Default Dielectric Union?

Thoughts on this please. I'm no plumber, but this looks like copper and galvanized to me. It's a water heater connection. New home. The builder says it fine because the county code enforcement folks approved it.

My understanding is that a dielectric union is brass, and I must admit I sometimes have difficulty telling the difference between brass and copper. But the fitting is certainly the same color as the copper pipe, which you can see a little bit of at the top of the photo. Was I right to write it up?

dielectric-union-061507-023-small-.jpg.jpg
Views:	142
Size:	36.9 KB
ID:	12493



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #2  
Old 6/20/07, 10:41 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Dielectric Union?

Looks like a heat trap fitting.

http://www.perfectioncorp.com/water/heattrap.html

http://www.accentshopping.com/produc...&strReturnUrl=

The heat traps are lined with plastic so the water never touches the steel nipple.

Last edited by mlarson; 6/21/07 at 12:38 PM..
Reply With Quote
  #3  
Old 6/21/07, 12:07 AM
Darrell B. Hadler's Avatar
Darrell B. Hadler Darrell B. Hadler is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Medicine Hat, AB
Posts: 360
Default Re: Dielectric Union?

definately copper fitting



Darrell Hadler CMI
Five Star Home Inspections
Medicine Hat, AB. Canada
NACHI# 04111082 Cell phone# (403)502-3593
Inspected once . . . inspected right!
Reply With Quote
  #4  
Old 6/21/07, 11:00 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dielectric Union?

I have done alot of plumbing in the past but never heard of this heat trap thingy.
Is it some kind of fad or what is the story on these things.
Guess it would rule out use of a recirculating system.
Reply With Quote
  #5  
Old 6/21/07, 11:02 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Dielectric Union?

Quote:
Originally Posted by relliott
I have done alot of plumbing in the past but never heard of this heat trap thingy.
Is it some kind of fad or what is the story on these things.
Guess it would rule out use of a recirculating system.
Follow the links in my earlier post Bob.

Recirc lines still work fine BTW.
Reply With Quote
  #6  
Old 6/21/07, 12:33 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,831
Send a message via Yahoo to jfunderburk
Default Re: Dielectric Union?

Just got off the phone with the guy who put this in. He wanted to know what gave me the right to go behind a state inspector and claim something wasn't right . I replied, "my state license".

I sensed he didn't understand the concept of corrosion that can occur between dissimilar metals. I said, "I'm not a plumber and don't claim to be. If you can find a licensed plumber that will say this is OK, then he should clarify to me why it is. Are you a licensed plumber?"

"Uh, no", he replied.

"I'll email you the code and you can look it over. Have a nice day", I said.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 6/21/07, 1:40 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dielectric Union?

Good going.
It is always good to be confident
Reply With Quote
  #8  
Old 6/21/07, 1:56 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Dielectric Union?

1. There is no dielectric union in the photo.

2. There is a copper fittng fitting 3/4" female pipe to 1/2'" sweat adapter(small for the outlet of a water heater)

3.The galvanized "nipple" is a heat trap fitting with a check ball built into it and is plastic lined(you can tell by the machined line in it and there is should also be a direction arrow on it)

4. If the local AHJ approved it (which actually is not known for sure) Why fight. I don't spend my time bucking AHJ's. That doesn't mean I don't talk to them for their take on things.
I would report what I find and the possible effects and move on.

Does anyone else see this differently? Just curious.
Reply With Quote
  #9  
Old 6/22/07, 8:21 PM
William J. Decker's Avatar
William J. Decker William J. Decker is online now
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,526
Default Re: Dielectric Union?

Quote:
Originally Posted by mlarson
Looks like a heat trap fitting.

http://www.perfectioncorp.com/water/heattrap.html

http://www.accentshopping.com/produc...&strReturnUrl=

The heat traps are lined with plastic so the water never touches the steel nipple.
Heat trap fittlings have nothing to do with galvanic corrosion.

When galvanized touches copper, you have galvanic corrosion, and a bad, prone to failure, connection.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #10  
Old 6/22/07, 8:29 PM
William J. Decker's Avatar
William J. Decker William J. Decker is online now
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,526
Default Re: Dielectric Union?

Quote:
Originally Posted by jfunderburk
Just got off the phone with the guy who put this in. He wanted to know what gave me the right to go behind a state inspector and claim something wasn't right . I replied, "my state license".

I sensed he didn't understand the concept of corrosion that can occur between dissimilar metals. I said, "I'm not a plumber and don't claim to be. If you can find a licensed plumber that will say this is OK, then he should clarify to me why it is. Are you a licensed plumber?"

"Uh, no", he replied.

"I'll email you the code and you can look it over. Have a nice day", I said.
I have had similar calls, from "electicians" (which are not state licensed, in Illinois), 'plumbers' and 'roofer' (which ARE state licensed, here, but these guys weren't. They had the chutzpah (a jewish term for 'affrontary') to claim that because they had a local business license, that they were 'licensed'.) and 'licensed' General contractors (which does not require a state license, in Illinois. Just get a 1 Mil G/L insurance policy and pay $35.00.) all asking what my problem was.

I merely ask, "Are you state licensed?". After about 1/2 hour where they explain to me how they have been in business for 20 or 30 years, they finally say, "No.".

I then, simply, explain to them that I have a State License and must, under law, do my job according to that law.

They are still p*ss*d off, but at least they shut up.

Keep on doing what you are doing.

Educate the public, but also educate the tradesmen. They are, mostly, simple folk who don;t really know what they are doing, of the law behind it.

Hope this helps;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #11  
Old 6/22/07, 10:02 PM
lclark's Avatar
lclark lclark is offline
Active Poster
 
Join Date: Jan 2005
Location: Wabash, IN
Posts: 194
Please Note: lclark is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dielectric Union?

Will,
Read the second paragraph of the first link.
Larry
Reply With Quote
  #12  
Old 6/22/07, 11:12 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Dielectric Union?

All,

Galvanic action can be a bit confusing to understand so the following from the copper.org site may help clear it up.

When dissimilar metals are in contact with one another in the presence of an electrolyte, galvanic action occurs, resulting in the deterioration of the metal with the lower galvanic number. The electrolyte may be rain water running from one surface to another, or moisture from the air containing enough acid to cause it to act as an electrolyte. LINK
---------------------------------------------------------------------

The plastic sleeve in the heat trap fitting does not allow the water(a weak electrolyte) to come in contact with the galvanized steel fitting. This will significantly reduce any flow of galvanic current. Hope this helps.
Reply With Quote
  #13  
Old 6/22/07, 11:37 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dielectric Union?

Makes sense to me.How often do you guys notice these heat traps?
Also how much energy do they actualy save.?
Reply With Quote
  #14  
Old 6/23/07, 6:47 PM
ccurrins's Avatar
ccurrins ccurrins is offline
Active Poster
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 3,234
Please Note: ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dielectric Union?

Quote:
Originally Posted by wdecker
Heat trap fittlings have nothing to do with galvanic corrosion.

When galvanized touches copper, you have galvanic corrosion, and a bad, prone to failure, connection.
Exactly, and this is why a Dielectric Union is required in this situation.
Reply With Quote
  #15  
Old 6/23/07, 6:50 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Dielectric Union?

Quote:
Originally Posted by ccurrins
Exactly, and this is why a Die-Lectric Union is required in this situation.
Please explain as I used to believe that myself.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is this dielectric? pwigle Plumbing 8 11/2/07 12:05 PM
Dielectric question rbrady Plumbing 4 8/11/07 7:42 PM
Continued Education Log mcyr Misc. Discussion 5 4/1/07 11:25 AM
Petition to the Minister for CMHC lewens Canadian Inspectors 5 4/24/06 4:51 PM
Olympic Peninsula Chapter meeting in Union Washington on April 15, 2006. gromicko Misc. Discussion 0 3/15/06 12:37 PM


All times are GMT -4. The time now is 11:25 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts