Default CSST Fuel Gas Supply

What is the max allowable bend on CSST? Any problem with 90 degree angles?



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member

Last edited by jhagarty; 2/18/08 at 5:34 PM..
Reply With Quote
  #2  
Old 4/24/07, 11:34 AM
gmagee gmagee is offline
New User
 
Join Date: Jan 2004
Location: Monterey, CA
Posts: 45
Please Note: gmagee is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CSST Fuel Gas Supply

http://www.gastite.com/include/langu...IGuide2007.pdf
p. 45
p. 70

Last edited by gmagee; 4/24/07 at 11:36 AM.. Reason: no link
Reply With Quote
  #3  
Old 4/24/07, 11:38 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: CSST Fuel Gas Supply

I just emailed a 105 page Gastite Corp CSST Installation Guide to the e-mail address on your website. It says, on page 45, that for 3/4" CSST the minimum bend radius is 1" and the recommended is 3". Hope that helps. Ooops...Greg beat me to it!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
CSST Class Action jhagarty Inspecting HVAC Systems 31 1/31/12 1:15 AM
No "H" clips? jbreazeale Structural Inspections 7 5/17/07 3:28 PM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 8:47 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 6:58 PM
Emergency Lighting (commercial) mcyr Electrical Inspections 24 6/10/06 11:06 AM


All times are GMT -4. The time now is 2:54 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts