Inspected townhouse today that had flexible gas line running in from supply line outside house across unfinished basement ceiling through trusses all the way to furnace and water heater. I thought max was six feet for appliances, also had flexible line running back through ceiling to fireplace. Sent picture along to see. I'm assuming that all the townhouses in this association are done this way. This is Cottage Grove, MN maybe local codes differ here. I'll check back later, thanks, Mark
Attached Thumbnails
flexible-gas-lines-img_1866.jpg  
Reply With Quote
Find an InterNACHI certified Alaska Home Inspector (and anywhere else in North America)
  #2  
Old 6/29/09, 9:27 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Flexible gas lines

That's CSST.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #3  
Old 6/29/09, 9:28 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Flexible gas lines

CSST (Corrugated Stainless Steel Tubing). It's designed to be the conduit for gas supply all over the house. What you've described is perfectly acceptable, provided it's adequately secured and not exposed to sharp edges. Here's a reference document.

http://www.omegaflex.com/trac/techni...Omega_Flex.pdf



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 6/29/09, 9:34 PM
Mark Thiltgen Mark Thiltgen is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: St Michael, MN
Posts: 73
Default Re: Flexible gas lines

Thank you very much gentlemen, I don't see much of it here, just wanted to make sure.
Reply With Quote
  #5  
Old 6/29/09, 9:44 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Flexible gas lines

If it's yellow, it needs to be bonded...forgot to tell you that. You should see a copper electrode from the gas system to a ground--usually tied to a bus in the main panel box. The yellow CSST was involved in a lawsuit and bonding is required. Search this board for more info about the lawsuit. Here's my comment about the lack of bonding:

"A common gas piping system called Corrugated Stainless Steel Tubing or CSST is present in this home. OmegaFlex's product is known as "TRACPIPE" or "COUNTERSTRIKE," Titeflex's CSST product is known as "GASTITE," Ward's CSST product is known as "WARDFLEX," and Parker Hannifin's CSST product is known as "PARFLEX." A lawsuit in 2005 claimed that CSST poses an unreasonable risk of fire due to lightning strikes. The lawsuit was settled and the manufacturers agreed to require additional electrical bonding above the minimum requirements set by the National Electric Code. We could not confirm that such bonding was present. You should consider a further evaluation and repair as deemed necessary by a competent, licensed electrician. More information regarding the suit is available on the internet here and here. A reference document is attached for your information."

Also, another common defect: you'll see it enter the furnace cabinet. it should be connected to a steel nipple outside the cabinet.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 6/29/09, 9:56 PM
Mark Thiltgen Mark Thiltgen is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: St Michael, MN
Posts: 73
Default Re: Flexible gas lines

Thanks Joe!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
Gas supply lines to water heaters. dkoehl Plumbing Inspections 5 3/6/11 2:07 AM
Flexible stainless steel lines? five.five Plumbing Inspections 9 7/27/06 7:01 PM


All times are GMT -4. The time now is 8:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts