hspinnler is a non-member guest and is in no way affiliated with InterNACHI or its members.
This is the first time I have seen this connection of the flue vent cap to the water heater. The tabs were spread out and the cap was installed flush to the water heater. A downward facing open Tee was installed inline. (likely to induce drafting) Is there anything wrong with this? I did recommend further evaluation.
Anybody out there that would like to reply to this one?
Hello Hank,
The installation is not installed to any manufacturers guidelines I have ever seen..... Maybe its the newest "gig", but I doubt it..... |
Last time I saw something like that was on a fuel oil furnace converted from a coal furnace ( used for drafting)I will check with my hvac connection
Dale L. Staben President - New Mexico Chapter DLS HOME INSPECTIONS LLC. 505-450-7640 |
No need to check with anyone, it's just wrong. The legs of the draft hood have been bent away (you can see them in the second photo).
My guess is that they thought the rise of the exhaust was more critical than the need for a draft hood. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
Hi to all,
I have to agree with Jeff, it just needs replacement, but I have a question is this a gas or an oil feed? Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
Thank you fellas. I believe the right call was made. I appreciate the responses. Gerry, the water heater is natural gas fired.
Anytime you see something like that you have to look for the appliance manual on the side of the W.H. It should be there...it better be there The MFG install instructions will tell you. Then the AH can modify it.. MFG first.
I bet the flue above the W.H. was in the "way" so a a little field modification was in order.. |
lewens is a non-member guest and is in no way affiliated with InterNACHI or its members.
I bet the recovery efficiency went way down also. No fresh air = very poor combustion.
Larry |
tnoisaw is a non-member guest and is in no way affiliated with InterNACHI or its members.
The only time that you should see this kind of connection would be on a mobile home water heater. Otherwise I know of no manufaturer that would allow this. I've installed at least two-five water heaters per week for the last ten years using various manufactures and have not come across this type of instalation.
Tony |
Expand- I do have limited experience with mobile home water heaters because the companies I worked for usually did not work on mobile homes. The reason for a sealed vent is because mobile home water heaters are usually in confined spaces with bad access to them. The confined space does not allow enough fresh air to get to the chimney for proper updraft. I believe the fresh air comes from below. The gas one’s I replaced were replaced with electric water heaters. I hope this helps.
Someone who works on mobile homes would be better qualified to answer this. |
| Gas and oil hot water tank and Boiler Share Vents | hvanderbeek | Miscellaneous Discussion for Inspectors | 8 | 1/25/07 6:22 PM |
| Water heater vent & corrosion to tank. | dmacy | Plumbing Inspections | 2 | 1/4/07 12:01 PM |
| Venting an oil-fired water heater | mh718 | Inspecting HVAC Systems | 3 | 11/16/06 10:36 AM |
| HVAC / Water Heater Flue | abishop | Inspecting HVAC Systems | 5 | 2/22/06 12:30 PM |