Default Pex & Tpr

I inspected some new construction the other day where they had a PEX line running from the TPR on the water heater.

I'm not real familiar with PEX and was wondering how flexible it gets when hot water is running through it. Is this discharge going to turn into a broken fire-hose during a major discharge, or will it remain mostly rigid?
Attached Thumbnails
cross-linked-polyethylene-and-tpr-p1050337smaller.jpg  



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #2  
Old 12/28/07, 12:53 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,489
Default Re: Pex & Tpr

I'd write it up, siting that its use is restricted to cold water supply, only.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #3  
Old 12/28/07, 12:58 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Pex & Tpr

Are you sure about that? They had both Red and Blue PEX (hot and cold) throughout the house. I've seen this before, just not on a TPR.
Attached Thumbnails
cross-linked-polyethylene-and-tpr-p1050455smaller.jpg  



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #4  
Old 12/28/07, 1:08 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,489
Default Re: Pex & Tpr

Quote:
Originally Posted by mnahrgang
Are you sure about that? They had both Red and Blue PEX (hot and cold) throughout the house. I've seen this before, just not on a TPR.
Depends on who you talk to.

The vendors say it can be used for both systems, but several plumbing resources (i.e. "Plumber's Pocket Manual, 10th Edition, Miller, Miller and Almond, page 183) advise using it only with cold water systems.

In your case though, since it is used for hot water throughout the house, why not the TPR - unless the copper pipe serves to provide a rigid channel to force the scalding discharge to the ground where the PEX could have it shooting in all directions?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #5  
Old 12/28/07, 1:16 PM
bzimbelman bzimbelman is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Silver City, NM
Posts: 353
Default Re: Pex & Tpr

Quote:
Originally Posted by mnahrgang
Are you sure about that? They had both Red and Blue PEX (hot and cold) throughout the house. I've seen this before, just not on a TPR.
Mark,

This was discussed not to long ago, and the answer is some locals allow it on the TPR and others do not.

No one gave an instance where it has failed on a TPR, so if/when I see it my write up is going to basically say that various areas allow PEX, others do not but I know of no known instances where it has failed.

Hope that helps!

-- bz



Brian Zimbelman
Circle Z Inspection Services
http://www.circlezinspections.com
575-535-4481 (wk)
575-313-1281 (cell)
Reply With Quote
  #6  
Old 12/28/07, 1:16 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Pex & Tpr

Quote:
Originally Posted by mnahrgang
I inspected some new construction the other day where they had a PEX line running from the TPR on the water heater.

I'm not real familiar with PEX and was wondering how flexible it gets when hot water is running through it. Is this discharge going to turn into a broken fire-hose during a major discharge, or will it remain mostly rigid?
I called the folks at pexconnection.com (http://www.pexconnection.com), and asked the guy who answered the phone if it was a proper usage of the material. His response was "absolutely". He said the material is pretty rigid, and there should be no problems with a discharge.

I found their catalog to also be fairly informative as well (pexconnection catalog) and helpful in helping educate me a little more.

Thank you all for your comments. That's very helpful.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.

Last edited by mnahrgang; 12/28/07 at 1:19 PM..
Reply With Quote
  #7  
Old 12/28/07, 1:21 PM
cgoyette cgoyette is offline
Active Poster
 
Join Date: May 2007
Posts: 364
Please Note: cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pex & Tpr

Mark,

I would right it up as not a appropriate application. Think about 150 PSI and 210 degrees....you get a fire hose flying around.

Curt
Reply With Quote
  #8  
Old 12/28/07, 1:34 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Pex & Tpr

Quote:
Originally Posted by cgoyette
Mark,

I would right it up as not a appropriate application. Think about 150 PSI and 210 degrees....you get a fire hose flying around.

Curt
Hey Curt,

I clearly see your point, and agree with with what you are saying. What would you say in the report?

Because I could see this as becoming a huge "p...ing" match between me an the builder. Especially if the manufacturers say it's appropriate, and the AHJ doesn't have a problem with it.

Mark



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #9  
Old 12/28/07, 2:01 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Pex & Tpr

Quote:
Originally Posted by cgoyette
Mark,

I would right it up as not a appropriate application. Think about 150 PSI and 210 degrees....you get a fire hose flying around.

Curt
Ah, but the pressure is not 150 PSI on a open unterminated line.
PEX is just fine for this application though I would recommend it be secured to prevent whipping in the event of TPR discharge.
My opinion. Take it or leave it.
Reply With Quote
  #10  
Old 12/28/07, 2:05 PM
cgoyette cgoyette is offline
Active Poster
 
Join Date: May 2007
Posts: 364
Please Note: cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pex & Tpr

Quote:
Originally Posted by mlarson
Ah, but the pressure is not 150 PSI on a open unterminated line.
PEX is just fine for this application though I would recommend it be secured to prevent whipping in the event of TPR discharge.
My opinion. Take it or leave it.
Mike,

Agree but how do you PROPERLY secure it? no matter what if the TPRV has to be used it will cause a nightmare even if for just a second as a hot water waving wildcat! Way easier to make it copper or gold guard. IMHO.

Curt
Reply With Quote
  #11  
Old 12/28/07, 2:10 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Pex & Tpr

For the record everyone... This PEX wasn't particularly flexible. It's pretty firm. I could move it a few inches, but that's about all. It was just slightly more flexible can a copper tube. My concern was how it would react after it got hot and under pressure.

I wrote up another TPR valve that same day that had a rubber hose connected to it. That one was totally flexible.

I just don't know with this one. That's why I posted, and it's also why I'm so appreciative of this ongoing discussion.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #12  
Old 12/28/07, 2:20 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Pex & Tpr

The best course of action whuld be to check with your local AHJ as I know at least some states do not permit the use of PEX for the TPR discharge piping.


If you want a definitive answer for what is permitted in the areas you inspect, contact your AHJs.
Reply With Quote
  #13  
Old 12/28/07, 2:33 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pex & Tpr

I have never heard of pex becoming more flexible with hot water in it. If it was, the spacing of horizontal supports would be different. I seriously doubt it is a problem on the TPRV----some jurisdictions require that it be strapped to the side of the tank at the bottom, which I think is a good idea any way. It just looks kinda funky because it usually curls a little
Reply With Quote
  #14  
Old 12/28/07, 4:01 PM
dgagneur's Avatar
dgagneur dgagneur is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Alpena, MI
Posts: 445
Please Note: dgagneur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pex & Tpr

I am not an expert on PEX but have worked with it in my last two homes. Even when hot water is run through it, it stays fairly rigid. I'd have a hard time believing it would actually whip around upon discharge of the TPR.

My opinion, if the local AHJ allows it, then it's not wrong so why write it up???

Dave
Reply With Quote
  #15  
Old 12/28/07, 5:25 PM
Randy L. Thomas Randy L. Thomas is offline
New User
 
Join Date: Mar 2007
Location: Oregon
Posts: 11
Please Note: Randy L. Thomas is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pex & Tpr

As an inspector, PEX is no problem but we require it to be secured at the bottom. Usually installers will use a hose clamp with 2 very short screws into the metal jacket. Code doesn't spell out the method or materials of the discharge line, just per mfr's recommendations.

Uponor bought out Wirsbo a couple years ao and they are the industry leader in PEX >>> http://www.uponor-usa.com/.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 6:57 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts