Old 6/1/09, 10:48 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,096
Default Re: Do you allow the TPR to discharge into the WH pan?

Chuck's right, the 2006 IRC (not sure of other versions) states:
Quote:
P2801.5 Required pan. Where water heaters or hot water storage
tanks are installed in locations where leakage of the tanks
or connections will cause damage, the tank or water heater
shall be installed in a galvanized steel pan having a minimum
thickness of 24 gage (0.016 inch) (0.4 mm) or other pans for
such use. Listed pans shall comply with CSA LC3.

Where leaks from a water heater or storage tank or the
associated connections will cause damage to the
structure, the tank must be installed in a drain pan. The
pan must be constructed of galvanized steel or other
material intended for such use. Where listed pans are
used they must conform to the requirements of CSA
LC3. Such a pan is intended to catch water from a
leaking tank, a leaking connection to the tank or condensate
from the tank. The relief valve discharge piping
is prohibited from terminating into such pan
(see
Commentary Figure P2801.5). A 3/4-inch-diameter
(19.1 mm) pan drain is not capable of carrying the
pressurized discharge of the relief valve at full flow.
See Section P2803.6.1.
And the diagram shows:

do-you-allow-tpr-discharge-into-wh-pan-whsafetypan.gif
Reply With Quote
Find an InterNACHI certified Oklahoma Home Inspector (and anywhere else in North America)
  #17  
Old 6/1/09, 11:34 AM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 1,216
Default Re: Do you allow the TPR to discharge into the WH pan?

Wow!
You guys are goood.

We're thinking of publishing this Online Residential Plumbing Course in a hard-cover book format. It has been technically-edited by many members/students who have helped edit the first draft of the course. It has been grammatically-edited by a professional book editor too.

If anyone can provide necessary corrections to the course, I'll send you a gift in the mail. Just email me the valid correction/edition at ben@nachi.tv.

The gift will be this marketing tool.




BEN GROMICKO
Director of InterNACHI Online Education
President of NACHI.TV - Online Training Videos
President of Mountain Warranty Corporation
ben@nachi.tv
(303)862-2611 ben@mountainwarranty.com

IMPROVE YOUR REPORT

Reply With Quote
  #18  
Old 6/1/09, 1:56 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,524
Default Re: Do you allow the TPR to discharge into the WH pan?

I see this all the time, and I call it out.

There is a problem here with understanding the concept, even for plumbers.

The TPR valve is NOT a water drainage device, although many people, including plumbers, think it is. It is a STEAM drainage device. When those things let loose, what comes out is not water, it is live steam. The reason for the pipe is to have the steam discharge spray on the floor or some other place where it will not hit human beings.

If the pipe "drains" into the pan, it will splash up and scald a person. The amount and flow rate of the discharge is also more than the pan can handle.

Hope this helps;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #19  
Old 6/1/09, 2:28 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
Originally Posted by wdecker View Post
I see this all the time, and I call it out.

There is a problem here with understanding the concept, even for plumbers.

The TPR valve is NOT a water drainage device, although many people, including plumbers, think it is. It is a STEAM drainage device. When those things let loose, what comes out is not water, it is live steam. The reason for the pipe is to have the steam discharge spray on the floor or some other place where it will not hit human beings.

If the pipe "drains" into the pan, it will splash up and scald a person. The amount and flow rate of the discharge is also more than the pan can handle.

Hope this helps;
Here we go again.

Please explain to us how 210 deg. water is steam.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #20  
Old 6/1/09, 3:50 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,524
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
Originally Posted by mlarson View Post
Here we go again.

Please explain to us how 210 deg. water is steam.
Under pressure. 210 degrees, under pressure, and then it hits normal pressure and flashes to steam.

Hope this helps;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #21  
Old 6/1/09, 3:51 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
Originally Posted by wdecker View Post
Under pressure. 210 degrees, under pressure, and then it hits normal pressure and flashes to steam.

Hope this helps;
Not at normal pressures with no head space.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #22  
Old 6/1/09, 5:33 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,219
Default Re: Do you allow the TPR to discharge into the WH pan?

For those that consider the 3/4 drain pipe improper, would you like it if it had a 1" drain pipe off the water heater safety pan?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #23  
Old 6/1/09, 8:32 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,591
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
Originally Posted by wdecker View Post
I see this all the time, and I call it out.

There is a problem here with understanding the concept, even for plumbers.

The TPR valve is NOT a water drainage device, although many people, including plumbers, think it is. It is a STEAM drainage device. When those things let loose, what comes out is not water, it is live steam. The reason for the pipe is to have the steam discharge spray on the floor or some other place where it will not hit human beings.

If the pipe "drains" into the pan, it will splash up and scald a person. The amount and flow rate of the discharge is also more than the pan can handle.

Hope this helps;
Seems the pan would be irrelevant when steam comes out.



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #24  
Old 6/1/09, 8:41 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,591
Default Re: Do you allow the TPR to discharge into the WH pan?

http://www.ilga.gov/commission/jcar/...00I12300R.html
Quote:
Originally Posted by IL plumbing code
Relief Discharge Outlet.

1) A relief discharge outlet shall be indirectly connected to waste. The discharge pipe from the relief valve shall not be located so as to create a safety hazard or to discharge in such a way as to cause damage to the building or its contents. The relief valve shall not discharge through a wall into the outside atmosphere or where there is a possibility of freezing.

2) No reduced coupling, valve or any other restriction shall be installed in the discharge line of any relief valve that would impede the flow of discharge. The discharge line shall be installed from the relief valve to within 6 inches of the floor or receptor and the end of such line shall not be threaded.

3) Any piping used for discharge from the relief valve shall be of metallic material and conform with the requirements of Appendix A, Table A (Approved Materials for Water Distribution Pipe) for potable water piping and shall drain continuously downward to the outlet.

4) The discharge piping shall discharge indirectly into a floor drain, hub drain, service sink, sump or a trapped and vented P-trap which is located in the same room as the water heater. (See Sections 890.1010 and 890.1050(a), (b) and (c).) The trap must have a deep seal to protect against evaporation or shall be fed by means of a priming device designed and installed for that purpose. (The use of a light grade oil in the trap will retard evaporation.)



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #25  
Old 6/2/09, 12:08 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,728
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
Originally Posted by rmaday View Post
Seems the pan would be irrelevant when steam comes out.

Very unlikely comming out af a WATER heater, now a boiler is a different story.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #26  
Old 6/2/09, 12:39 AM
ccurrins's Avatar
ccurrins ccurrins is offline
Active Poster
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 3,233
Please Note: ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Do you allow the TPR to discharge into the WH pan?

Steam or water?


How it Works:
Water boils at 212° F when at sea level or under 14.7 psi of pressure, however, the boiling point increases when under pressure, which allows the water to superheat beyond 212° F. Typical residential water pressure ranges between 40 and 80 psi and at 50 psi, the water can reach 300° F.


Superheated water (now significantly above 212°F) would immediately return to atmospheric pressure (the boiling point of water is 212°F) and flash into steam, causing a sudden increase in volume and release of energy.


If the water in a water heater reaches a temperature of 210°F (before superheating occurs) or the water pressure exceeds 150 psi, the TPR valve will open and release the overheated water. This will allow cold water to enter, lowering the temperature of the water in the tank and consequently the water pressure. The valve will remain open as long as the temperature or pressure exceeds the preset limit.


If the TPR is functioning correctly it will discharge water. If it malfunctions and waits until the water has converted to steam you'll probably have an airborne water heater.
Reply With Quote
  #27  
Old 6/2/09, 7:05 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
If the TPR is functioning correctly it will discharge water. If it malfunctions and waits until the water has converted to steam you'll probably have an airborne water heater.
Exactly Chris,

Thank you for finding that.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #28  
Old 6/2/09, 7:08 PM
Jonathan T. Hittle's Avatar
Jonathan T. Hittle Jonathan T. Hittle is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Eaton, OH
Posts: 94
Default Re: Do you allow the TPR to discharge into the WH pan?

This is a Code question that depends on your local plumbing code. Here it is acceptable. You must be able to see the air gap so that you know that there is a problem. Also many manufactures suggests that you test your TPRV yearly but we all know that they will stick on!
Reply With Quote
Find an InterNACHI certified Oklahoma Home Inspector (and anywhere else in North America)
  #29  
Old 6/2/09, 11:44 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: Do you allow the TPR to discharge into the WH pan?

What about this setup, from today's inspection. How is this different from going directly to the pan???


do-you-allow-tpr-discharge-into-wh-pan-060209-193.jpg do-you-allow-tpr-discharge-into-wh-pan-060209-204.jpg



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #30  
Old 6/2/09, 11:55 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 690
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
Originally Posted by jfunderburk View Post
What about this setup, from today's inspection. How is this different from going directly to the pan???


Attachment 29022 Attachment 29023
That is also a defect as it is not piped separately - write it up
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Radon Discharge bhartley IAC2 Forum 5 3/27/09 7:10 PM
Discharge into a vent? Bob Smith, Jr. Plumbing 1 2/1/09 6:43 AM
Gas water heater TPRV discharge tube?? jacaron Plumbing 10 11/21/08 10:35 PM
And another A/C condensate line discharge question bwilliams HVAC 4 11/7/08 12:20 AM
TPR has PEX2 for discharge piping jlybolt Plumbing 11 7/10/06 12:14 AM


All times are GMT -4. The time now is 7:03 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts