  #1  
Old 10/28/11, 1:49 PM
John Safstrom John Safstrom is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Allen,TX
Posts: 63
Default flexible gas line in fireplace (pics)

This wasn't from an inspection, but rather a question I was asked. Someone sent me this picture and asked me a question about this fireplace in their home. Obviously there is a leak at the fitting and looks to be cross-threaded. My question is about the flexible gas line. Does that fall under manufacturer's requirments of the insert? Are there any code requirements against flexible gas lines in the firebox?






John Safstrom
TREC #10566
Systematic Home Inspections, PLLC
Allen,TX
www.systematichomeinspections.com
john@systematichomeinspections.com


Last edited by jsafstrom; 10/28/11 at 2:01 PM..
Reply With Quote
Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/28/11, 2:00 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: flexible gas line in fireplace (pics)

Fine like that
BUT NOT LIKE THAT!!!
Reply With Quote
  #3  
Old 10/28/11, 2:04 PM
John Safstrom John Safstrom is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Allen,TX
Posts: 63
Default Re: flexible gas line in fireplace (pics)

So one would follow the manufacturer rec's for gas supply piping for the gas logs or the insert itself?



John Safstrom
TREC #10566
Systematic Home Inspections, PLLC
Allen,TX
www.systematichomeinspections.com
john@systematichomeinspections.com

Reply With Quote
  #4  
Old 10/28/11, 2:18 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: flexible gas line in fireplace (pics)

Quote:
Originally Posted by jsafstrom View Post
So one would follow the manufacturer rec's for gas supply piping for the gas logs or the insert itself?
Yes manufacturers instructions always.
They are similar in use of 1/2 inch blackpipe through the knockout with an 18 inch 3/8" flex (stainless)
Reply With Quote
  #5  
Old 10/28/11, 2:26 PM
John Safstrom John Safstrom is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Allen,TX
Posts: 63
Default Re: flexible gas line in fireplace (pics)

thanks Bob



John Safstrom
TREC #10566
Systematic Home Inspections, PLLC
Allen,TX
www.systematichomeinspections.com
john@systematichomeinspections.com

Reply With Quote
  #6  
Old 10/28/11, 2:57 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: flexible gas line in fireplace (pics)

That brass thread is striped on the threads of the black iron pipe according to what your picture shows.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676

Last edited by kwood; 10/28/11 at 3:03 PM..
Reply With Quote
  #7  
Old 10/30/11, 9:32 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: flexible gas line in fireplace (pics)

They have flames comming out of a gas line and they don't call a plumber ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #8  
Old 10/30/11, 12:37 PM
An HI An HI is offline
Active Poster
 
Join Date: Oct 2011
Location: cyberspace
Posts: 196
Please Note: An HI is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: flexible gas line in fireplace (pics)

Quote:
Originally Posted by roconnor View Post
They have flames comming out of a gas line and they don't call a plumber ...
Isn't that the pilot light?
Reply With Quote
  #9  
Old 10/30/11, 7:48 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: flexible gas line in fireplace (pics)

Flex in firebox can be OK for gas logs. Not OK if using wood to burn.

AND like the man said / CALL a plumber.
Reply With Quote
  #10  
Old 10/31/11, 9:27 PM
Pete Campbell's Avatar
Pete Campbell Pete Campbell is offline
InterNACHI Member
 
Join Date: Apr 2011
Location: Fort Pierce, FL
Posts: 592
Default Re: flexible gas line in fireplace (pics)

you need a flexible line to accommodate whatever the distance from the gas line rough-in to the appliance.





Pete Campbell

pete4545@comcast.net
http://www.PortStLucieInspections.com
http://www.ChooseGI.com
http://ifwemissitwewillfixit.com


Inspecting Fort Pierce, St. Lucie Village, Lakewood Park, Vero Beach, Indian River Shores, Sebastian, Fellsmere, Fort Drum, Okeechobee, Jensen Beach, Stuart, Palm City, Hobe Sound and Indiantown, Florida.
Reply With Quote
  #11  
Old 11/1/11, 7:20 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: flexible gas line in fireplace (pics)

For gas logs copper and aluminum tubing are also allowed in some areas and per the IRC



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 11/1/11 at 7:25 PM..
Reply With Quote
  #12  
Old 11/7/11, 9:57 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: flexible gas line in fireplace (pics)

Quote:
Originally Posted by An HI View Post
Isn't that the pilot light?
kind of like pre-ignition.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #13  
Old 11/8/11, 12:33 PM
Kevin T. McDade's Avatar
Kevin T. McDade Kevin T. McDade is offline
InterNACHI Member
 
Join Date: Jan 2010
Location: Hamilton Ontario
Posts: 80
Default Re: flexible gas line in fireplace (pics)

Love second picture. Tape or Liquid dope visible on flange fitting, dont see that on pipe fitting side. Home owner tried repair again and in wrong spot?



Can-Am Home Inspections Inc.
Level 1 Thermography
Specializing in Building Infrared Thermography
ProLab Certified
INACHI #09113003
IAC2 #01-8254
www.can-amhomeinspections.com
Reply With Quote
Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/11/11, 1:34 AM
Keith Silva Keith Silva is offline
New User
 
Join Date: Dec 2011
Posts: 1
Please Note: Keith Silva is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: flexible gas line in fireplace (pics)

So it is safe to use flex line in a gas fireplace that has a vented log set in it? My girlfriend just bought a new log set for her gas fireplace and the gas inlet on the new set is on the right hand side but the gas inlet into the fireplace is on the left. Is it safe for me to run a flex line around and behind the pan that came with the set to the other side?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Flexible gas lines mthiltgen Plumbing Inspections 5 6/29/09 9:56 PM
Main Line vs. Supply Line Reporting Details sshockley Plumbing Inspections 2 6/14/09 3:07 PM
Difficult Chimneys thance Inspecting HVAC Systems 2 1/29/08 8:16 PM
Selected Electrical Incidents and Occurrences - First Quarter pabernathy Electrical Inspections 0 12/2/07 1:43 PM
Need HVAC Pics! hgordon Inspecting HVAC Systems 2 2/17/06 10:06 AM


All times are GMT -4. The time now is 2:32 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts