InterNACHI


Go Back   InterNACHI Inspection Forum > Specific Inspection Topics > Plumbing Inspections

Notices

Plumbing Inspections Contains discussions about plumbing.

 
Reply
 
LinkBack Thread Tools
  #1  
Old 10/25/08, 7:38 PM
David B. Alvares David B. Alvares is offline
InterNACHI Member
 
Join Date: May 2008
Location: Hilmar, CA
Posts: 16
Default Exhaust Flue identification and clearances

My question is there are main types of flues out there from single wall to multi walled. Is there a stamp, label or a marking of some sort that I should be looking for that tells me what type of flue it is.

Further more what are the appropriate clearances for a single walled pipe compared to a multi walled pipe. Along with the clearance issue I have read in some posts that because fiberglass insulation is not flammable that it can be in contact with a flue but cellulose insulation can not. If someone knows of a good website with this information then please let me know. I have also attached some pictures that might present some more discussion.

I have also attached a picture of a water heater flue located in a garage that is missing a collar at the ceiling. I called it out because of the fire rating between the interior and exterior of the home. I just wanted to know if that how you would call that issue out or if it's an issue at all.
Attached Thumbnails
exhaust-flue-identification-and-clearances-100_5933.jpg   exhaust-flue-identification-and-clearances-100_5934.jpg   exhaust-flue-identification-and-clearances-100_5838.jpg  




David Alvares
Modesto, CA 95354
866-757-8480
Reply With Quote
  #2  
Old 10/25/08, 8:15 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Exhaust Flue identification and clearances

CLEARANCES
Reply With Quote
  #3  
Old 10/26/08, 8:01 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exhaust Flue identification and clearances

Quote:
Originally Posted by dvalley View Post
For Canadians, some of these distances are different for different fuels. Refer to codes or manufacturer's specs.
Reply With Quote
  #4  
Old 11/2/08, 12:34 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Exhaust Flue identification and clearances

Great site David. Thanks!
Reply With Quote
  #5  
Old 11/2/08, 9:36 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Exhaust Flue identification and clearances

All the B-vents I've ever seen have a label on them that specify 1" clearance. The site David posted says 2". All I've ever heard as an inspector is 1" for a B-vent and 6" for a single walled pipe. That company is located in the People's Republic of California. Maybe that has something to do with it.

Here's an example of what I say: "The water heater vent pipe is too close to combustible material, and should be serviced before the close of escrow. A single-walled vent pipe should be six inches away from any combustible material, and a double-walled vent pipe should be one inch away. This construction defect is considered a fire hazard. We recommend that repairs meeting the manufacturers specifications be conducted for fire safety reasons."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 11/2/08, 10:46 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exhaust Flue identification and clearances

Quote:
Originally Posted by jfunderburk View Post
All the B-vents I've ever seen have a label on them that specify 1" clearance. The site David posted says 2". All I've ever heard as an inspector is 1" for a B-vent and 6" for a single walled pipe. That company is located in the People's Republic of California. Maybe that has something to do with it.

Here's an example of what I say: "The water heater vent pipe is too close to combustible material, and should be serviced before the close of escrow. A single-walled vent pipe should be six inches away from any combustible material, and a double-walled vent pipe should be one inch away. This construction defect is considered a fire hazard. We recommend that repairs meeting the manufacturers specifications be conducted for fire safety reasons."
Joe:

Is the 6" for all fuels down there?

In Canada, it is:
-6" for gas
-9" for oil
-18" for wood
Reply With Quote
  #7  
Old 11/2/08, 10:50 AM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: Exhaust Flue identification and clearances

Joe F. is correct, Clearance to Combustibles: 1"

http://www.selkirkcorp.com/Default.aspx





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #8  
Old 11/2/08, 11:10 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exhaust Flue identification and clearances

Quote:
Originally Posted by mkyriacou View Post
Joe F. is correct, Clearance to Combustibles: 1"

http://www.selkirkcorp.com/Default.aspx

Mario:

It appears that one of your INACHI brothers is using your name or was this really you???

NACHI Bashing, should... 11/1/08 10:46 AM Shut up you whining little *****. You need a good ***** slapping. Love, Mario
Reply With Quote
  #9  
Old 11/2/08, 12:45 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: Exhaust Flue identification and clearances

Quote:
Originally Posted by Brian A. MacNeish View Post
Mario:

It appears that one of your INACHI brothers is using your name or was this really you???

NACHI Bashing, should... 11/1/08 10:46 AM Shut up you whining little *****. You need a good ***** slapping. Love, Mario
Not me.





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #10  
Old 11/2/08, 12:50 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: Exhaust Flue identification and clearances

That's the problem with this system, it doesn't automatically show the member giving the rep.

It's a very silly system if you ask me. It kind of reminds me of grade school, remember the stars the teacher gave students?

Brian, it appears that the rep system has become an obssesion with you. I suggest that you turn it off before you go into the red.





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #11  
Old 11/2/08, 1:47 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exhaust Flue identification and clearances

Quote:
Originally Posted by mkyriacou View Post
That's the problem with this system, it doesn't automatically show the member giving the rep.

It's a very silly system if you ask me. It kind of reminds me of grade school, remember the stars the teacher gave students?

Brian, it appears that the rep system has become an obssesion with you (Don't think so......Reverse that!!!). I suggest that you turn it off before you go into the red. (I can't do a thing with it!!!)



From my experiences with you, you surely use it more than any other member!!!!
Reply With Quote
  #12  
Old 11/2/08, 1:53 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: Exhaust Flue identification and clearances

Quote:
Originally Posted by Brian A. MacNeish View Post
[/color]

From my experiences with you, you surely use it more than any other member!!!!
Quote:

(I can't do a thing with it!!!)
That's because you are stupid!





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #13  
Old 11/2/08, 2:21 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exhaust Flue identification and clearances

Quote:
Originally Posted by mkyriacou View Post
That's because you are stupid!
OK, Mario!! You can have the last word. Now go take a few more pills!
Reply With Quote
  #14  
Old 11/2/08, 4:55 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: Exhaust Flue identification and clearances

Quote:
Originally Posted by Brian A. MacNeish View Post
Sorry Mario, Sometimes I have a very difficult time controlling myself, Raymond Wand has influenced me (in a bad way)beyond help.


I forgive you!





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com

Last edited by mkyriacou; 11/2/08 at 5:03 PM..
Reply With Quote
  #15  
Old 11/2/08, 5:46 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exhaust Flue identification and clearances

Quote:
Originally Posted by mkyriacou View Post
(Trying to be Brian)
Sorry Mario, Sometimes I have a very difficult time controlling myself, Raymond Wand has influenced me (in a bad way)beyond help.
Mario:
You obviously didn't get the pills in you in time. Now you think you're me........or has the obssession become so great you have 2 personalities (or more) inside your head..........me and you!! When I'm not around you can still carry on the discourse.....it's just I can't be there. Please record it!!

And get help!!!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 8:54 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts