Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information
Send a message via Yahoo to jfunderburk
Default CSST in furnace cabinet

Seems wrong to me. You can't run an appliance connector into a cabinet. Logic would say that CSST should be the same. The manufacturer recommends avoiding sharp edges. I'm writing it up. Anyone disagree?

111408 161.JPG



Joe Funderburk
Alpha & Omega Home Inspections, LLC
Hickory Grove, SC
NACHI ID: NACHI05120170
www.aohomeinspection.com
Reply With Quote
  #2  
Old 11/15/08, 12:10 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,208
Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: CSST in furnace cabinet

Quote:
Originally Posted by jfunderburk View Post
Seems wrong to me. You can't run an appliance connector into a cabinet. Logic would say that CSST should be the same. The manufacturer recommends avoiding sharp edges. I'm writing it up. Anyone disagree?
Nope, they should have run a rigid pipe to the outside of the cabinet and then coupled the CSST.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #3  
Old 11/15/08, 1:09 PM
escanlan escanlan is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Josephine, TX
Posts: 947
escanlan is well trusted escanlan is well trusted escanlan is well trusted
Please Note: escanlan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CSST in furnace cabinet

Gerry,

Can you provide a reference to that? I've been through the IFC, IMC, etc., etc. as a result of a previous find similar to this. The codes allow CSST to penetrate an equipment cabinet as long as it is installed per the manufacturers requirements. Gastite allows its piping to penetrate equipment cabinets if the penetration has a protective bushing or sleeve and the equipment will not cause excessive vibrations or movements that can damage the pipe. I would expect it would depend on what the manufacturer of this CSST extension allows?
Reply With Quote
  #4  
Old 11/15/08, 1:14 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,208
Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: CSST in furnace cabinet

Quote:
Originally Posted by escanlan View Post
Gerry,

Can you provide a reference to that? I've been through the IFC, IMC, etc., etc. as a result of a previous find similar to this. The codes allow CSST to penetrate an equipment cabinet as long as it is installed per the manufacturers requirements. Gastite allows its piping to penetrate equipment cabinets if the penetration has a protective bushing or sleeve and the equipment will not cause excessive vibrations or movements that can damage the pipe. I would expect it would depend on what the manufacturer of this CSST extension allows?
that is the issue Manny, I have never yet seen one with a bushing, and there's none present in Joe's picture either. We all know that plumbers and HVAC techs don't carry bushings, but as they do carry rigid pipe thats what they should use to transition through the cabinet.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #5  
Old 11/15/08, 1:42 PM
escanlan escanlan is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Josephine, TX
Posts: 947
escanlan is well trusted escanlan is well trusted escanlan is well trusted
Please Note: escanlan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CSST in furnace cabinet

Gerry,

I agree! I have yet to find an installation like this where a protective bushing or sleeve was used. I definitely write it up as lacking protection or use of black iron through the cabinet penetration as an alternative. Either way I call out an HVAC specialist, or plumber, to repair it.

Another question though. I've never seen a tail piece made that was as short as this one. Also since the CSST does not have a required identification label on it I would expect it is site fabricated? Are you aware of any manufacturers that make them this short?
Reply With Quote
  #6  
Old 11/15/08, 2:40 PM
Joe D. Funderburk's Avatar
Joe D. Funderburk Joe D. Funderburk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Rock Hill, SC
Posts: 2,087
Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information
Send a message via Yahoo to jfunderburk
Default Re: CSST in furnace cabinet

Quote:
Originally Posted by escanlan View Post
Another question though. I've never seen a tail piece made that was as short as this one. Also since the CSST does not have a required identification label on it I would expect it is site fabricated? Are you aware of any manufacturers that make them this short?

Indeed, no bushing. All the CSST was Tracpipe. It's all site fabricated. The photo doesn't show that they ran a long section to a shutoff valve, then this short section from the valve to the furnace.



Joe Funderburk
Alpha & Omega Home Inspections, LLC
Hickory Grove, SC
NACHI ID: NACHI05120170
www.aohomeinspection.com
Reply With Quote
  #7  
Old 11/15/08, 3:40 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 1,587
Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information
Default Re: CSST in furnace cabinet

If it were allowed (CSST into cabinet), I would think we would see a lot of it since it is much easier to install than iron pipe.

York County seems to allow the appliance connectors into the furnaces since about half of the newer homes have it. I write it up as improper, the tag on those connectors clearly states this under item 2 but is very small print.

Here is another discussion on this:

http://www.hvac-talk.com/vbb/showthread.php?p=1773201



B.A. King Home Inspections, LLC
York, South Carolina
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
Reply With Quote
  #8  
Old 11/16/08, 9:54 PM
Buck Hartley Buck Hartley is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 283
Buck Hartley is generally well trusted Buck Hartley is generally well trusted
Default Re: CSST in furnace cabinet

Should the CSST be bonded?
Reply With Quote
  #9  
Old 11/16/08, 10:02 PM
Joe D. Funderburk's Avatar
Joe D. Funderburk Joe D. Funderburk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Rock Hill, SC
Posts: 2,087
Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information
Send a message via Yahoo to jfunderburk
Default Re: CSST in furnace cabinet

Quote:
Originally Posted by bhartley View Post
Should the CSST be bonded?
Absolutely, and it wasn't. Wrote that up for the electrician.



Joe Funderburk
Alpha & Omega Home Inspections, LLC
Hickory Grove, SC
NACHI ID: NACHI05120170
www.aohomeinspection.com
Reply With Quote
  #10  
Old 11/16/08, 10:46 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 1,587
Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information Bruce A. King is very trusted source of information
Default Re: CSST in furnace cabinet

Quote:
Originally Posted by bhartley View Post
Should the CSST be bonded?

All gas furnace piping is bonded via the pipe connection to the furnace valve to the equipment cabinet grounding wire where the 120V connects.
This is a poor bond.

The new requirement is correctly referred to and called "additional bonding".



B.A. King Home Inspections, LLC
York, South Carolina
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM
Sweating decision:Settle for lower SEER to use existing furnace? Fel Randolph HVAC 2 6/6/07 3:56 PM
Armstrong Ultra 80 Oil Forced air furnace Stephen Frazer HVAC 19 4/9/07 9:00 PM
Condemned Furnaces Spark Safety Issues Gary Reecher HVAC 7 3/8/07 9:17 PM
CSST Class Action jhagarty HVAC 21 12/16/06 1:56 AM


All times are GMT -4. The time now is 8:47 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics