Does anyone know when the IRC and the NFGC started to prohibit running flex gas lines through cabinetry? I did an inspection recently where this condition was present. I wrote it up as a safety hazard and that a solid gas pipe needed to be installed to the furnace valve assembly that extended through the cabinet for the flex to connect to. The HVAC company that installed the equipment stated that this was allowed when they did the install (approximately 2 years ago), but that they would fix it if I could show them the code. The AHJ was using the 2000 IRC at the time of construction. I know this sounds like I'm trying to enforce code, but the HVAC company is trying to make me look bad with the Realtor. I have called the AHJ and they are little to no help. Thanks
|
|
#2
|
||||
|
||||
|
2003 IRC G2422.1.2 Appliance fuel connectors: Connectors shall have an overall length not to exceed 3 feet........ Connectors shall not be concealed within, or extended through, walls, floors, partitions, ceilings or appliance housings. A shutoff valve......blah, blah
|
|
#3
|
|||
|
|||
|
Flex line is not allowed to pass through the cabinet. I call it no matter how old the home is.
Sorry I do not have a code for you. I am sure someone will post the applicable code for you. |
|
#4
|
|||
|
|||
|
Please Note:
Tab M. Wilcox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks for the replies! I have the 2003 IRC code book and was aware of the 2003 IRC G2422.1.2 Appliance fuel connectors section. What I need is when was this brought into the IRC or NFGC code cycles. Thanks again!
|
|
#5
|
||||
|
||||
|
The listing of the appliance connector has never allowed these restricted conditions.
Have them show you otherwise. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Gas flex connector to furnace | jcahill | Inspecting HVAC Systems | 25 | 7/24/07 6:22 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Flex duct used for exhasut flue. | jlybolt | Inspecting HVAC Systems | 11 | 4/5/07 11:04 PM |
| Gas and oil hot water tank and Boiler Share Vents | hvanderbeek | Miscellaneous Discussion for Inspectors | 8 | 1/25/07 5:22 PM |
| surface yellow gas flex piping? | Coral | Inspecting HVAC Systems | 16 | 12/22/06 2:43 AM |