Default dielectric union

Where are dielectric unions used besides water heaters?

Ar they required on all water heaters?
Reply With Quote
  #2  
Old 1/22/08, 11:22 AM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: dielectric union

A dielectric union is designed to break the electrical contact between two dissimilar metals (to prevent galvanic corrosion). Most of the flexible copper connector hoses on water heaters have a plastic washer that acts as a dielectric union.

Dielectric unions are used anyplace where a copper pipe connects to a galvanized steel pipe.

You should not need it if you don't have dissimilar metals, especially galvanized steel to copper contact.

Last edited by rbrady; 1/22/08 at 4:13 PM..
Reply With Quote
  #3  
Old 1/22/08, 11:38 AM
John Cahill John Cahill is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Plano, TX
Posts: 826
Default Re: dielectric union

Quote:
Originally Posted by rbrady
A dielectric union is designed to break the electrical contact between two dissimilar metals (to prevent galvanic corrosion). Most of the flexible copper connector hoses on water heaters have a plastic washer that acts as a dielectric union.

They are used anyplace where a copper pipe connects to a galvanized steel pipe.

You should not need it if you don't have dissimilar metals, especially galvanized steel to copper contact.
If a flexible copper connector is used is it reasonable to assume the washer cannot be seen during a home inspection?

Texas is redoing their SoP and have this new requirement.
Reply With Quote
  #4  
Old 1/22/08, 11:42 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: dielectric union

Visual inspection means just that.
If you were unscrewing plumbing to check for missing parts , you, would have worse problems than lack of a proper dielectric union.
Reply With Quote
  #5  
Old 1/22/08, 11:45 AM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: dielectric union

You can typically see part of the plastic washer/flange sticking out at the top of the fitting.
This plastic fitting is frequently damaged when the fitting is tightened too much, causing a loss of the dielectric properties.

It would be difficult to verify the integrity of the washer/flange.

dielectric-union-p1228015.jpg

Last edited by rbrady; 1/22/08 at 12:01 PM..
Reply With Quote
  #6  
Old 1/22/08, 12:59 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: dielectric union

If there is a problem it will eventualy corrode.
Might as well watch the grass grow.
Reply With Quote
  #7  
Old 1/22/08, 1:59 PM
John Cahill John Cahill is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Plano, TX
Posts: 826
Default Re: dielectric union

Quote:
Originally Posted by relliott
If there is a problem it will eventualy corrode.
Might as well watch the grass grow.
Ya I thought of that. Seems like the water heater would fail before serious dielectric corrosion. They only last 6 to 10 years here.

Problem is if Texas puts it in the SoP I have to work with or around the requirement.

Thanks
Reply With Quote
  #8  
Old 1/22/08, 2:05 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: dielectric union

I hear ya.
All you can do is your best.
Kinda like how in Illinois we observe the plumbing which is worded differently from the other systems that we are required to inspect.
Everyone says it is because of the plumbing union , but my opinion is it also has to do with not unscrewing and turning shutoff's.
Plumbing is like that as we all know.
Reply With Quote
  #9  
Old 1/22/08, 2:52 PM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: dielectric union

Good Picture
Attached Thumbnails
dielectric-union-dialectric-union.jpg  



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain

Last edited by jgilleland; 1/22/08 at 2:57 PM..
Reply With Quote
  #10  
Old 1/22/08, 4:12 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: dielectric union

The corroded, leaking dielectric union in the back was installed by a 'licenced plumber'. I installed the copper tube/hose and fittings. I paid quite a bit more for the brass fittings, I guess that is why people like the galvanized steel ones (cheap).
Reply With Quote
  #11  
Old 6/12/09, 9:40 PM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 546
Default Re: dielectric union

Check out these steam pipes connected with galvanized metal fittings.
Attached Thumbnails
dielectric-union-101_9348-small-.jpg.JPG
Views:	932
Size:	40.5 KB
ID:	29236   dielectric-union-101_9349-small-.jpg.JPG
Views:	708
Size:	43.4 KB
ID:	29237   dielectric-union-101_9374-small-.jpg.JPG
Views:	642
Size:	37.1 KB
ID:	29238  
Reply With Quote
  #12  
Old 6/12/09, 11:01 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: dielectric union

IMO Dielectric unions have very limited benefit as the water within the pipe also conducts current, effectively defeating the "isolation" provided by the dielectric device. I see corroded nipples and fittings on and around water heaters all the time, regardless of whether dielectric isolated unions, couplings, connectors, etc. are used. Sometimes it's caused by the copper flex connector with the integral isolator itself. Brass seems to have more universal compatibility, which is why I prefer to see brass nipples.

I've attached and old tech bulleting from Rheem on the topic. I'm not sure if it's still accessible on their site. Also note that the nipples on top of the water heater are supposed to be dielectric, but as far as I know you can't tell visually once the plumbing is hooked up.

Probably better for the TX SOP to call out actual corrosion rather than all of the dielectric / non-dielectric scenarios or we'll wind up with another SOP standard as silly and confusing to the public as the no AFCI defects in older homes.

********** PDF too big to attach - here's the text - sorry for format *****
Published by Rheem / RUUD

Quote:
TECHNICAL SERVICE DEPARTMENT
Technical Service Bulletin
1-800-432-8373
Dielectric
Technical Competence, Product Confidence
Page 1 of 1
1221.doc
Dielectric – an electricity, especially a substance with electrical conductivity less than a millionth (10 to the –6) of an
MHO.

Water Heater and Water Connections

The installation of unions on the inlet and the outlet waterlines and a shut-off valve in at least the cold inlet
waterline is recommended, so the water heater may be easily disconnected for servicing.

Dielectric unions may have been used many years ago and were installed with the thought to assist in
reduction of corrosion that could develop at the piping connections. From time to time, this inquiry is brought to our
attention stating the use of dielectric unions may be suggested required or should be, perhaps used.

The required use of dielectric unions on our water heaters is not necessary. With this in mind, uniformity of
piping material must be administered by the installer. What is meant by this is “the piping used in the system i.e.:
copper, etc. must be the same throughout, to and from the water heater”. When different piping material connectors
are used, corrosion can be immediate and will commence deterioration within days of installation Why is this? When
two or more different metallic piping materials are used there can be some level of electrical current flow between the
materials due to their different levels of electrical voltage potential. By uniformly using the same material to pipe the
water heater, there is essentially no difference in electrical potential between the piping and the water heater tank.
Therefore, dielectric fittings are not required when following the uniformity of piping material.

The theory that is in practice is described as follows: All metals when immersed in an electrolyte, such as
water, have a voltage potential. This voltage potential varies from approximately +3.0 volts to a –3.0 volts. The
relative activity of the metal is determined by voltage potential with those metals with negative voltages being most
active and more likely to corrode. Magnesium, for instance, has a slightly negative voltage, approximately –2.0 volts,
and will corrode very rapidly in certain waters. Iron has a voltage potential of –0.4 volts and rusts (corrodes) very
rapidly when exposed to a moist atmosphere. Copper on the other hand has a voltage potential of +0.350

Any metal with a negative voltage when coupled with a metal with a more positive voltage potential will
sacrifice (corrode) itself to protect the metal with more positive (noble) voltage. By placing a dielectric (insulating)
fitting between two dissimilar metals, i.e. iron and copper, there is a break between the two. Therefore, in theory the
iron will not corrode to protect the copper. In fact, the circuit is generally completed through the water, and
depending on the water conductivity the iron will corrode at various rates.

The corrosive product often fills the pipe diameter restricting the water flow and is often the source of rusty
water. Our company does not promote the use of dielectric unions, because they do not effect the corrosion
characteristics of the water heater. Due to our cathodic protection system, the juncture of the supply piping and the
tank fitting is adequately protected by the cathodic protection system against corrosion without the buildups which
occur in the dielectric union.

When there is a concern with using dielectrics, a plastic lined nipple have the ends of the plastic fold over
the end of the nipple which provided an excellent dielectric. The plastic engages the thread of the fitting a attached,
whether it be the tank of the piping, thereby insulating the metal nipple from the water. This prevents corrosion on
either part. These nipples have been certified as dielectrics in numerous areas of the United States.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 6/12/09 at 11:07 PM..
Reply With Quote
  #13  
Old 2/21/11, 2:24 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: dielectric union

OK...What exactly are they saying? Are Dyelectric fittings needed or not?

dielectric-union-p1010048.jpg

The way I read it is that Dyelectric fittings are not to be used becase the SAME type of pipe is required throughout. Correct?



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901

Last edited by rhensel; 2/21/11 at 4:33 PM..
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/21/11, 4:22 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: dielectric union

Bump



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
  #15  
Old 2/25/11, 11:15 AM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 359
Default Re: dielectric union

Quote:
Originally Posted by rhensel View Post
OK...What exactly are they saying? Are Dyelectric fittings needed or not?

Attachment 42311

The way I read it is that Dyelectric fittings are not to be used becase the SAME type of pipe is required throughout. Correct?
Here is what happens when they are not used. Home was built in 2007
Attached Thumbnails
dielectric-union-scott-and-janell-dessingue-041.jpg   dielectric-union-scott-and-janell-dessingue-051.jpg  



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is this dielectric? pwigle Plumbing Inspections 8 11/2/07 11:05 AM
Dielectric question rbrady Plumbing Inspections 4 8/11/07 6:42 PM
Dielectric Union? jfunderburk Plumbing Inspections 33 6/25/07 7:51 AM
Petition to the Minister for CMHC lewens Canadian Inspectors 7 4/24/06 4:53 PM
Olympic Peninsula Chapter meeting in Union Washington on April 15, 2006. gromicko Miscellaneous Discussion for Inspectors 0 3/15/06 11:37 AM


All times are GMT -4. The time now is 8:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts