Default CPVC on Condensate Pump Drain

Hey Folks-

Hopefully I haven't used up my question quota for the week...but I wanted to ask on this one as well. Usually on condensate pumps I always see the flexible plastic tubing. On this one they did connect flexible tubing directly but then quickly changed over to CPVC, even on the uphill climb. Is that something to be concerned about?

Thanks.

Kenny
Attached Thumbnails
cpvc-condensate-pump-drain-img_6847.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272

Last edited by krigler; 4/20/10 at 5:54 PM..
Reply With Quote
Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/20/10, 7:37 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: CPVC on Condensate Pump Drain

I don't see why it would be a problem. I always include a note telling them a mechanical pump was in use, that they fail, and should be frequently monitored.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 4/20/10, 8:47 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: CPVC on Condensate Pump Drain

I didn't get the manufacturer on this one but looked up the installation instructions on a standard condensate pump and it said:

"The outlet piping should be flexible tubing secured with a hose
clamp (not provided) or pipe (3/8 inch I.D. maximum to prevent
excessive flow back to unit)."

I would interpret the "or pipe" to include CPVC but wanted to double-check with you all. Thanks.

Kenny



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #4  
Old 4/20/10, 8:51 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: CPVC on Condensate Pump Drain

Was it larger than 3/8"?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 4/20/10, 10:20 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: CPVC on Condensate Pump Drain

Quote:
Originally Posted by lkage View Post
Was it larger than 3/8"?
Yep, I just found a pic that confirms it's 1/2" pipe. Is that enough information to call it out? Or do I need to determine the exact manufacturer of the pump and check it's installation instructions to see what it requires?

Kenny



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #6  
Old 4/20/10, 10:26 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: CPVC on Condensate Pump Drain

IMO it will not work, I would Write it up .No back check so it will run back



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #7  
Old 4/20/10, 10:38 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: CPVC on Condensate Pump Drain

I would write up that bad chimney too.
Reply With Quote
  #8  
Old 4/20/10, 10:39 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: CPVC on Condensate Pump Drain

If the unit has been there for a while and you saw no evidence of overflow, I'd just learn from this thread and move on. I doubt you'll be sued over it. We'll all know better next time we see it.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 4/20/10, 10:41 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: CPVC on Condensate Pump Drain

Where was it located?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 4/20/10, 10:42 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: CPVC on Condensate Pump Drain

Hehe
Since no one asked yet ,check out the hood.
Reply With Quote
  #11  
Old 4/20/10, 11:11 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: CPVC on Condensate Pump Drain

Quote:
Originally Posted by jfunderburk View Post
Where was it located?
Hey Joe-

Furnace room is in the middle of the basement. Interestingly, they shot that thing up and then probably over a good 15' and then brought it down into the washer drain. Problem though..the 1/2" drain line takes up enough space in the washer drain that the washer hose doesn't fully fit in there.
Attached Thumbnails
cpvc-condensate-pump-drain-img_6803.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #12  
Old 4/20/10, 11:16 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: CPVC on Condensate Pump Drain

So if you don't call it out and if the unit fails in the basement, what type of damage would result?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 4/20/10, 11:17 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: CPVC on Condensate Pump Drain

Quote:
Originally Posted by belliott View Post
I would write up that bad chimney too.
Bob - what the hey are you talking about? I didn't give you any pictures of the hood or chimney (but they were both bad!)
Attached Thumbnails
cpvc-condensate-pump-drain-img_6842.jpg   cpvc-condensate-pump-drain-img_6844.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 4/20/10, 11:18 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: CPVC on Condensate Pump Drain

Quote:
Originally Posted by krigler View Post
Problem though..the 1/2" drain line takes up enough space in the washer drain that the washer hose doesn't fully fit in there.
Looks like it fit to me. Not much room to spare, but it fit.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #15  
Old 4/20/10, 11:24 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: CPVC on Condensate Pump Drain

Quote:
Originally Posted by jfunderburk View Post
So if you don't call it out and if the unit fails in the basement, what type of damage would result?
I didn't see any open floor drains in the basement. Half the basement has recently been re-done...other half is crawlspace. I just sent out the report earlier today (client accesses online). I think I'll update the report and email the client on the change. I feel it's worth noting...even if I likely won't get sued over it. I'd rather not take the chance .



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sump pump requirements Matthew Klein Plumbing Inspections 0 12/30/09 3:53 PM
Condensate pump in the attic jfunderburk Inspecting HVAC Systems 7 9/15/08 11:26 AM
Condensate pump instead of drain piping lfoster Inspecting HVAC Systems 7 6/22/08 3:16 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
condensate drain lprinzi Inspecting HVAC Systems 3 8/11/06 5:57 PM


All times are GMT -4. The time now is 2:20 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts