Default Is this csst

From todays inspection.
I found this flex coming out of a central feed black pipe with three of these yellow jacketed guys coming off Ts and feeding straight in the walls to appliances.
Is this ok.?
[ATTACH][ATTACH]corrugated-stainless-steel-tubing-dscn4507-small-.jpg.JPG
Views:	72
Size:	24.8 KB
ID:	19109[/ATTACH][/ATTACH]
Attached Thumbnails
corrugated-stainless-steel-tubing-dscn4509-small-.jpg.JPG
Views:	54
Size:	26.5 KB
ID:	19107   corrugated-stainless-steel-tubing-dscn4510-small-.jpg.JPG
Views:	35
Size:	25.1 KB
ID:	19108  
Reply With Quote
  #2  
Old 3/2/08, 12:10 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Is this csst

Yes, that is CSST. It can be used anywhere you would normally see rigid piping (black iron).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 3/2/08, 12:15 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this csst

That was fast .
Thanks.
Is there one not rated for this that looks the same?
Also I do not know if this is common specs , but peoples gas here in Chicago says it should not terminate directly to the appliance.
Know anything about that.
It is referring to movable verses fixed appliances.
Stoves no
furnace or vent less fire place OK
discrepancy for vent less is apparently due to the fact a log could hit it and cause damage.Sound correct.
Sorry for all the questions but I never dealt with this stuff in walls before and I do not feel good about flammables in walls inside flex.
Reply With Quote
  #4  
Old 3/2/08, 12:31 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Is this csst

IL is an animal of a different color, so there may be some exceptions here, but generally, CSST can be attached directly to appliances, just as with black iron/rigid.

In some jurisdictions, such as CA, a listed appliance connector is still required for most residential applications.

CSST is often confused with "appliance connectors." While they are made from the same or similar materials, they have very different listings and requirements.

Appliance connectors are manufactured in specific lengths with connectors already in place. They are not allowed to pass through walls or appliance cabinets, and cannot be used in concealed locations (within wall cavities or other unaccessible locations) - they are required to be "readily accessible."

CSST piping, on the other hand, can be run in length, through walls and wall cavities, indoors, outdoors, etc., etc., just as you can with steel piping.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 3/2/08, 12:34 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this csst

Correct me if I'm wrong, but I remember right from the TracPipe class I took, CSST is not rated for protection against physical damage. The instructor advised not running it exposed outdoors at or near grade level.
Reply With Quote
  #6  
Old 3/2/08, 12:37 AM
Linas I. Dapkus's Avatar
Linas I. Dapkus Linas I. Dapkus is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Lockport, IL
Posts: 3,730
Default Re: Is this csst

Robert,
Peoples Gas offers a 2 day gas appliance class that is great. Check it out.
Reply With Quote
  #7  
Old 3/2/08, 12:42 AM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,591
Default Re: Is this csst

Quote:
Originally Posted by jpope
In some jurisdictions, such as CA, a listed appliance connector is still required for most residential applications.
What's that?
Do they come in copper?















Sorry, couldn't resist!
</IMG></IMG></IMG>



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #8  
Old 3/2/08, 12:50 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this csst

Thanks guys .
The answers helped me alot.
From that same peoples gas guide Marc is right about outdoor use.
Yes Linus I know all about the great two day class on the near south side.
Hopefully I will have a good spring and dig up the cash.
Remember I just went full time and counting pennies to keep going.
So far I am way ahead of last year , but I gotta tell you there are easier ways to make money.
Goofy me I choose what I enjoy.
EDIT
Marc here is what you refered to

corrugated-stainless-steel-tubing-csst.jpg

Last edited by relliott; 3/2/08 at 12:54 AM..
Reply With Quote
  #9  
Old 3/2/08, 12:53 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,753
Default Re: Is this csst

Quote:
Originally Posted by Marc D. Shunk
Correct me if I'm wrong, but I remember right from the TracPipe class I took, CSST is not rated for protection against physical damage. The instructor advised not running it exposed outdoors at or near grade level.
Correct Marc



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #10  
Old 3/2/08, 12:55 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this csst

Brian see edit pic post 8
Reply With Quote
  #11  
Old 3/2/08, 1:04 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Is this csst

Quote:
Originally Posted by Marc D. Shunk
Correct me if I'm wrong, but I remember right from the TracPipe class I took, CSST is not rated for protection against physical damage. The instructor advised not running it exposed outdoors at or near grade level.
You are correct Marc. CSST does require shielding in some applications.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #12  
Old 3/2/08, 1:05 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,753
Default Re: Is this csst

Quote:
Originally Posted by relliott
Brian see edit pic post 8
Still correct Bob.

I beleive we need you to devise a poll on something soon.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #13  
Old 3/2/08, 1:20 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this csst

Ha hah yes I have been thinking of a few good ideas on that line.
I am a frusterated artist and have been working on trying to invent some thing new for the summer fairs in between posting and drumming up inspections.
Reply With Quote
  #14  
Old 3/3/08, 11:37 AM
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 844
Default Re: Is this csst

Do all brands of CSST pipe need a BONDING wire install?
Reply With Quote
  #15  
Old 3/3/08, 3:34 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Is this csst

CSST, as with all metallic gas piping, is required to be bonded to the electrical system of the building. Some CSST will require additional bonding measures or a supplementary grounding electrode.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Does anyone know anything about corrugated stainless steel tubing (CSST)? gromicko Structural 5 9/28/07 7:24 PM
CSST Fuel Gas Supply jhagarty Plumbing 2 4/24/07 11:38 AM
Csst lcapaul Plumbing 5 3/4/07 2:00 PM
CSST Class Action jhagarty HVAC 21 12/16/06 1:56 AM
CSST gas pipe rtruluck HVAC 2 11/14/06 1:48 PM


All times are GMT -4. The time now is 6:15 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts