Default electric water heater

A GE electric water heater stated "total wattage - 4500/3308" The instruction manual stated that for 240v 4500w, the breaker is 25 amps. For 208v, it's 30 amp. Do I say that the breaker should be 25 amps cause it's a 240v circuit or do i say the installed 30amp is ok cause the heating elements run at 208v? thanks
Reply With Quote
  #2  
Old 6/1/07, 4:48 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: electric water heater

Quote:
Originally Posted by Scott Schultz
A GE electric water heater stated "total wattage - 4500/3308" The instruction manual stated that for 240v 4500w, the breaker is 25 amps. For 208v, it's 30 amp. Do I say that the breaker should be 25 amps cause it's a 240v circuit or do i say the installed 30amp is ok cause the heating elements run at 208v? thanks
30 amp breaker is fine 240 volt heater on 208 will just be a little slower .If this is a home I would not be concerned.
Reply With Quote
  #3  
Old 6/1/07, 7:32 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: electric water heater

208Volts is a 3-phase service distribution panel.
Can someone tell me why a home would have such?
Roy is correct, you can run a AC/DC Welder on 208, but the amperage setting will have to be set higher than it would be at 240 volts.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #4  
Old 6/1/07, 7:49 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: electric water heater

Quote:
Originally Posted by mcyr
208Volts is a 3-phase service distribution panel.
Can someone tell me why a home would have such?
Roy is correct, you can run a AC/DC Welder on 208, but the amperage setting will have to be set higher than it would be at 240 volts.

Marcel
I have never seen a 208 volt system in a home in Canada.
I expect the manufacture just put two voltages on the name plate .
This unfortunately leads to some confusion with many people .
The Water heater is single phase so it does not care as long as the voltage is not above 240 volts.
Reply With Quote
  #5  
Old 6/1/07, 10:01 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: electric water heater

Quote:
Originally Posted by rcooke
I have never seen a 208 volt system in a home in Canada
Do they serve condo units at 120/208 in Canada like they so often do in the US? A condo or high-rise is where you'd normally expect to find 208 in a dwelling unit.
Reply With Quote
  #6  
Old 6/1/07, 10:08 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: electric water heater

Quote:
Originally Posted by Marc D. Shunk
Do they serve condo units at 120/208 in Canada like they so often do in the US? A condo or high-rise is where you'd normally expect to find 208 in a dwelling unit.
We do not have a lot of Condos in my area but any I have seen are 120/240 volt.
I have often though how great it would be to have 208 in the home one more wire and 50% more power.
Must be a reason but I have no idea why not.
Reply With Quote
  #7  
Old 6/2/07, 8:45 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: electric water heater

Another thing you have to remember.......if the system is truly 120/240V then you can't use a 208V breaker in the panel....the line to line would be 240V and the breaker is only listed for 208V.....

if the breaker is listed 120/240V then you are fine but if the breaker is a 120/208V then it is not supposed to be in that panel enclosure...IF the panel inclosure is a 120/240V listed panel....and the voltage you are dealing with is truly 120/240V and indeed not 208V....

Sorry...that gets a bit cryptic but you know what I mean.......if breaker is a 208V rated breaker and the line to line potential is 240V then the breaker has to be rated for 240V line to line.....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 6/2/07, 9:05 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: electric water heater

Quote:
Originally Posted by Scott Schultz
Do I say that the breaker should be 25 amps cause it's a 240v circuit or do i say the installed 30amp is ok cause the heating elements run at 208v? thanks
There may be some confusion here.
If I read your post correctly it is a residential WH being supplied by 240 VAC. The installed OCP is 30 A and therfore exceeds the mfgs. recommended OCP of 25 A when supplied by 240 V.
Reply With Quote
  #9  
Old 6/2/07, 9:24 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: electric water heater

Mine was just educational Michael...in regards to reading breakers ratings...seemed like a nice educational moment...lol

If the manual says install a 25A breaker...I would install a 25A breaker.....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 6/2/07, 9:30 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: electric water heater

Paul,
Absolutely!
Your always educational and a great NACHI asset.

Now apply some ice to your head to prevent swelling.
Reply With Quote
  #11  
Old 6/2/07, 9:49 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: electric water heater

hell man.......I am so humble...CRAP sits higher on the plain of life than me and my swelling head.....but it's all good.....wife reminds me everyday what I am...(sigh)....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 6/2/07, 9:55 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: electric water heater

Quote:
Originally Posted by pabernathy
...wife reminds me everyday what I am...(sigh)....
Wives are way too good at that. I know mine is.
Reply With Quote
  #13  
Old 6/5/07, 12:18 AM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 211
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: electric water heater

Michael,

The manual for the water heater stated....
240v - 25 amp breaker
208v - 30 amp breaker

I'm thinking that the line itself is 240v but the heating element may be 208v? wasn't sure, but this particular house had a 30 amp breaker installed in the panel and since I've never seen 208v, assumed it was a 240v(like everything else is) and said to change the breaker to 25.
Reply With Quote
  #14  
Old 6/5/07, 6:20 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: electric water heater

Quote:
Originally Posted by Scott Schultz
Michael,

The manual for the water heater stated....
240v - 25 amp breaker
208v - 30 amp breaker

I'm thinking that the line itself is 240v but the heating element may be 208v? wasn't sure, but this particular house had a 30 amp breaker installed in the panel and since I've never seen 208v, assumed it was a 240v(like everything else is) and said to change the breaker to 25.
Scott, the heater element is probably rated in watts so a different breaker is required for protection depending on input voltage.

You did the right thing in calling out the need for a change.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical 72 3/12/08 12:19 AM
Solar water heating + electric water heater Todd M. Soper Plumbing 20 5/30/07 7:31 AM
Venting an oil-fired water heater mh718 HVAC 3 11/16/06 10:36 AM
TPR & Combusiton Air thejnicki Plumbing 16 9/18/06 9:55 PM


All times are GMT -4. The time now is 8:39 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts