Default Discharge pipe

So far in nearly have of my HIs , the TPR valves have no discharge pipes . In one case it was a recent replaced hot water tank . Of course I report it . Then short time later the plumber who installed it calls and carries on for a while , in sumery he tells me that it's only an option to install , that it's an extra charge to add it . I'm wondering if there is some kind of action I can take to change these guys minds ? That is with out making a small war ! Haha .



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/30/10, 3:06 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,629
Default Re: Discharge pipe

Send them this.

International Plumbing Code

504.6 Requirements for discharge piping.

The discharge piping serving a pressure relief valve, temperature relief valve or combination thereof shall:


1. Not be directly connected to the drainage system.

2. Discharge through an air gap located in the same room as the water heater.

3. Not be smaller than the diameter of the outlet of the valve served and shall discharge full size to the air gap.

4. Serve a single relief device and shall not connect to piping serving any other relief device or equipment.

5. Discharge to the floor, to an indirect waste receptor or to the outdoors. Where discharging to the outdoors in areas subject to freezing, discharge piping shall be first piped to an indirect waste receptor through an air gap located in a conditioned area.

6. Discharge in a manner that does not cause personal injury or structural damage.

7. Discharge to a termination point that is readily observable by the building occupants.

8. Not be trapped.

9. Be installed so as to flow by gravity.

10. Not terminate more than 6 inches (152 mm) above the floor or waste receptor.

11. Not have a threaded connection at the end of such piping.

12. Not have valves or tee fittings.13. Be constructed of those materials listed in Section 605.4 or materials tested, rated and approved for such use in accordance with ASME A112.4.1.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #3  
Old 11/30/10, 3:42 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Discharge pipe

It's a requirement in the states. What does Canadian code say in the matter?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 11/30/10, 3:57 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Discharge pipe

Quote:
Originally Posted by agallatin View Post
So far in nearly have of my HIs , the TPR valves have no discharge pipes . In one case it was a recent replaced hot water tank . Of course I report it . Then short time later the plumber who installed it calls and carries on for a while , in sumery he tells me that it's only an option to install , that it's an extra charge to add it . I'm wondering if there is some kind of action I can take to change these guys minds ? That is with out making a small war ! Haha .
When ever I get challenged by the Local Tradespersons about my findings in my Written Report, I just ask them to kindly show me, and or guide me, to the Documents backing up their findings.

Something like a Code or Manufactures Documents will suffice. I have yet to have anyone comply.
Reply With Quote
  #5  
Old 11/30/10, 7:45 PM
agallatin agallatin is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Trail BC
Posts: 194
Default Re: Discharge pipe

Thanks for your replys ,
Yes the code is the same here . What happened is the home owner asked for the discharge pipe to installed after my HI report . The client called the plumbing co. that put the tank in they billed the client a $187 w/ tax . Client phoned me , I advised that they shouldn't have to pay the bill . That's when the plumber contacted me . Their opinion was that I didn;t know anything and I was out of line . Waiting for results from client .



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
  #6  
Old 11/30/10, 8:23 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Discharge pipe

Quote:
Originally Posted by agallatin View Post
Client phoned me , I advised that they shouldn't have to pay the bill.
That was poor advice IMHO. Who are we to say what should be paid for.

Your comment should have been along these lines;

"The plumbing contractor should have installed the discharge piping as a standard part of the water-heater installation. As it stands, the installation is incomplete."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 11/30/10, 8:29 PM
lgreen's Avatar
lgreen lgreen is offline
InterNACHI Member
 
Join Date: Jan 2009
Location: Buckeye, Arizona
Posts: 36
Default Re: Discharge pipe

The Arizona Registrar of Contractors would make them put it in if the home owner complained. Does BC have a similar agency?

The AHJ should also back you up. I wouldn't go that route unless there was a permit pulled for it.
Reply With Quote
  #8  
Old 12/1/10, 4:12 PM
agallatin agallatin is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Trail BC
Posts: 194
Default Re: Discharge pipe

Yes Jef , your risght ! I should have worded it along the lines that you said . In the phone conversation , however I did write it much like you said in my report .
And Loren I'm looking into that . Thanks for the good advice , to you both .



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
  #9  
Old 12/1/10, 4:36 PM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,715
Default Re: Discharge pipe

Installers will complain back, just so their lack of licensing, insurance, code compliance, and education will not be discovered and/or reported by you. Perhaps it is really Uncle Bob who did the installation. I see it alot.



CMI, CPI, KS #0110-0094 Termite #16601
KS Radon #KS-MS-0027
BBB A+ Accredited Business
Serving the Greater Kansas City Metro Area
Eastern Kansas/Western Missouri
http://www.metrospeckc.com
"If opportunity doesn't knock, build a door"--Milton Berle
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 41 4/5/12 6:43 AM
Pellet stove help chellickson General Inspection Discussion 23 8/19/10 1:23 AM
Is this allowed? belliott Plumbing Inspections 4 7/15/09 6:40 PM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 8:16 AM
Identify ABS defective pipe mcyr Plumbing Inspections 6 1/29/09 6:39 PM