Old 5/27/11, 11:12 AM
ctasker ctasker is offline
Active Poster
 
Join Date: Nov 2010
Location: Alberta Canada
Posts: 226
Please Note: ctasker is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Dishwasher question

Hey all, had a question, was there a specific year when dishwashers were required to have a built in back-flow device installed, also, with that style dishwasher, does the waste discharge line still have to rise up and fasten to the underside of counter, have been seeing some new installations where the discharge line is almost direct (no loop or fastening to underside of cabinet) thanks, PS, fairly New Construction.

Last edited by ctasker; 5/27/11 at 11:50 AM..
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/27/11, 11:36 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Dishwasher question

They are required to have an air gap.

Recommend an air gap or high loop to prevent bacterial infection.Only a air gap is acceptable by code however.
Reply With Quote
  #3  
Old 5/27/11, 11:49 AM
ctasker ctasker is offline
Active Poster
 
Join Date: Nov 2010
Location: Alberta Canada
Posts: 226
Please Note: ctasker is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dishwasher question

Thanks bob for confirming the loop, still stuck on the air gap thing, I do not always see those on newer installs, I assumed it was because the newer ones were equipped with an integral back flow device, with no need for air gap.
Reply With Quote
  #4  
Old 5/27/11, 11:52 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Dishwasher question

Quote:
Originally Posted by ctasker View Post
Thanks bob for confirming the loop, still stuck on the air gap thing, I do not always see those on newer installs, I assumed it was because the newer ones were equipped with an integral back flow device, with no need for air gap.
You would have no way of knowing that.Assume none do.
Reply With Quote
  #5  
Old 5/27/11, 12:20 PM
ctasker ctasker is offline
Active Poster
 
Join Date: Nov 2010
Location: Alberta Canada
Posts: 226
Please Note: ctasker is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dishwasher question

Thanks Bob, I will just write up, no visible Air Gap, Discharge line should have loop. are most HI`s running full cycle of dishwasher, thanks.
Reply With Quote
  #6  
Old 5/27/11, 12:21 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Dishwasher question

Quote:
Originally Posted by ctasker View Post
Thanks Bob, I will just write up, no visible Air Gap, Discharge line should have loop. are most HI`s running full cycle of dishwasher, thanks.
You are not required to check appliances in the SOP but to answer ,yes I do.
Reply With Quote
  #7  
Old 5/27/11, 12:35 PM
ctasker ctasker is offline
Active Poster
 
Join Date: Nov 2010
Location: Alberta Canada
Posts: 226
Please Note: ctasker is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dishwasher question

Thanks bob.
Reply With Quote
  #8  
Old 5/27/11, 12:41 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Dishwasher question

Quote:
Originally Posted by belliott View Post
They are required to have an air gap.

Recommend an air gap or high loop to prevent bacterial infection.Only a air gap is acceptable by code however.
2009 IRC P2717.2 Sink and dishwasher.A sink and dishwasher are permitted
to discharge through a single 11/2-inch (38 mm) trap.
The discharge pipe from the dishwasher shall be increased to a
minimum of 3/4 inch (19 mm) in diameter and shall be connected
with a wye fitting to the sink tailpiece. The dishwasher
waste line shall rise and be securely fastened to the underside of
the counter before connecting to the sink tailpiece.

Commentary: Dishwashing machines may connect directly to the
drainage system and do not require an indirect connection
by drainage air gap or air break
. The direct
connection is acceptable, because the potable water
supply is adequately protected against backflow. This
section requires that the waste line be looped as high
as possible and be securely fastened to the underside
of the sink rim or countertop to minimize the potential
of waste backflow into the dishwasher unit (see Commentary
Figure P2717.2).



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 5/27/11, 12:55 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Dishwasher question

Quote:
Originally Posted by jfunderburk View Post
2009 IRC P2717.2 Sink and dishwasher.A sink and dishwasher are permitted
to discharge through a single 11/2-inch (38 mm) trap.
The discharge pipe from the dishwasher shall be increased to a
minimum of 3/4 inch (19 mm) in diameter and shall be connected
with a wye fitting to the sink tailpiece. The dishwasher
waste line shall rise and be securely fastened to the underside of
the counter before connecting to the sink tailpiece.

