PEX as the TPR drain line is allowed in all the jurisdictions where I have checked. Whenever I have a question, I usually check the city of San Diego and then the cities where all the rich people live (La Jolla, Heritage Golf Estates in Poway, Coronado, Solana Beach, Cardiff by the Sea). If the rich people accept it, then Mr and Mrs Average Joe Blow, the poor people in Logan Heights, and the rednecks in Lakeside and Santee tend to follow along.
NACHI 2005 U.S. Member of the Year
|
|
#17
|
||||
|
||||
|
Quote:
http://www.healthyarkansas.com/phc/p...egulations.htm SECTION IV. RESTRICTIONS This regulation does not allow Cross-linked Polyethylene PEX pipe or fittings to be installed for T & P discharge on water heaters. This regulation does not allow Crosslinked Polyethylene PEX pipe or fittings to be installed directly into a water heater opening. |
|
#18
|
||||
|
||||
|
Quote:
PEX wasn't even allowed in California at all until, I believe, February 2002, when a Superior Court Judge up in, I believe, Ventura County basically told the Plumbers' Union to go back to their caves because they didn't have the public's best interest in mind by continuing to disallow the use of PEX by their plumbers. NACHI 2005 U.S. Member of the Year
|
|
#19
|
||||
|
||||
|
PEX is not allowed for use as TPR drain piping in CA. It must be specifically listed for this use, and PEX is not. CPC 608.5 Relief valves located inside a building shall be provided with a drain, not smaller than the relief valve outlet, of galvanized steel, hard drawn copper piping and fittings, CPVC, or listed relief valve drain tube with fittings. . . The CPC does not even allow PEX to be used for the plumbing distribution system, but it allows local jurisdictions to use it at their discretion. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#20
|
||||
|
||||
|
Quote:
NACHI 2005 U.S. Member of the Year
|
|
#21
|
||||
|
||||
|
I think they ought to see if you can make a hangmans knot with it, then I could tell you how to use PEX.
In the world view we are all important and our mere existence effects all life. Jack Gilleland Home Inspection Services Clayton Commercial, Multifamily, and Residential jgilleland1@att.net Ohio_Commercial and_Home_Inspections activerain |
|
#22
|
||||
|
||||
|
Quote:
Regarding its use as a TPR discharge material, P2803.6 , paragraph 13 of the 2006 IRC states: "Requirements for discharge pipe. The discharge piping serving a pressure-relief valve, temperature-relief valve or combination valve shall: Be constructed of those materials listed in Section P2904.5 or materials tested, rated and approved for such use in accordance with ASME A112.4.1." Table P2904.5 (approved water distribution piping) specifically lists PEX. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#23
|
|||
|
|||
|
Please Note:
sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
We don't do new construction but with the high cost of copper now, we use PEX on almost all of our remodel and re pipe jobs unless the customer prefers the copper. We NEVER use anything but 3/4" copper on our TPR valve drains though. |
|
#24
|
|||
|
|||
|
Documentation I have read states PEX is not allowed within 18 inches minimum to connection to water heater... Rated dishcarge piping for TPR should cover 150 PSI and 210 degrees as a minimum I thought? Wirsbo is 80 PSI at 200 degrees. At sea level water boils at 212 degrees...
Tony Siegert SafeHome Inspection Denver CO NACHI05021692 |
|
#25
|
||||
|
||||
|
I thought a lot of AHJ's (at least what I'm fam. with) don't allow anything except rigid material....and standard heights for discharge and such.
Call local AHJ? |
|
#26
|
||||
|
||||
|
By the time I get to a house, the AHJ has already done his code inspection -- and missed everything I write up. Why call him to get his interpretation?
I use the 2006 IRC and my judgment as my guide personally. If the item meets the IRC code, then I don't see how its relevant what the AHJ thinks...he'll never be back to the house again once the CO is obtained. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#27
|
||||
|
||||
|
Used commonly up here in new construction. Mike had it correct earlier. PSI does not matter as the TPR drain line is not closed and subject to pressure.
Stephen Stanczyk Washington State Licensed Home Inspector # 221 President, Washington Association of Property Inspectors (WAPI) (253) 241-0602 calls answered until 10pm Pierce County -Thurston County - King County - Snohomish County |
|
#28
|
||||
|
||||
|
I would write it because it is closer than 18 inches, And just for the solid part just my thought someone standing beside it will get scalded It would need more than one strap to hold it it in Place. I have seen tank blow .
|
![]() |