  #16  
Old 1/14/11, 9:12 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Expansion Tanks

Quote:
Originally Posted by bkelly2 View Post
When they put a Back Flow device and or Regulator on the water supply to the house, and you have Copper or CPVC Piping then yes they are needed.
The type of piping is irrelevant. The code doesn't specify a piping exception.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 1/14/11, 9:16 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Expansion Tanks

Quote:
Originally Posted by krunquist View Post
Good article Nick. All correct. But what I'm asking is the expansion tank really a needed item or is it code overkill? I'll continue with code etc. for inspections but personally I see overkill and wonder what others have seen in the field. I'm especially interested if ther are any plumbers out there with field experience with expansion tanks or lack of them.
How do you define "code overkill"? There is no way to know what occurs without dissecting the water heater to see if damage is present. I always assume people smarter than I am wrote the codes and don't question it, as I'm not privy to the information they used in deciding to promulgate it.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #18  
Old 1/14/11, 9:32 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Expansion Tanks

Quote:
Originally Posted by jfunderburk View Post
How do you define "code overkill"? There is no way to know what occurs without dissecting the water heater to see if damage is present. I always assume people smarter than I am wrote the codes and don't question it, as I'm not privy to the information they used in deciding to promulgate it.
Wasn't the expansion tank for DHW systems brought in when some codes/municipalities required a backflow/check valve on the municipal water supply line? We don't have the backflow/check valve requirement here, hence, no expansion tanks on the DHW system.
Reply With Quote
  #19  
Old 1/14/11, 11:21 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Expansion Tanks

Quote:
Originally Posted by Brian A. MacNeish View Post
Wasn't the expansion tank for DHW systems brought in when some codes/municipalities required a backflow/check valve on the municipal water supply line? We don't have the backflow/check valve requirement here, hence, no expansion tanks on the DHW system.
Do you have pressure regulators? Those valves create a closed system at the house and would meet the criteria for requiring an expansion control device.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #20  
Old 1/14/11, 2:02 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Expansion Tanks

The average pressure regulator has a diaphragm. If you run water backs through the valve, the diaphragm will open up.
Reply With Quote
  #21  
Old 1/14/11, 2:10 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Expansion Tanks

Quote:
Originally Posted by jfunderburk View Post
1) Use the term "an approved device for thermal expansion control." That is how the code references it. "Expansion tank" is inappropriate as some valves have thermal expansion control built in.

2) Expansion control is not to prevent backflow. Instead, thermal expansion control is required whenever the house is a closed system (and the water cannot back up into the municipal water system).

1. We are not talking about code.

2. Expansion tees work for a closed loop systems. And expansion tanks do prevent backflow.
Reply With Quote
  #22  
Old 1/14/11, 3:30 PM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,715
Default Re: Expansion Tanks

I do not open hot water heater drain valves, as there is too much risk in getting them to turn off after they are opened.



CMI, CPI, KS #0110-0094 Termite #16601
KS Radon #KS-MS-0027
BBB A+ Accredited Business
Serving the Greater Kansas City Metro Area
Eastern Kansas/Western Missouri
http://www.metrospeckc.com
"If opportunity doesn't knock, build a door"--Milton Berle
Reply With Quote
  #23  
Old 1/14/11, 3:34 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Expansion Tanks

Quote:
Originally Posted by gfarnsworth View Post
I do not open hot water heater drain valves, as there is too much risk in getting them to turn off after they are opened.
I was curious about that myself. It sounded like at least a couple inspectors check pressure at the WH. I do not open the valves either.

Perhaps another poll is in order.
Reply With Quote
  #24  
Old 1/14/11, 3:52 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Expansion Tanks

Quote:
Originally Posted by jjonas View Post
I was curious about that myself. It sounded like at least a couple inspectors check pressure at the WH. I do not open the valves either.

Perhaps another poll is in order.
I do not open water heater drain valves for a very good reason.

Hard water deposits buildup in a tank that has not been drained regularly and WILL cause the valve to not close again.

Do you have to ask why I know that?

Use and outside faucet, the end of a washing machine hose or another hose fitting like on a laundry tub faucet.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI


Last edited by mlarson; 1/14/11 at 6:44 PM..
Reply With Quote
  #25  
Old 1/14/11, 3:54 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Expansion Tanks

Quote:
Originally Posted by jbraun View Post
1. We are not talking about code.
Then don't call out their absence at all, as the only reason they exist is because of codes.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #26  
Old 1/14/11, 5:19 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Expansion Tanks

I do not call out their absence.
Anyway, my local code authority says expansion tees are acceptable.
Reply With Quote
  #27  
Old 1/14/11, 5:33 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Expansion Tanks

Quote:
Originally Posted by sstanczyk View Post
After 20 minutes or so, the hot water should be replenished, check your reading again. If the pressure has increased more than 8-10 pounds or more, the unit is bad and should be replaced.
A failing regulator will give you similar results. So I would call that an indication, but inconclusive to determining that an expansion-tank has failed.

The water heater drain-valve was where I checked for pressure for many years. After ruining four or five pressure gauges (at $60 a pop) I stopped doing it, unless there's absolutely no other place to check.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #28  
Old 1/14/11, 7:25 PM
Marc-Andre Beauchemin's Avatar
Marc-Andre Beauchemin Marc-Andre Beauchemin is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: BROSSARD,Quebec Canada
Posts: 298
Default Re: Expansion Tanks

Keith,

I believe the 2008 Plumbing code is when it was introduced. I have not come across such installations.
Personally, I do not believe that they are as necessary as TPRV.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Closed plumbing systems & expansion tanks jfunderburk Plumbing Inspections 31 1/4/12 2:21 PM
Roof Deck Seams Visible - What's Wrong? psullivan Roofing Inspections 35 11/30/10 1:22 AM
Potable Water Expansion Tanks inxil InterNACHI & RealMatcher Blogs 1 4/9/09 12:05 AM
Please proof this article: An Overview of Water Heater Expansion Tanks. gromicko Plumbing Inspections 5 3/30/09 2:54 PM
Pressure regulators and expansion tanks rray Plumbing Inspections 22 9/20/08 12:22 PM


All times are GMT -4. The time now is 2:30 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts