A GE electric water heater stated "total wattage - 4500/3308" The instruction manual stated that for 240v 4500w, the breaker is 25 amps. For 208v, it's 30 amp. Do I say that the breaker should be 25 amps cause it's a 240v circuit or do i say the installed 30amp is ok cause the heating elements run at 208v? thanks
|
|
#2
|
|||
|
|||
|
Please Note:
rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#3
|
||||
|
||||
|
208Volts is a 3-phase service distribution panel.
Can someone tell me why a home would have such? Roy is correct, you can run a AC/DC Welder on 208, but the amperage setting will have to be set higher than it would be at 240 volts. Marcel Cyr Home and Commercial Property Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards Commercial Builder CertainTeed Master Shingle Applicator Shingle Technology Ouellet Associaties Inc. http://www.oaconstruction.com/ |
|
#4
|
|||
|
|||
|
Please Note:
rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I expect the manufacture just put two voltages on the name plate . This unfortunately leads to some confusion with many people . The Water heater is single phase so it does not care as long as the voltage is not above 240 volts. |
|
#5
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#6
|
|||
|
|||
|
Please Note:
rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I have often though how great it would be to have 208 in the home one more wire and 50% more power. Must be a reason but I have no idea why not. |
|
#7
|
||||
|
||||
|
Another thing you have to remember.......if the system is truly 120/240V then you can't use a 208V breaker in the panel....the line to line would be 240V and the breaker is only listed for 208V.....
if the breaker is listed 120/240V then you are fine but if the breaker is a 120/208V then it is not supposed to be in that panel enclosure...IF the panel inclosure is a 120/240V listed panel....and the voltage you are dealing with is truly 120/240V and indeed not 208V.... Sorry...that gets a bit cryptic but you know what I mean.......if breaker is a 208V rated breaker and the line to line potential is 240V then the breaker has to be rated for 240V line to line..... Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#8
|
||||
|
||||
|
Quote:
If I read your post correctly it is a residential WH being supplied by 240 VAC. The installed OCP is 30 A and therfore exceeds the mfgs. recommended OCP of 25 A when supplied by 240 V. |
|
#9
|
||||
|
||||
|
Mine was just educational Michael...in regards to reading breakers ratings...seemed like a nice educational moment...lol
If the manual says install a 25A breaker...I would install a 25A breaker..... Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#10
|
||||
|
||||
|
Paul,
Absolutely! Your always educational and a great NACHI asset. Now apply some ice to your head to prevent swelling. |
|
#11
|
||||
|
||||
|
hell man.......I am so humble...CRAP sits higher on the plain of life than me and my swelling head.....but it's all good.....wife reminds me everyday what I am...(sigh)....
Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#12
|
||||
|
||||
|
Quote:
|
|
#13
|
|||
|
|||
|
Please Note:
Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Michael,
The manual for the water heater stated.... 240v - 25 amp breaker 208v - 30 amp breaker I'm thinking that the line itself is 240v but the heating element may be 208v? wasn't sure, but this particular house had a 30 amp breaker installed in the panel and since I've never seen 208v, assumed it was a 240v(like everything else is) and said to change the breaker to 25. |
|
#14
|
||||
|
||||
|
Quote:
You did the right thing in calling out the need for a change. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Help. What is the correct way to report a breaker that is too big. | gromicko | Electrical | 72 | 3/12/08 12:19 AM |
| Solar water heating + electric water heater | Todd M. Soper | Plumbing | 20 | 5/30/07 7:31 AM |
| Venting an oil-fired water heater | mh718 | HVAC | 3 | 11/16/06 10:36 AM |
| TPR & Combusiton Air | thejnicki | Plumbing | 16 | 9/18/06 9:55 PM |