Default Double TPR

Here's a good one. I like that they used a second TPR instead of a 90 deg bend. The question is, do we think this is dangerous? It's clearly improper.
My thought was that it is dangerous as it may require more pressure to build up before it will actually release, but i'm not up on my engineering enough to know whether that's really the case.
Attached Thumbnails
double-tpr-double-tpr2.jpg  
Reply With Quote
  #2  
Old 6/26/08, 9:43 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Double TPR

That's just stupid.

The second TPR is acting a a check valve in the wrong direction.

Yes it's very Dangerous as effectively there is no TPR.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #3  
Old 6/26/08, 9:46 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,744
Default Re: Double TPR

Quote:
Originally Posted by Matthew Hopkins
The question is, do we think this is dangerous?
Yes, this part of we does.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #4  
Old 6/26/08, 9:52 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: Double TPR

We say it's a lot cheaper to just buy and install a plug

That's what all of these components have accomplished



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #5  
Old 6/26/08, 10:23 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 4,403
Default Re: Double TPR

very very not good....and then some....



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #6  
Old 6/26/08, 10:29 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,647
Default Re: Double TPR

It certainly defies the manufacturer's installation instructions...should there be an argument anywhere.

You may as well had sweated a cap on the end of it.
Reply With Quote
  #7  
Old 6/26/08, 10:34 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 789
Default Re: Double TPR

Safety Issue, Repair: I recommend removing the TPR valve installed within the discharge piping. TPR dip tub must be positioned within the top 8 in. of water heater to be effective. Present installation could cause injury/death.



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
  #8  
Old 6/26/08, 10:42 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 789
Default Re: Double TPR

Quote:
Originally Posted by jbushart
You may as well had sweated a cap on the end of it.
Why sweat it when you can screw it...
Attached Thumbnails
double-tpr-dcp00524a.jpg  



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
  #9  
Old 6/26/08, 11:10 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,647
Default Re: Double TPR

Quote:
Originally Posted by mgratton
Safety Issue, Repair: I recommend removing the TPR valve installed within the discharge piping. TPR dip tub must be positioned within the top 8 in. of water heater to be effective. Present installation could cause injury/death.
The temperature relief valve, required and designed to prevent the water heater from exploding, is incorrectly installed. Recommend that a qualified plumber be contracted to repair or replace as necessary.
Reply With Quote
  #10  
Old 6/26/08, 11:31 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 789
Default Re: Double TPR

Quote:
Originally Posted by jbushart
The temperature relief valve, required and designed to prevent the water heater from exploding, is incorrectly installed. Recommend that a qualified plumber be contracted to repair or replace as necessary.
The Temperature Pressure Relief valve required and designed to prevent the water heater from exploding is correctly installed... However, the other TPR valve installed within the discharge tube isn't and could cause injury/death.

I recommend that a licensed plumber be contacted promptly for appropriate repairs.



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
  #11  
Old 6/26/08, 11:46 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: Double TPR

Quote:
Originally Posted by mgratton
Safety Issue, Repair: I recommend removing the TPR valve installed within the discharge piping. TPR dip tub must be positioned within the top 8 in. of water heater to be effective. Present installation could cause injury/death.
Marcel,

Typo or misinformation
6" not 8"

Watts http://www.watts.com/pro/divisions/watersafety_flowcontrol/support/support_t-p.asp
Correct Installation of T&P Relief Valves Important Instructions: Relief Valves and Automatic Gas Shut-Off Devices
Combination temperature and pressure relief valves with extension thermostats must be installed so that the temperature-sensing element is immersed in the water within the top 6" (152mm) of the water storage tank. They must be installed either in the hot outlet service line or directly in a tank tapping. Combination temperature and pressure relief valves that do not have extension elements must be mounted directly in a tank tapping located within the top 6" (152mm) of the water storage tank. Valves must be located so as to assure isolation from flue gas heat or other ambient conditions that are not indicative of stored water temperature.



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #12  
Old 6/26/08, 11:59 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 789
Default Re: Double TPR

Quote:
Originally Posted by badair
Marcel,

Typo or misinformation
6" not 8"
Neither, it's actually 5 7/8 inches according to some local buildling code but will an inch or two make that much of a difference...



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/

Last edited by mgratton; 6/27/08 at 12:03 AM..
Reply With Quote
  #13  
Old 6/27/08, 2:12 AM
Matthew Hopkins Matthew Hopkins is offline
New User
 
Join Date: Jun 2007
Location: Portland, OR
Posts: 23
Please Note: Matthew Hopkins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double TPR

Crap, I hadn't actually noticed the second was going the wrong way, VERY BAD. Gotta call the realtor back. Thanks guys.
Reply With Quote
  #14  
Old 6/27/08, 8:20 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,744
Default Re: Double TPR

Quote:
Originally Posted by Matthew Hopkins
Crap, I hadn't actually noticed the second was going the wrong way, VERY BAD. Gotta call the realtor back. Thanks guys.
You may also want to consider amending the report to your client. A verbal warning is not sufficient, IMO.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #15  
Old 6/27/08, 3:41 PM
Kenneth Lott's Avatar
Kenneth Lott Kenneth Lott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,361
Default Re: Double TPR

Quote:
Originally Posted by Matthew Hopkins
Here's a good one. I like that they used a second TPR instead of a 90 deg bend. The question is, do we think this is dangerous? It's clearly improper.
My thought was that it is dangerous as it may require more pressure to build up before it will actually release, but i'm not up on my engineering enough to know whether that's really the case.
Most definitely dangerous, first of all it is backwards, you need to report this guy before he gets someone hurt or worse.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Double lugged breakers? dbook Electrical 7 4/30/08 1:35 AM
Double tapping question mroe Electrical 17 8/30/07 9:32 AM
Double Tap Questions jkogel Electrical 6 6/28/07 10:46 PM
Doorbell transformer double tap bsmith Electrical 11 4/17/06 1:48 PM
Double Taps rwand1 Canadian Inspectors 30 3/29/06 8:16 PM


All times are GMT -4. The time now is 10:42 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts