Default Flexible Gas Line Underground

The line was run underground from the meter to the back patio grill. Probably about 20'. Did not see any reference in the IRC that hard pipe must be used. The only reference I saw was that the line must be buried at least 8". Can it be flexible line?
Attached Thumbnails
flexible-gas-line-underground-dsc04295.jpg  



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/22/10, 9:18 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Flexible Gas Line Underground

As long as the line is approved for underground, but I am betting it is not. I have never seen a yellow colored underground rate flex line before. You definitely need to check into it. Underground flex line is used all the time in my area.
Reply With Quote
  #3  
Old 11/22/10, 9:43 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,629
Default Re: Flexible Gas Line Underground

This brand, WARDFLEX, says it may be installed underground with non-metallic conduit. But the ends should be sealed to keep out foreign matter and moisture.

Page 55 http://www.wardflex.com/images/design_install_guide.pdf



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 11/22/10, 9:46 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Flexible Gas Line Underground

Quote:
Originally Posted by ccurrins View Post
This brand, WARDFLEX, says it may be installed underground with non-metallic conduit. But the ends should be sealed to keep out foreign matter and moisture.

Page 55 http://www.wardflex.com/images/design_install_guide.pdf
Same with Diamond Back. http://www.mtlfab.com/media/L1627.pdf

ACCEPTABLE USAGE
DIAMONDBACK™ CSST shall not be buried directly in the ground or directly embedded in
concrete. When DIAMONDBACK™ is to be buried in the ground or embedded into concrete it
shall be routed inside of a nonmetallic conduit such as schedule 40 PVC. The conduit must be
sealed at any end that is exposed to outdoor weather conditions to prevent water from entering.
It is recommended that the CSST be one continuous piece inside the conduit from end to end.
CSST mechanical fittings are not allowed or permitted inside the conduit.
Reply With Quote
  #5  
Old 11/23/10, 2:21 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Flexible Gas Line Underground

http://www.gastite.com/include/langu..._D+I_Guide.pdf

Here is the gastite brand instructions. They allow penetrations through wood, but must be protected through masonry. THey also manufacture a different covering for underground applications.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #6  
Old 11/23/10, 3:41 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Flexible Gas Line Underground

If you want to sound knowledgeable and professional in your reports, call it Corrugated Stainless Steel Tubing (CSST). If you want to sound otherwise, call it flex pipe, flex line, yellow pipe, etc.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 11/23/10 at 3:48 PM..
Reply With Quote
  #7  
Old 11/23/10, 3:51 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Flexible Gas Line Underground

Quote:
Originally Posted by jfunderburk View Post
If you want to sound knowledgeable and professional in your reports, call it Corrugated Stainless Steel Tubing (CSST). If you want to sound otherwise, call it flex pipe, flex line, yellow pipe, etc.
If you want to be knowledgable, then call the local rep. Many offer free classes and certifacations. I talked to the one for flextite since I was curious. He said they are having one soon. Only a couple of hours educational class. And then like magic wola you are certified...




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #8  
Old 11/23/10, 4:02 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Flexible Gas Line Underground

http://www.wardflex.com/images/design_install_guide.pdf

"The WARDFLEX system described in this guide is intended primarily for interior use. See section 4.6.4.2 for specifics on outdoor applications. [That section speaks about connections to outdoor appliances.]

4.3.5 OUTDOOR ISSUES
General Provisions

WARDFLEX Mechanical Joint Fittings shall be protected from the effects of weather when used outdoors. After the connection is made to outdoor equipment the WARDFLEX Mechanical Joint Fitting shall be sealed by wrapping two layers of tape (e.g. PVC, Silicone) or by applying shrink sleeves (e.g. PVC, Polyolefin).

The following additional instructions regard the use of WARDFLEX in systems in which portions of the piping are exposed to the outdoors as required to make connections to gas meters or gas appliances,
which are attached to, mounted on, or located in close proximity to the building structure.

The external protective covering shall remain intact as much as practical for the given installation.

When installed along the side of a structure (between the ground and 6 ft.) in an exposed condition, the WARDFLEX must be protected inside a conduit or installed in a location which will not subject it to mechanical damage.

WARDFLEX shall not be buried directly in the ground or directly embedded in concrete (e.g. patio slabs, foundations or walk ways). When burial or embedment is required,WARDFLEX shall be routed inside nonmetallic (e.g.PVC) conduit. The conduit shall be sealed at any exposed end to prevent water from entering using double wrapped PVC tape or PVC shrink sleeves.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 11/23/10, 4:03 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Flexible Gas Line Underground

Don't forget bonding requirements.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 11/23/10, 4:27 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Flexible Gas Line Underground

Good stuff Joe. The gastite is allowed in all weather applications. Go figure.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Flexible Natural Gas line thejnicki Plumbing Inspections 4 8/1/06 11:30 AM
TPRV line and condensate line marriage ccarrington Plumbing Inspections 3 4/29/06 7:59 AM


All times are GMT -4. The time now is 2:32 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts