Hello,
Fellow inspector!I have a question about expansion tanks on closed water system.Is it correct that an expansion tank be installed on a closed water system to be installed on all water heaters?I read in National plumbing code that on a closed water system(were their is a water regulator valve installed)that an expansion tank is required for thermal expansion. Anyone know the correct answer cpetty |
My understanding is that the installation of a regulator or other device that prevents backflow to accomdate expansion requires an expansion tank or pther approved means of handling expansion in the system.
Do you follow the IRC or UPC? As far as I can tell, an expansion tank is required only on a boiler, by the IRC. Here is what the UPC says. . . 608.3 In addition to the required pressure or combination pressure and temperature relief valve, an approved, listed expansion tank or other device designed for intermittent operation for thermal expansion control shall be installed whenever the building supply pressure is greater than the required relief valve pressure setting or when any device is installed that prevents pressure relief through the building supply. The tank or device shall be sized in accordance with the manufacturer’s recommendation. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
Most water heaters require an expansion tank if a closed loop setup is used.
Without it TPR valves and tub or sink valves will very often drip when a hot water circulation pump is turned on.. |
In ky they were requiring expansion tanks on water heaters if you installed a back flow preventer.
Bungalows to Mansions Professional Inspection Services, LLC dba 1st Inspection Services Bruce M. Graham III Gainesville, FL 32608 352 871 8989 NACHI05091592 ICC 5268478 www.1stinspectionsfl.com www.bungalowstomansions.com |
I went to do an inspection at a home where the water heater was an electric heater.It had no expansion tank and the T&P drain was routed through the wall and a 90 deg.elbow that went up then crossed through the ceiling at the subfoor area then down the oppsite wall to discharge outside.I called this an area of concern.The T&P valve was aready rusted & leaking.The owners called a plumber and he said the w.heater was up to code.I'm not a code enforcer,but this is a improper installation.Any feed back?
The vast majority of tanks I see lack overflow legs all together. All the piped ones I have seen dispense onto the foundation floor. Of course, the climate differences may explain our different experiences.
Laura Line is a non-member guest and is in no way affiliated with InterNACHI or its members.
here in maryland, (this info came from a county plumber who came to check my findings that the listing agent didn't think was correct, the drain exited into a sanitary tub and not outside, and had no check valve)
expansion tanks have to be installed on all new 2005-2006 HWH's that are on city water, and those that don't have them will have to have them installed within the next 8 or so years to prevent backflow to the main line that may rupture if correct valve is not installed on water main to house. |
| Expansion tank immediately downstream of main shut-off? | pcoulter | Plumbing | 11 | 1/30/08 1:00 PM |
| Expansion tank on side! | pcoulter | HVAC | 16 | 11/16/07 9:07 PM |
| Septic System Care | mlarson | Ancillary Services & Additional Topics | 49 | 8/31/07 11:26 PM |
| Oil Tank in Basement Bedroom! | csteele | HVAC | 15 | 10/23/06 9:25 AM |