Default Electric water heater?

Do electric water heaters need to be at a height of 18" as well? I sure the answer is yes, but I thought I would ask yall before I write it up.
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/6/10, 5:10 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Electric water heater?

Uh....no. They don't.

Why are you sure...or why would you even think...the answer is "yes"?

Start with thinking about exactly what part of the water heater is required to be 18" from the floor and when.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 5/6/10, 5:13 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Electric water heater?

One must be aware of the reason behind a code, before one can elaborate further.
Make suggestions based on code, plus common sense.
Reply With Quote
  #4  
Old 5/6/10, 5:21 PM
Chris Mainka's Avatar
Chris Mainka Chris Mainka is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Houston, Tx
Posts: 128
Default Re: Electric water heater?

Thanks Bob - That is why I asked.
Reply With Quote
  #5  
Old 5/6/10, 6:10 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Electric water heater?

Not busting your chops as much as showing my reasoning when writing reports.
Required 18" is in garages for gas heaters only.

P.S (has nothing to do with water)(all about flammable gases)
Reply With Quote
  #6  
Old 5/6/10, 6:13 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Electric water heater?

Quote:
Originally Posted by belliott View Post

P.S (has nothing to do with water)(all about flammable gases)
And that which can ignite them.

Now, if the electric WH was set-up like an old electric range, with the heat elements exposed and underneath the tank, I would say yes, 18 inches is necessary.
Reply With Quote
  #7  
Old 5/6/10, 6:22 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Electric water heater?

Perhaps you guys should explain to Chris under what circumstances a gas water heater in a garage would NOT need to be raised.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #8  
Old 5/6/10, 9:25 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Electric water heater?

Quote:
Originally Posted by jbushart View Post
Uh....no. They don't.

Why are you sure...or why would you even think...the answer is "yes"?

Start with thinking about exactly what part of the water heater is required to be 18" from the floor and when.
I wouldn't be too quick to make that my final answer for all situations and jurisdictions. I have seen it required that the bottom element be elevated 18 inches above the floor.

IRC P2801.6 Water heaters installed in garages (note that this is in the plumbing section, not the gas fired appliance section).
Quote:
Water heaters having an ignition source shall be elevated such that the source of ignition is not less than 18 inches (457 mm) above the garage floor.
The commentary goes on to describe ignition source as including "electrical component capable of producing a spark or an arc." and "This section effectively prohibits the installation of water heaters directly on the floor of residential garages."

R202 Ignition Source
Quote:
A flame spark or hot surface capable of igniting flammable vapors or fumes. Such sources include appliance burners, burner ignitions and electrical switching devices
Excerpt from electric water heater installation manual http://www.americanwaterheater.com/s.../res-elect.pdf
Quote:
Note: Local codes and requirements in your area may
require the installation of your water heater be
accomplished in a way that the bottom element is elevated
from the floor at least 18 inches.
If the bottom element is not at least 18 inches above the floor, I will comment on it. Lowboy units also often have the thermostat and contacts located near the bottom of the unit.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 5/7/10 at 2:25 AM..
Reply With Quote
  #9  
Old 5/6/10, 10:12 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Electric water heater?

Quote:
Originally Posted by cevans View Post
I wouldn't be too quick to make that my final answer for all situations and jurusdictions. I have seen it required that the bottom element be elevated 18 inches above the floor.
We will agree to disagree.

Your interpretation would require all electrical receptacles to be elevated at that same height, as well, in addition to any other permanently installed electrical device, such as freezers. That is not what the code is addressing, here.

If it were, the same code would not forbid your scenerio and still allow for the FVIR gas heater to be placed on garage floor.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #10  
Old 5/6/10, 10:33 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Electric water heater?

Quote:
Originally Posted by jbushart View Post
We will agree to disagree.

Your interpretation would require all electrical receptacles to be elevated at that same height, as well, in addition to any other permanently installed electrical device, such as freezers. That is not what the code is addressing, here.

If it were, the same code would not forbid your scenerio and still allow for the FVIR gas heater to be placed on garage floor.
M1307.3 Elevation of Ignition Source (mechanical section) addresses the issue with regard to appliances not specifically covered in other sections.

G2408.2 Elevation of Ignition Sources (fuel gas section) specifically addresses the issue relative to gas fired appliances (e.g., gas fired water heaters) and includes the exception for appliances listed as flammable vapor ignition resistant.

We can agree to disagree and we can agree to disagree with the standards, but the standards are what they are. The 18 inch standard in garages is not restricted to water heaters nor is it restricted to fuel fired appliances. The topic is addressed specifically in at least three separate sections of the IRC. This is not accidental.

Not directly related but I came upon this tidbit of Darwin's theory at work while looking for a real life example. A little humor to keep it light
Quote:
Four or five years ago, Farina said, a couple of gentlemen in Anchorage put some rusty gun barrels in gasoline in the bathtub in their mobile home to soak. They thought that would remove rust while they went to the other room to have a smoke. The resulting explosion and fire almost removed them.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 5/7/10 at 2:19 AM..
Reply With Quote
  #11  
Old 5/6/10, 10:39 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Electric water heater?

I stand firm that an "ignition source" (pilot and burner) is different from a "potential ignition source" (spark from an electrical receptacle, electric heating element in a water heater, etc) and the IRC is addressing open flames and sparks intended to ignite them, which is why this requirement is in the Mechanical and Gas codes (as you pointed out) and not the Electrical code portion of the IRC.

You can warn your client about anything you want, since codes do not restrict home inspection reports, but I would never write up an unelevated electrical water heater in a garage as being defective.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167

Last edited by jbushart; 5/6/10 at 10:44 PM..
Reply With Quote
  #12  
Old 5/6/10, 11:48 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Electric water heater?

Quote:
Originally Posted by jbushart View Post
I stand firm that an "ignition source" (pilot and burner) is different from a "potential ignition source" (spark from an electrical receptacle, electric heating element in a water heater, etc) and the IRC is addressing open flames and sparks intended to ignite them, which is why this requirement is in the Mechanical and Gas codes (as you pointed out) and not the Electrical code portion of the IRC.

You can warn your client about anything you want, since codes do not restrict home inspection reports, but I would never write up an unelevated electrical water heater in a garage as being defective.
You can argue this both ways as many have and still do (including AHJs). You have chosen to ignore the reference to electrical switching devices in the IRC definition of ignition sources (not potential)

My point was that the answer was not so simple and straight forward as you indicated and for a TX inspector such as Chris your reply is downright wrong.

From the TREC SOP for Texas Real Estate Inspections (emphasis added):
Quote:
(3) report as Deficient:
(A) inoperative unit(s);
(B) leaking or corroded fittings or tank(s);
(C) broken or missing parts or controls;
(D) the lack of a cold water shut-off valve;
(E) if applicable, the lack of a pan and drain system and the improper termination of the pan drain line;
(F) an unsafe location;
(G) burners, burner ignition devices or heating elements, switches, or thermostats that are not a minimum of 18 inches above the lowest garage floor elevation, unless the unit is listed for garage floor installation;
(H) inappropriate location;
(I) inadequate access and clearances;
(J) the lack of protection from physical damage;
(K) a temperature and pressure relief valve that:
(i) does not operate manually;
(ii) leaks;
(iii) is damaged;
(iv) cannot be tested due to obstructions;
(v) is corroded; or
(vi) is improperly located; and
(L) temperature and pressure relief valve discharge piping that:
(i) lacks gravity drainage;
(ii) is improperly sized;
(iii) has inadequate material; or
(iv) lacks proper termination;
So back to Chris' original question, for him the correct answer is emphatically YES, but only to the lowest electrical component. There is no reason Chris should be made to feel foolish for asking his question.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 5/6/10 at 11:55 PM..
Reply With Quote
  #13  
Old 5/7/10, 6:53 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Electric water heater?

I agree Chuck...
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/7/10, 9:21 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Electric water heater?

You're right. TREC requirements were not considered in my answer. I was wrong. Sorry.

While I defer to your TREC requirements, I still disagree, however, with your IRC interpretation.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167

Last edited by jbushart; 5/7/10 at 9:25 AM..
Reply With Quote
  #15  
Old 5/7/10, 9:33 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Electric water heater?

While debatable because of ambiguous wording (imagine that) even the 2006 IRC Commentary on this subject supports Chuck's interpretation in my opinion. It's not just a TREC thing.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Whirlpool Electric Water Heater bhartley Plumbing Inspections 2 4/20/07 9:41 PM
Water Heater Dip Tube Failure jacaron Plumbing Inspections 2 2/24/07 11:28 PM
Venting an oil-fired water heater mh718 Inspecting HVAC Systems 3 11/16/06 9:36 AM


All times are GMT -4. The time now is 2:29 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts