Default Do you allow the TPR to discharge into the WH pan?

I recently learned something. According to NACHI plumbing training course....


(I'll post that quote later.)



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Find an InterNACHI certified Oklahoma Home Inspector (and anywhere else in North America)
  #2  
Old 5/28/09, 2:54 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,695
Default Re: Do you allow the TPR to discharge into the WH pan?

Personally, I don't think it's up to me to "allow" anything!



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #3  
Old 5/28/09, 3:51 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Do you allow the TPR to discharge into the WH pan?

Not allowed in CA. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #4  
Old 5/28/09, 9:07 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
Originally Posted by dandersen View Post
Personally, I don't think it's up to me to "allow" anything!
Ok, perhaps I worded it poorly. You know what I mean.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 5/28/09, 9:09 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: Do you allow the TPR to discharge into the WH pan?

OK. Over half of you are wrong.

NACHI's training on plumbing:

"A relief-valve pipe terminating into a water leak catch pan is not permitted, because the pan is not an indirect waste receptor. Most pans have only a ¾ inch-diameter (19 mm) drain outlet, which is not capable of gravity draining the pressurized discharge of the relief valve at full flow."



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 5/28/09, 9:27 PM
Tom Deehan Tom Deehan is offline
InterNACHI Member
 
Join Date: Mar 2009
Location: Stoney Creek ON
Posts: 40
Default Re: Do you allow the TPR to discharge into the WH pan?

Not so up in Canada..
Reply With Quote
  #7  
Old 5/28/09, 9:34 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,513
Default Re: Do you allow the TPR to discharge into the WH pan?

About the only place you are going to see a WH pan here is at Home Depot.



Doug Edwards, CMI







Reply With Quote
  #8  
Old 5/28/09, 10:27 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
Originally Posted by dedwards View Post
About the only place you are going to see a WH pan here is at Home Depot.
Required in Chicago Buildings.(I call them drain pans)
Reply With Quote
  #9  
Old 5/28/09, 11:56 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Do you allow the TPR to discharge into the WH pan?

Here are the exact codes.(Chicago )

18-29-504.7.1 Discharge.

The discharge from the relief valve shall be piped separately to an indirect waste receptor located inside the building. The discharge shall be piped full size and installed in a manner that does not cause personal injury or property damage and that is readily observable by the building occupants. The discharge from a relief valve shall not be trapped. The diameter of the discharge piping shall not be less than the diameter of the relief valve outlet. The discharge pipe shall be installed so as to drain by gravity flow and shall terminate atmospherically not more than 6 inches (150 mm) above the floor. The end of the discharge pipe shall not be threaded.

18-29-504.8 Required pan.

Water heaters or hot water storage tanks installed in locations where leakage of the tanks or connections will cause damage shall be installed in a galvanized steel or other metal pan of equal corrosion resistance having a minimum thickness of 24 gauge, 0.0276 inch (0.70 mm) Any water heater installed in a cabinet below a counter shall be provided with a drain pan.
Reply With Quote
  #10  
Old 5/29/09, 1:24 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Do you allow the TPR to discharge into the WH pan?

Although I'm in California with Jeff (see comment #3), I do have one large jurisdiction here that allows it.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #11  
Old 5/31/09, 7:15 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,353
Default Re: Do you allow the TPR to discharge into the WH pan?

Code Section 3303.6.1 does allow for the discharge pipe to terminate inside a receptacle (or spill pan) as long as an air gap is provided between the end of the discharge pipe and the top rim of the spill pan itself without creating a hazard or potential cause of damage.

The problem here is, the risk of personal injury when the TPR valve discharges. This is because the discharge pipe terminates into a spill pan that cannot safely catch the flow of water or steam during discharge.
When you consider that the TPR valve discharges at 150 psi, which is five times greater than the force of your domestic water system, the scalding water can strike the bottom of the shallow pan and spray out in all directions. A deeper receptacle with adequate circuference would be advisable over the shallower, tightly-fitting spill pans commonly observed in the field. Even better would be to the exterior when possible or to an indirect waste receptor when initially constructed.

JM




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #12  
Old 5/31/09, 11:19 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
Originally Posted by mcyr View Post
Code Section 3303.6.1 does allow for the discharge pipe to terminate inside a receptacle (or spill pan) as long as an air gap is provided between the end of the discharge pipe and the top rim of the spill pan itself without creating a hazard or potential cause of damage.
What code is that? (It's not the IRC.) Would you please quote it verbatim?



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 6/1/09, 4:04 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 690
Default Re: Do you allow the TPR to discharge into the WH pan?

I report it as improper, also if it is "T"ed into the pan drain line or another T&P discharge line.

IRC Commentary (P2801.5) specifically states that "The relief valve discharge is prohibited from terminating into such pan"
Reply With Quote
Find an InterNACHI certified Oklahoma Home Inspector (and anywhere else in North America)
  #14  
Old 6/1/09, 5:11 AM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 1,216
Default Re: Do you allow the TPR to discharge into the WH pan?

TPRs should not discharge into the safe pan. A safe pan or "water leak catch pan" under the hot water tank is not an indirect waste receptor, because it has usually a 3/4 inch outlet. That's the determining factor. Now...the floor drain next to it is. The size of the pan's outlet would have to meet the minimum size of a indirect waste drain pipe (1 and 1/4). At full discharge, the pan would not be able to hold and drain the discharged water - defeating its "intended" purpose.

Has anyone actually tugged on the TPR with a shirt sleeve during an inspection? Oh! Instant heart thumper...




BEN GROMICKO
Director of InterNACHI Online Education
President of NACHI.TV - Online Training Videos
President of Mountain Warranty Corporation
ben@nachi.tv
(303)862-2611 ben@mountainwarranty.com

IMPROVE YOUR REPORT

Reply With Quote
  #15  
Old 6/1/09, 5:14 AM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 1,216
Default Re: Do you allow the TPR to discharge into the WH pan?

Question: Can a sump pump be an indirect waste receptor with a TPR valve discharge directed towards it?




BEN GROMICKO
Director of InterNACHI Online Education
President of NACHI.TV - Online Training Videos
President of Mountain Warranty Corporation
ben@nachi.tv
(303)862-2611 ben@mountainwarranty.com

IMPROVE YOUR REPORT

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Radon Discharge bhartley IAC2 Forum 5 3/27/09 7:10 PM
Discharge into a vent? Bob Smith, Jr. Plumbing 1 2/1/09 6:43 AM
Gas water heater TPRV discharge tube?? jacaron Plumbing 10 11/21/08 10:35 PM
And another A/C condensate line discharge question bwilliams HVAC 4 11/7/08 12:20 AM
TPR has PEX2 for discharge piping jlybolt Plumbing 11 7/10/06 12:14 AM


All times are GMT -4. The time now is 8:50 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts