View Poll Results: Can the TPR discharge to a plumbed WH pan?
Yes 39 57.35%
No 28 41.18%
Not sure 1 1.47%
Voters: 68. You may not vote on this poll

Reply
 
LinkBack Thread Tools
  #31  
Old 6/3/09, 12:21 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
Originally Posted by cevans View Post
That is also a defect as it is not piped separately - write it up
Is that a condensate line at top?
Not to mention plastic pipe.
Reply With Quote
Find an InterNACHI certified Idaho Home Inspector (and anywhere else in North America)
  #32  
Old 6/5/09, 12:05 AM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,143
Default Re: Do you allow the TPR to discharge into the WH pan?

Wow, that's so wrong - in so many awesome many ways.
It seems to be a condensate drainage pipe going downward through the insulation - yes? HA!
Reply With Quote
  #33  
Old 6/5/09, 12:09 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
Originally Posted by relliott View Post
Is that a condensate line at top?
Not to mention plastic pipe.
The plastic tubing is from a thermal control relief valve. CPVC is approved for TPR discharge pipes.

They had the thermal control valve, TPR valve, and pan all going to one indirect waste receptor. It was in the attic of a 3 story town home. There is not an easy solution. They'll probably have to live with it.

Here's an interesting find on the same water heater. I pulled back the insulation on the water pipe at the WH to see what type of piping was present...lookie what I found:

do-you-allow-tpr-discharge-into-wh-pan-060209-198.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #34  
Old 6/5/09, 12:22 AM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,143
Default Re: Do you allow the TPR to discharge into the WH pan?

I thought I'd throw in the following:

Relief Valve Importance*

Water is essentially an incompressible solid. It has no latent heat energy within itself to expand when released, unless the water is superheated. Water above 212˚ F is superheated water, and superheated water would really like to turn into steam at atmospheric pressure. It possesses latent heat energy, which can flash into steam and create a force that is not unlike an explosion.

Water would normally boil at 212 ˚F, but inside a tank it can’t expand anywhere so it can’t boil off into steam. Water in a “closed” system and under pressure, such as inside a hot water tank, has a much higher boiling point. For example, where water supplied to a tank is at 50 psi, the boiling point is 297.7˚ F.

Let’s assume a water heater tank has 30 gallons of superheated water inside it. Assume 50 psi and the water temperature is superheated at 300 ˚F. Remember that superheated water really wants to turn into steam. If the tank ruptures, then 30 gallons of superheated water will instantaneously turn into steam in an outwards direction through the rupture.

There is a tremendous amount of energy released as the superheated water is exposed to atmospheric pressure and immediately turns into steam. Every cubic inch of water becomes a foot of steam!
do-you-allow-tpr-discharge-into-wh-pan-energy-30-gal-tank.jpg
Note that at 50 psi, water flashes into steam at 297.7˚ F, and the energy released equals more than 2 million foot-pounds of energy, similar to the explosive energy released by one pound of Nitroglycerin. A 16-inch gun on a USS Iowa class battleship produced a 7,500,000 foot-pounds of energy.
do-you-allow-tpr-discharge-into-wh-pan-uss-iowa-30-gal-tank.jpg
This is why it is essential to avoid excessively high water temperatures and pressures at a water heater tank.

* Excerpt from the course book included with the training course: Hot Water Tank Online Video Course (4 CE).
Reply With Quote
  #35  
Old 6/8/09, 8:02 AM
Shawn Rowe's Avatar
Shawn Rowe Shawn Rowe is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: St. Augustine, FL
Posts: 274
Default Re: Do you allow the TPR to discharge into the WH pan?

2007 Florida Code allows TPR discharge to pan

P2803.6.1.1 Discharge.
The relief valve shall discharge
full size to a safe place of disposal such as the floor, water
heater pan, outside the building or an indirect waste
receptor. The discharge pipe shall not have any trapped
sections and shall have a visible air gap or air gap fitting
located in the same room as the water heater. The discharge
shall be installed in a manner that does not cause
personal injury to occupants in the immediate area or

structural damage to the building.



**************************************
Shawn Rowe, CMI
HomeFirst Inspection Services, LLC
- InfraRed Specialist (Level 1 & Building Science certified)
- Code Certified Residential Building Inspector
- Certified Master Inspector
-- Serving NE Florida, St. Johns, Duval, Flagler, Putnam counties --
Reply With Quote
  #36  
Old 10/2/09, 3:02 PM
Robert Sole's Avatar
Robert Sole Robert Sole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 360
Default Re: Do you allow the TPR to discharge into the WH pan?

Just for information, all the water heater drain pans I have seen have a 1" drain connection.



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #37  
Old 10/2/09, 7:52 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is online now
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 951
Default Re: Do you allow the TPR to discharge into the WH pan?

In my area it is discharges right onto the basement floor.
Attached Thumbnails
do-you-allow-tpr-discharge-into-wh-pan-158.jpg  



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #38  
Old 10/2/09, 8:18 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,918
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
Originally Posted by dokeefe View Post
In my area it is discharges right onto the basement floor.
That looks like a normal installation to me too!

After all, does anyone believe that when a TPR lets go, that a pan and outlet will take care of it? Think again.
Reply With Quote
  #39  
Old 10/2/09, 11:31 PM
John Cahill John Cahill is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Plano, TX
Posts: 812
Default Re: Do you allow the TPR to discharge into the WH pan?

In 25 years I have seen 2 TPR valves discharging. Neither discharged at full volume. It was like a puny spewing. The water heaters were in deplorable condition and I would have recommended replacement regardless of what the valve did.

The risk of water damage is insignificant compared to the problem at hand. Water damage is covered by home owners insurance.

The water heater itself poses the same unrestricted water flow potential as a TPR valve.




Reply With Quote
  #40  
Old 10/3/09, 8:40 AM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is online now
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 951
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
Originally Posted by mcyr View Post
That looks like a normal installation to me too!

After all, does anyone believe that when a TPR lets go, that a pan and outlet will take care of it? Think again.
This will take care of any water.
Attached Thumbnails
do-you-allow-tpr-discharge-into-wh-pan-151.jpg  



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #41  
Old 10/3/09, 11:23 AM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 336
Default Re: Do you allow the TPR to discharge into the WH pan?

international residental code chapter 28 code article 2803.6.1 paragraph 5
Requirements For Discharge Pipe
Discharge to the floor, to an indirect waste receptor or to the outdoors. Where discharging to the outdoors in areas subject to freezing, discharege piping shall first be piped to an indirect waste receptor thru an air gap located in a conditioned space.
Florida Building Code Plumbing chapter 5 code article 504.6 paragraph 5
Requirements For Discharge Pipe
Discharge to the floor,To the water heater pan,to an indirect waste receptor or to the outdoors. etc. etc.

I guess to answere the question it depends on your local jurisdiction



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
  #42  
Old 10/3/09, 12:48 PM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 336
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
Originally Posted by bgromicko View Post
Question: Can a sump pump be an indirect waste receptor with a TPR valve discharge directed towards it?
provided that the discharge point is readily observable by the building occupants. i would say yes



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
  #43  
Old 10/6/09, 10:11 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is online now
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,043
Default Re: Do you allow the TPR to discharge into the WH pan?

Why can you allow it to discharge onto the cement floor in a garage? It will still splatter all over the floor, an 18 inches higher will make a bigger mess. I would think it is a safety issue period, unless it discharges into a plumbing drain.




Fogarty Inspection Services Group of Knoxville TN
Sean Fogarty
Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.homeinspectionknoxville.com
Reply With Quote
Find an InterNACHI certified Idaho Home Inspector (and anywhere else in North America)
  #44  
Old 10/6/09, 10:28 PM
Jeffrey Moore Jeffrey Moore is offline
InterNACHI Member
 
Join Date: Feb 2008
Location: Mesa, AZ
Posts: 255
Default Re: Do you allow the TPR to discharge into the WH pan?

Discharging onto the garage floor is a very common finding
here in AZ. Some will take the time to pipe it to the outside
but not in most of the neighborhoods that are selling now.



Jeff Moore
www.quantumhomeinspections.com
Flir (ITC) Level 1 Thermographer
Mesa, AZ
Reply With Quote
  #45  
Old 10/7/09, 3:14 PM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 336
Default Re: Do you allow the TPR to discharge into the WH pan?

Quote:
Originally Posted by sfogarty View Post
Why can you allow it to discharge onto the cement floor in a garage? It will still splatter all over the floor, an 18 inches higher will make a bigger mess. I would think it is a safety issue period, unless it discharges into a plumbing drain.
ICC residental
p2803.6.1
paragraph1
Shall not be directly connected to a drainage system



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Radon Discharge bhartley IAC2 Indoor Air Forum 5 3/27/09 7:10 PM
Discharge into a vent? Bob Smith, Jr. Plumbing Inspections 1 2/1/09 6:43 AM
Gas water heater TPRV discharge tube?? jacaron Plumbing Inspections 10 11/21/08 10:35 PM
And another A/C condensate line discharge question bwilliams Inspecting HVAC Systems 4 11/7/08 12:20 AM
TPR has PEX2 for discharge piping jlybolt Plumbing Inspections 11 7/10/06 12:14 AM