#1
|
||||
|
||||
|
Hello All
I would like some imput on electric water heaters being elevated 18 inches if installed in a garage. Some of the water heater manufactures state in their instalation instructions that electric water heaters need to be elevated 18 inches because of the risk of explosion due to a spark when turned on. some have gaskets around the access covers some don't. So should they be elevated or not? Gas was required to be elevated untill 2004 when the design was changed and became sealed at the lower section. Thanks Mark House 2 Home LLC 503-602-1420 HomePros@House2HomeLLC.ORG Protecting Peace of Mind One House at a Time IAC2 Certified IR Certified A favorite place on Google Maps |
| Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
An electric water heater can be an ignition source as well, and if you look in the IRC it includes not only flame but also "spark" and includes electrical switching devices.
Look in the mechanical section, it references ignition source, look in the definitions, it matches up to what an electric water heater is. P. Nathan Thornberry Inspector Services Group www.InspectorServicesGroup.com | www.RecallChek.com | www.90daywarranty.com | www.AlarmLeadsProgram.com | www.BAMdashboard.com | www.UltimateInspectorWebsites.com | www.PowerUserConference.com Nick Gromicko, the founder of InterNACHI, endorses RecallChek and personally negotiated for InterNACHI members to receive 5 FREE RecallChek reports! To Contact me: Nathan@NathanThornberry.com www.NathanThornberry.com |
|
#3
|
||||
|
||||
|
Please Note:
dandersen is a non-member guest and is in no way affiliated with InterNACHI or its members.
The ignition source (for electric) is not at the bottom of the water heater (gas is).
Why does it have to be raised 18"? Furnaces don't have to be raised either. Their burner is >18" above the floor. |
|
#4
|
||||
|
||||
|
The bottom coil on my electric water heater is 10" off the floor so it would not require the normal height stand but would still need to be elevated.
Washington requires that home inspectors "Report as a fire hazard the presence of any ignition source (gas and electric water heaters, electrical receptacles, electronic air cleaners, motors of installed appliances, etc.) that is within eighteen inches of the garage floor." Stephen Stanczyk Washington State Licensed Home Inspector # 221 President, Washington Association of Property Inspectors (WAPI) (253) 241-0602 calls answered until 10pm Pierce County -Thurston County - King County - Snohomish County |
|
#5
|
||||
|
||||
|
That applies here also!
THE RIGHT TRAK CIAQP, IAC2 Board Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq apoteyes@gmail.com Cell: 705-971-2096 Ph : 705-946-2676 |
|
#6
|
||||
|
||||
|
It is a matter of interpetation.
The T-stat on a residential electric water heater are #1) sealed contacts and #2) more than 18" above the bottom of the water heater on some models, so there is no reason to elevate the tank. Let the Code Officer know how stupid his determination is. LEED Green Associates Inachi US Member of the Year Award 2009 Best Home Inspector Software http://co.nachi.org/inachiawards |
|
#7
|
||||
|
||||
|
Quote:
Stephen Stanczyk Washington State Licensed Home Inspector # 221 President, Washington Association of Property Inspectors (WAPI) (253) 241-0602 calls answered until 10pm Pierce County -Thurston County - King County - Snohomish County |
|
#8
|
||||
|
||||
|
The screws you are looking at is for the Line Voltage, and the contactor is in a sealed case.
Believe what you want. I will not call out an electric water heater in a garage. LEED Green Associates Inachi US Member of the Year Award 2009 Best Home Inspector Software http://co.nachi.org/inachiawards |
|
#9
|
||||
|
||||
|
As David alluded to, the requirement is for elevation of the ignition source. That does not equate to the water heater needing to be elevated 18 inches above the floor.
I have an electric water heater in my garage. The lowest potential source of ignition is 10 inches above the bottom of the unit. The unit itself only needs to be elevated 8 inches to to meet the 18 inch requirement. In Texas the state SOP requires electric water heaters to be reported as a defect if they do not meet the clearance requirement. Check for any specific rules in your state. Has Evacuated to a Nate Free Zone Chuck Evans (TREC #7657) Level III Infraspection Institute Certified Infrared Thermographer (#8402) HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook Houston Thermal Inspections & Infrared Imaging Find us on Facebook Houston Home Inspector Houston, TX |
|
#10
|
||||
|
||||
|
For those that are really worried that the electric water heater needs to be at 18", because of the if "Spark", and I don't believe the garage has been labeled as a hazardous zone as of yet, maybe you should recommend one of these.
![]() http://www.hubbellheaters.com/html/modeler.htm LEED Green Associates Inachi US Member of the Year Award 2009 Best Home Inspector Software http://co.nachi.org/inachiawards |
|
#11
|
||||
|
||||
|
Why be a smartass about it?
Has Evacuated to a Nate Free Zone Chuck Evans (TREC #7657) Level III Infraspection Institute Certified Infrared Thermographer (#8402) HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook Houston Thermal Inspections & Infrared Imaging Find us on Facebook Houston Home Inspector Houston, TX |
|
#12
|
||||
|
||||
|
Because I don't think they have to be elevated for the worse scenario of any flammable fumes that can accumulate in a residential garage.
It is an over reaction. If it were that dangerous, they would have mandated electric water heaters to be designed like the gas ones in 2003. Flammable Vapor Ignition Resistance (FVIR). Which they have not to my knowledge. Maybe the "what ifs" in this industry is getting a little to paranoid. LEED Green Associates Inachi US Member of the Year Award 2009 Best Home Inspector Software http://co.nachi.org/inachiawards |
|
#13
|
||||
|
||||
|
He asked about the rules. People conveyed what the rules were. I didn't witness any fear mongering here.
If you disagree with the rule, you might take it up with the ICC and the various state regulatory agencies that require it. Smartassery was not necessary. Has Evacuated to a Nate Free Zone Chuck Evans (TREC #7657) Level III Infraspection Institute Certified Infrared Thermographer (#8402) HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook Houston Thermal Inspections & Infrared Imaging Find us on Facebook Houston Home Inspector Houston, TX |
| Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
I don't disagree with the rules, just the interpetation of the readers here.
LEED Green Associates Inachi US Member of the Year Award 2009 Best Home Inspector Software http://co.nachi.org/inachiawards |
|
#15
|
|||
|
|||
|
Is a thermostat control a switching device??
Juan Jimenez
A House on a Rock Home Inspections LLC God. Family. Home. 804-269-4321 Richmond Home Inspector Richmond Radon Testing Recommend Us! |
![]() |