Commentary: Dishwashing machines may connect directly to the
drainage system and do not require an indirect connection
by drainage air gap or air break
. The direct
connection is acceptable, because the potable water
supply is adequately protected against backflow. This
section requires that the waste line be looped as high
as possible and be securely fastened to the underside
of the sink rim or countertop to minimize the potential
of waste backflow into the dishwasher unit (see Commentary
Figure P2717.2).
Does that include when connected ted to a disposal?(did not think so)
They are required here.
Reply With Quote
  #10  
Old 5/27/11, 2:03 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,629
Default Re: Dishwasher question

Quote:
Originally Posted by belliott View Post
Does that include when connectedted to a disposal?(did not think so)
They are required here.
PART 890 ILLINOIS PLUMBING CODE

Section 890.770 Dishwashing Machines


a) Domestic Dishwasher (Private Residence). When a domestic dishwashing machine drain line is connected to the house side of a trap from a sink, the drain from the dishwasher shall be carried up to the underside of the spill rim of the sink. Dishwashing machines shall discharge separately into a trap or tail piece of the kitchen sink and shall not connect to the food waste disposal unit.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #11  
Old 5/27/11, 2:17 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Dishwasher question

Quote:
Originally Posted by ccurrins View Post
PART 890 ILLINOIS PLUMBING CODE

Section 890.770 Dishwashing Machines


a) Domestic Dishwasher (Private Residence). When a domestic dishwashing machine drain line is connected to the house side of a trap from a sink, the drain from the dishwasher shall be carried up to the underside of the spill rim of the sink. Dishwashing machines shall discharge separately into a trap or tail piece of the kitchen sink and shall not connect to the food waste disposal unit.
But allowed in other states Chris.
Airgaps are required in Chicago.

This makes for a good general statement.

Airgaps are now standard equipment to assure a separation between
supply and waste water. It is advised that either an airgap or a high loop
be installed between the dishwasher and the waste connection
Reply With Quote
  #12  
Old 5/27/11, 2:21 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,629
Default Re: Dishwasher question

Quote:
Originally Posted by belliott View Post
But allowed in other states Chris.
Airgaps are required in Chicago.
I know. Chicago's in IL.

You said "Does that include when connected to a disposal?"

That also is not allowed in Chicago, or the other half of Illinois.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #13  
Old 5/27/11, 3:03 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Dishwasher question

Quote:
Originally Posted by ccurrins View Post
I know. Chicago's in IL.

You said "Does that include when connected to a disposal?"

That also is not allowed in Chicago, or the other half of Illinois.
How about the poster of the thread?
Is Canada part of Illinois.
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/27/11, 7:08 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Dishwasher question

Quote:
Originally Posted by belliott View Post
How about the poster of the thread?
Is Canada part of Illinois.
If he is in Canada then why did you post "Only a air gap is acceptable by code however." ? Are you that familiar with Canadian codes?




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #15  
Old 5/28/11, 12:50 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Dishwasher question

Quote:
Originally Posted by sstanczyk View Post
If he is in Canada then why did you post "Only a air gap is acceptable by code however." ? Are you that familiar with Canadian codes?
That is a side bar with Chris.He does well on his own, big brother.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sump Pit/Pump Question Joey D'Adamo Plumbing Inspections 4 11/26/08 1:04 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Hydrogen Bomb DISHWASHERS rspriggs Miscellaneous Discussion for Inspectors 8 8/3/06 4:55 PM
Dishwasher question mmorgan Plumbing Inspections 3 4/6/06 12:09 PM
Exploding Dishwasher mbledsoe Plumbing Inspections 8 2/28/06 7:13 AM


All times are GMT -4. The time now is 2:24 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts