Default Electric next to gas regulator

I would like to here your thoughts on this.

I was wondering if anyone writes up the 3 foot clearance from the gas regulator and any electrical connection that can ignite that gas. If you don't call it out, why not. It only makes sense to me that you do no want electric next to something that has the potential to release natural gas into the air.


Gas Meter Clearance
National Fuel Gas Code 54-5.7.2.3 “Gas meters shall be located at least 3 ft. from sources of ignition.” Ignition is considered anything that can ignite gas, such as electric motors, switches, outlets and most exhaust/vent terminations such as furnace and/or dryer vent. 3 foot clearance also applies to windows that can be opened and/or crawlspace vents.
Reply With Quote
  #2  
Old 10/2/07, 10:49 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Electric next to gas regulator

Gas meter yes, gas regulator no.
Reply With Quote
  #3  
Old 10/2/07, 10:55 PM
William M. Corbett's Avatar
William M. Corbett William M. Corbett is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Remlap, AL
Posts: 231
Default Re: Electric next to gas regulator

Quote:
Originally Posted by Kevin Luce
I would like to here your thoughts on this.

I was wondering if anyone writes up the 3 foot clearance from the gas regulator and any electrical connection that can ignite that gas. If you don't call it out, why not. It only makes sense to me that you do no want electric next to something that has the potential to release natural gas into the air.


Gas Meter Clearance
National Fuel Gas Code 54-5.7.2.3 “Gas meters shall be located at least 3 ft. from sources of ignition.” Ignition is considered anything that can ignite gas, such as electric motors, switches, outlets and most exhaust/vent terminations such as furnace and/or dryer vent. 3 foot clearance also applies to windows that can be opened and/or crawlspace vents.
The code stated is for a gas meter not a regulator. If there was an electrical outlet, switch exhaust vent, etcetera near the gas meter I would write it up. (however, I rarely see such practices here)



Bill Corbett C.H.I.
Magic City Inspections LLC
InspectingtheUnexpected.com
Reply With Quote
  #4  
Old 10/2/07, 10:59 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Electric next to gas regulator

Agreed. I don't make up my own standards.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 10/2/07, 11:39 PM
Kevin Luce's Avatar
Kevin Luce Kevin Luce is offline
Active Poster
 
Join Date: Apr 2005
Location: Highland, Indiana
Posts: 201
Please Note: Kevin Luce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electric next to gas regulator

When I talked to the local gas company years ago, we talked about the three foot clearance needs to be from the item that can ignite gas and the port where gas can be release from.
Attached Files
File Type: pdf Clearance from electric and gas.pdf (101.6 KB, 340 views)
Reply With Quote
  #6  
Old 10/3/07, 10:51 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Electric next to gas regulator

If you know that your local AHJ has such a requirement in addition to the meter itself, then you probably should note that in your report.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #7  
Old 2/4/10, 11:40 AM
thorn2 thorn2 is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Pleasantville, Ohio
Posts: 30
Default Re: Electric next to gas regulator

Should a gas regulator vent be piped to the exterior? In commercial applications it is required.
Reply With Quote
  #8  
Old 2/4/10, 5:17 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Electric next to gas regulator

Quote:
Originally Posted by thorn2 View Post
Should a gas regulator vent be piped to the exterior? In commercial applications it is required.
It is required around here.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Battery Recall - Milwaukee Electric Tool Co. pabernathy Electrical Inspections 3 7/12/07 10:08 AM
Square D Files Lawsuit to Prevent Counterfeiting jtedesco1 Electrical Inspections 2 5/26/06 6:36 PM
Electric rates go up! darnold1 Electrical Inspections 3 4/28/06 3:06 PM


All times are GMT -4. The time now is 2:29 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts