Do you bond the plumbing supply, when the service to the regulator and stub outs are copper, but the rest is pex??
Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
| Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
|||
|
|||
|
Not sure what you meen by regulator (pressure reducing valve)? If there is considerable length to the copper in the house from the meter, then possibly that would be bonded. But Most pex systems do not need to be bonded. And definitely not the stub outs, that would be a nightmare at all the fixtures. Or maybe nobody has come up with a plastic ground clamp yet !
|
|
#3
|
||||
|
||||
|
2009 IRC E3608.1.1 Metal underground water pipe. A metal underground
water pipe that is in direct contact with the earth for 10 feet (3048 mm) or more, including any well casing effectively bonded to the pipe and that is electrically continuous, or made electrically continuous by bonding around insulating joints or insulating pipe to the points of connection of the grounding electrode conductor and the bonding conductors, shall be considered as a grounding electrode (see Section E3608.1). Interior metal water piping located more than 5 feet (1524 mm) from the entrance to the building shall not be used as part of the grounding electrode system or as a conductor to interconnect electrodes that are part of the grounding electrode system. Commentary: Any metal water pipe in contact with the earth for 10 feet (3048 mm) or more is considered a grounding electrode. It is often thought that only the main water service piping fits this description, but any metal water pipe, such as an irrigation pipe or pipe from a water well, if buried in the earth for 10 feet (3048 mm) or more, must be bonded as part of the grounding electrode system. The pipe could be of any material such as copper or steel because the code does not mention the type of metal. In many houses, a water meter, water-pressure reducing valve, or similar equipment is installed in the water supply line. A bonding jumper of the same size as the grounding electrode conductor is installed around such devices because many of these devices are made of nonconductive materials. In many cases, when the device is removed and/or replaced, the grounding electrode is disconnected. A useful practice is to leave enough slack in the bonding jumper around the device that the jumper will not have to be taken off the piping in the event the device is replaced. The code assumes that the first 5 feet (1524 mm) of water piping, measured from the point that the piping penetrates an outside wall or floor slab on grade, will not be disturbed or altered by plumbing work. Any piping beyond 5 feet (1524 mm) into the building is more likely to be altered such that electrical continuity is lost. This alteration could take the form of the installation of plastic piping, nonconductive components (e.g. water filters), dielectric fittings or the removal of grounding clamps. A supplemental grounding electrode is always required when a water pipe electrode is used. The most commonly used supplemental grounding electrode is the ground rod. That is why in so many dwellings a grounding electrode conductor is run from the service equipment to the entry point of the water pipe and another grounding electrode conductor is run to a ground rod. The ground rod is quite often driven into the ground close to the service equipment. A grounding electrode conductor that connects the service equipment to a ground rod, pipe or plate electrode and connects to no other elec- trodes is not required to be larger than size 6 AWG copper or 4 AWG aluminum (see note to Table E3603.1 and Section E3610.2). “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com Last edited by jfunderburk; 3/17/11 at 12:41 PM.. |
|
#4
|
||||
|
||||
|
The answer is run a grounding wire from your copper main to all plumbing and bond to it!
Beauchemin, Marc-Andre (CMI) BMAinspection.com Brossard-Quebec Canada Last edited by mbeauchemin; 3/17/11 at 12:36 AM.. Reason: plumbing |
|
#5
|
||||
|
||||
|
Uh, no? Was this a serious question, or are you jerking our chain?
You cannot create an electrical bond between plastic and metal. Stub-outs and fixtures do not require independent bonding as they are not "likely to become energized." IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
||||
|
||||
|
Jeff, he seems to be saying the service pipe is copper. Irrespective of the distribution being PEX, if the service pipe is buried for 10' or more, it should be treated as part of the GES.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#7
|
||||
|
||||
|
Quote:
Only sections of the pipe were copper. There was no bond, but I wanted to make sure since some of the pipe was copper you still were not required in some manner. I didn't think it should be but was just wondered more than anything. Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#8
|
||||
|
||||
|
I'm not sure I agree with that, but it certainly can't hurt anyting to have the main line bonded to the GE.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
||||
|
||||
|
See the code in Post 3. I know you CA guys don't use the IRC, however I think that comes from the NEC.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#10
|
||||
|
||||
|
That code says the pipe can be used as the GE. A UFER would make that pipe unnecessary as the GE. Bonding it to the existing GE would be optional.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#11
|
||||
|
||||
|
Quote:
And it must be grounded within 5' of entry into the home. So, to answer one of his questions, any metal piping more than 5' from the house wall penetration does not require bonding/grounding. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#12
|
|||
|
|||
|
Quote:
I think it depends where he is. Up here the incoming copper tubing is the only GE required. |
|
#13
|
||||
|
||||
|
An entry water line is not required to be bonded in my neck of the woods.
|
| Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
A few comments about the info in this thread.
Any metallic water pipe that qualifies as an electrode (10' in contact with the earth) must be used as part of a GES (grounding electrode system) since it's considered present by the NEC. That connection to the system must be within 5' of it's entrance into the structure and it must be supplemented by at least one other electrode. If there is not 10' of metallic pipe in contact with the earth but the interior of the structure has a metallic piping system, then that piping system is require to be bonded even though it does not qualify as an electrode. Since short sections of metallic pipe do not make a system they are not required to be bonded. |
|
#15
|
||||
|
||||
|
Quote:
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| HELP! What do you call a 3 prong male plug with a cord. | gromicko | Electrical Inspections | 5 | 1/9/09 12:33 AM |
| Plumbing Supply Tubing | rroeske | Plumbing Inspections | 17 | 1/15/07 9:14 AM |
| PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. | gromicko | Miscellaneous Discussion for Inspectors | 53 | 8/30/06 5:58 PM |
| A few useful posts - I forget from whom | jmichalski | Plumbing Inspections | 12 | 3/30/06 9:06 PM |