Default CPVC Connected to Water Heater

I'm fairly new to the NACHI boards and I hate to post two questions almost back-to-back but here goes...

In the past I've seen CPVC connected directly to the water heater and have written it up with the following:

Currently, CPVC piping is connected directly to the water heater. The Plastic Pipe and Fittings Association (PPFA) recommends, "that on gas water heaters there should be at least 6 inches of clearance between the exhaust flue and any CPVC piping. Twelve inch long metal nipples or appliance connectors should be connected directly to the heater so that the CPVC tubing cannot be damaged by the build-up of excessive radiant heat from the flue." I recommend a licensed plumber inspect further and repair as necessary.


Attached is the PPFA document I quote. It's on the second PDF (Page 7) since I had to break it up into 3 PDF files to bypass the 256K upload limit for PDF files.


Do you agree/disagree with this write-up? If you agree, and this is what I saw yesterday, what if the lines are wrapped in an insulation sleeve? If the problem with CPVC connected directly to the WH is due to the radiant heat from the flue, would insulated sleeves remedy that problem? Or, if the heat from the flue can cause problems to the CPVC, would it also cause problems to an insulated sleeve?


Thanks guys in advance...I really appreciate this community of experts (and all the rest of you too)!
Attached Thumbnails
cpvc-connected-water-heater-img_0153.jpg  
Attached Files
File Type: pdf Plastic Pipe and Fittings Association Doc1.pdf (181.9 KB, 85 views)
File Type: pdf Plastic Pipe and Fittings Association Doc2.pdf (196.9 KB, 14 views)
File Type: pdf Plastic Pipe and Fittings Association Doc3.pdf (105.0 KB, 23 views)
Reply With Quote
Find an InterNACHI certified Washington Home Inspector (and anywhere else in North America)
  #2  
Old 10/14/09, 10:47 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: CPVC Connected to Water Heater

I agree. Did you write up the foam insulation...I bet it's in contact with the flue.

Did you write up the water heater laying sideways?



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 10/14/09, 11:27 AM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 17
Default Re: CPVC Connected to Water Heater

Actually the foam insulation was not in contact with the flue...it's was wrapped tightly around the pipe. So if there is insulation around the pipe protecting the CPVC from the radiant heat from the flue and the insulation is not touching the flue, would you let it pass?
Reply With Quote
  #4  
Old 10/14/09, 11:35 AM
Chuck Lambert Chuck Lambert is offline
New User
 
Join Date: Jan 2008
Location: Southern California
Posts: 77
Please Note: Chuck Lambert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CPVC Connected to Water Heater

Quote:
Originally Posted by krigler View Post
Actually the foam insulation was not in contact with the flue...it's was wrapped tightly around the pipe. So if there is insulation around the pipe protecting the CPVC from the radiant heat from the flue and the insulation is not touching the flue, would you let it pass?

The foam is a combustible material. Single wall vent pipe has a 6 inch clearance to combustible materials , double wall has a 1 inch clearance.

Chuck
Reply With Quote
  #5  
Old 10/14/09, 1:47 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 17
Default Re: CPVC Connected to Water Heater

Okay, if it was a double walled vent pipe and there was 1" clearance from the foam insulation, would you then allow the CPVC?
Reply With Quote
  #6  
Old 10/14/09, 1:51 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is online now
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,901
Default Re: CPVC Connected to Water Heater

Quote:
Originally Posted by krigler View Post
Okay, if it was a double walled vent pipe and there was 1" clearance from the foam insulation, would you then allow the CPVC?
I've never seen a double walled vent pipe at a water heater. They are always single until they merge into the furnace flue. and then both go double through the floor or wall.
Reply With Quote
  #7  
Old 10/14/09, 3:01 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: CPVC Connected to Water Heater

Quote:
Originally Posted by mnahrgang View Post
I've never seen a double walled vent pipe at a water heater. They are always single until they merge into the furnace flue. and then both go double through the floor or wall.
Mark, a B-vent (double-walled) is what I see 95% of the time.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 10/14/09, 3:05 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: CPVC Connected to Water Heater

Quote:
Originally Posted by krigler View Post
The Plastic Pipe and Fittings Association (PPFA) recommends, "that on gas water heaters there should be at least 6 inches of clearance between the exhaust flue and any CPVC piping. Twelve inch long metal nipples or appliance connectors should be connected directly to the heater so that the CPVC tubing cannot be damaged by the build-up of excessive radiant heat from the flue." I recommend a licensed plumber inspect further and repair as necessary.
I think your recommendations are sound based on what you quoted. (I didn't take the time to read the documents.) I don't recall ever seeing CPVC connected like that.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 10/14/09, 10:59 PM
Chuck Lambert Chuck Lambert is offline
New User
 
Join Date: Jan 2008
Location: Southern California
Posts: 77
Please Note: Chuck Lambert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: CPVC Connected to Water Heater

Quote:
Originally Posted by krigler View Post
Okay, if it was a double walled vent pipe and there was 1" clearance from the foam insulation, would you then allow the CPVC?

I agree with Joe, I have never seen CPVC attached like that. I would write it up as a substandard installation.

Chuck
Reply With Quote
  #10  
Old 10/20/09, 5:54 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 17
Default Re: CPVC Connected to Water Heater

Thanks guys...I appreciate your input.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Longevity of Conventional Water Heater Tanks. lagudo Plumbing 8 9/7/08 7:13 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM
Need Help On Chimney Liners Nick Scibetta Exterior 10 1/11/06 10:53 PM


All times are GMT -4. The time now is 5:51 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts