspecting HVAC Systems 14 1/30/09 8:38 AM
Inspector in hot water after approving unit without drain rcooke Canadian Inspectors 7 2/20/08 3:59 PM
Air leak from floor drain yolhovsky Plumbing Inspections 5 2/24/07 6:43 AM
French drain tied into main drain rwashington Plumbing Inspections 6 2/16/07 11:04 PM


All times are GMT -4. The time now is 8:46 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts