Default elevating hot water heaters.

Hello All
I would like some imput on electric water heaters being elevated 18 inches if installed in a garage.
Some of the water heater manufactures state in their instalation instructions that electric water heaters need to be elevated 18 inches because of the risk of explosion due to a spark when turned on. some have gaskets around the access covers some don't. So should they be elevated or not? Gas was required to be elevated untill 2004 when the design was changed and became sealed at the lower section.
Thanks
Mark





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
Need a home inspection in Kansas? Check out InterNACHI's listing of Kansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/29/12, 1:11 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 7,859
Default Re: elevating hot water heaters.

The ignition source (for electric) is not at the bottom of the water heater (gas is).
Why does it have to be raised 18"?

Furnaces don't have to be raised either. Their burner is >18" above the floor.



"working together to get-IR-done" Chris Walsh
Bracebridge, Ontario:


David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #3  
Old 12/29/12, 1:54 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 6,936
Send a message via AIM to sstanczyk
Default Re: elevating hot water heaters.

The bottom coil on my electric water heater is 10" off the floor so it would not require the normal height stand but would still need to be elevated.

Washington requires that home inspectors "Report as a fire hazard the presence of any ignition source (gas and electric water heaters, electrical receptacles, electronic air cleaners, motors of installed appliances, etc.) that is within eighteen inches of the garage floor."




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #4  
Old 12/29/12, 2:02 PM
KEVIN WOOD, CMI's Avatar
KEVIN WOOD, CMI KEVIN WOOD, CMI is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 10,187
Default Re: elevating hot water heaters.

That applies here also!
Reply With Quote
  #5  
Old 12/29/12, 3:21 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 24,926
Default Re: elevating hot water heaters.

It is a matter of interpetation.

The T-stat on a residential electric water heater are #1) sealed contacts and #2) more than 18" above the bottom of the water heater on some models, so there is no reason to elevate the tank.

Let the Code Officer know how stupid his determination is.
Reply With Quote
  #6  
Old 12/29/12, 3:33 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 6,936
Send a message via AIM to sstanczyk
Default Re: elevating hot water heaters.

Quote:
Originally Posted by mcyr View Post
It is a matter of interpetation.

The T-stat on a residential electric water heater are #1) sealed contacts and #2) more than 18" above the bottom of the water heater on some models, so there is no reason to elevate the tank.

Let the Code Officer know how stupid his determination is.
Sorry Marcel but just look at the photo you posted. Those contact screws are in the wide open, not sealed. The same goes with the contact screws on the end of the heating elements. They are not sealed either. The thermostat is normally located at the top element with the reset button, so it is not an issue. The bottom heating element is less than 18 inches from the bottom of the tank, therefore the connection is also less than 18 inches. A loose wire can mean arcing. Don't ask me why it would arbitrarily come loose without movement of some sort but there are times when people just replace the $20 element instead of spending $500-800 for a complete new heater.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #7  
Old 12/29/12, 3:49 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 24,926
Default Re: elevating hot water heaters.

The screws you are looking at is for the Line Voltage, and the contactor is in a sealed case.
Believe what you want. I will not call out an electric water heater in a garage.
Reply With Quote
  #8  
Old 12/29/12, 3:55 PM
cevans cevans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: TX
Posts: 3,494
Please Note: cevans is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: elevating hot water heaters.

As David alluded to, the requirement is for elevation of the ignition source. That does not equate to the water heater needing to be elevated 18 inches above the floor.

I have an electric water heater in my garage. The lowest potential source of ignition is 10 inches above the bottom of the unit. The unit itself only needs to be elevated 8 inches to to meet the 18 inch requirement.

In Texas the state SOP requires electric water heaters to be reported as a defect if they do not meet the clearance requirement. Check for any specific rules in your state.
Reply With Quote
  #9  
Old 12/29/12, 4:38 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 24,926
Default Re: elevating hot water heaters.

For those that are really worried that the electric water heater needs to be at 18", because of the if "Spark", and I don't believe the garage has been labeled as a hazardous zone as of yet, maybe you should recommend one of these.

http://www.hubbellheaters.com/html/modeler.htm

Reply With Quote
  #10  
Old 12/29/12, 4:43 PM
cevans cevans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: TX
Posts: 3,494
Please Note: cevans is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: elevating hot water heaters.

Quote:
Originally Posted by mcyr View Post
For those that are really worried that the electric water heater needs to be at 18", because of the if "Spark", and I don't believe the garage has been labeled as a hazardous zone as of yet, maybe you should recommend one of these.

Why be a smartass about it?
Reply With Quote
  #11  
Old 12/29/12, 4:52 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 24,926
Default Re: elevating hot water heaters.

Because I don't think they have to be elevated for the worse scenario of any flammable fumes that can accumulate in a residential garage.
It is an over reaction.

If it were that dangerous, they would have mandated electric water heaters to be designed like the gas ones in 2003.

Flammable Vapor Ignition Resistance (FVIR). Which they have not to my knowledge.

Maybe the "what ifs" in this industry is getting a little to paranoid.
Reply With Quote
  #12  
Old 12/29/12, 4:57 PM
cevans cevans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: TX
Posts: 3,494
Please Note: cevans is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: elevating hot water heaters.

He asked about the rules. People conveyed what the rules were. I didn't witness any fear mongering here.

If you disagree with the rule, you might take it up with the ICC and the various state regulatory agencies that require it.

Smartassery was not necessary.
Reply With Quote
  #13  
Old 12/29/12, 4:59 PM
Marcel R. Cyr, CMI's Avatar
Marcel R. Cyr, CMI Marcel R. Cyr, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 24,926
Default Re: elevating hot water heaters.

I don't disagree with the rules, just the interpetation of the readers here.
Reply With Quote
Need a home inspection in Kansas? Check out InterNACHI's listing of Kansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/29/12, 5:20 PM
Juan C. Jimenez Juan C. Jimenez is offline
InterNACHI Member
 
Join Date: Jan 2012
Location: central va
Posts: 5,912
Default Re: elevating hot water heaters.

Is a thermostat control a switching device??



Juan Jimenez
A House on a Rock Home Inspections LLC
God. Family. Home.
804-269-4321
Richmond Home Inspector
Chesterfield Home Inspector
Petersburg Home Inspector
Richmond Radon Testing


Reply With Quote
  #15  
Old 12/29/12, 5:26 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 6,936
Send a message via AIM to sstanczyk
Default Re: elevating hot water heaters.

Quote:
Originally Posted by mcyr View Post
I don't disagree with the rules, just the interpetation of the readers here.
My quote was directly from the Washington State Standards of Practice as codified in State law. No Washington State inspector has a choice. It must be reported as a fire hazard.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Rental water heaters rcooke Canadian Inspectors 35 1/26/11 2:32 PM
Need Help On Chimney Liners Nick Scibetta Exterior Inspections 13 1/11/06 9:53 PM

All times are GMT -4. The time now is 8:44 AM.
no new posts